Originally Posted by EdFNJ View Post
Found these interesting tidbits:

Do I/you need a condensate drain trap if you have a condensate pump?
Yes, you need a condensate drain trap, even if you have a condensate pump. To repeat, the purpose of the condensate drain trap is usually to stop conditioned air from being blown outside. And this same logic applies if you have a condensate pump. However, without a trap, you will blow conditioned air into the pump, usually in the crawlspace, basement, or attic.

Are condensate drain traps required?

No code requires a condensate trap. However, IRC 1401.1 (we use the IRC here in Virginia) requires following the manufacturer’s instructions for installing “heating and cooling equipment and appliances.” You will be hard-pressed to find an AC installation manual that does not require condensate drain traps. Below is a diagram from a Carrier AC installation manual as an example. Notice that it requires installing a trap on both condensate drain lines.

Checked the manual from our just installed Carrier system and it does "require" one.

Copied from here: Your Air Conditioner Needs a Condensate Trap
My Carrier HVAC system was installed by The Villages builder and it does not have a trap on the condensate drain line.

However, I did have a Carrier system in Virginia, and it had a trap on the condensate drain.