I don't know if it was explained to you but the 10' clearance is a condition to operate the transformer.

Using fiberglas "hot sticks" requires the operator to pull the energized elbows off . It is necessary to have that clear zone to provide separation from the energized 7,200 /7,900 or 19,900 primary voltage to ground (what ever the existing operating voltage is.