The Villages electricians use the type receptacle where you strip and push the wire in a hole. Over time and a heavy load (microwave) these connections will arc. Very minor at first, but over time will cause the exact problem you have. I would strip the 12-2 Romex back a few inches if possible, replace the outlet with a new one, use the screws on the side vs the push in holes, replace the plug on the microwave cord, and you should be good to go. Might also check the screw on the breaker to be sure that is tight as well. Somewhere in the circuit there was a loose connection. Most likely the connection at the outlet, but would also check the CB in the panel.