I received 3 quotes for adding a dedicated outlet receptacle in the garage for our freezer and refridgerator.........all companies said ONLY GFI outlets could be installed. Were all 3 incorrect, maybe
They are correct. According the NEC:

210.8(A) Dwelling Units. All 125-volt through 250-volt receptacles installed in the locations specified in 210.8(A)(1) through (A)⁠(11) and supplied by single-phase branch circuits rated 150 volts or less to ground shall have ground-fault circuit-interrupter protection for personnel.

(1) Bathrooms

(2) Garages and also accessory buildings that have a floor located at or below grade level not intended as habitable rooms and limited to storage areas, work areas, and areas of similar use

(3) Outdoors