anyone have a electric receptacle installed in lamp post
Yes. Many have them. Several things to consider.

1) Is the circuit on your lamppost GFCI protected. Depending on where you live in The Villages, some are, some aren't. It's important to know your particular status.

2) If it is GFCI protected, you can install an appropriate receptacle box, which will include a TR/WR receptacle, and an in-use cover.

3) If it is not GFCI protected, you'll need an appropriate receptacle box, to include a WR/TR GFCI receptacle and an in-use cover.

Lastly, avoid the receptacles that are curved and match the contour of the lamppost. There are often sold by local vendors. These are not NEC compliant, as they do not provide in-use protection.

If you have any doubts, and are not confident in tackling this job by yourself, hire an electrician.