Quote:
Originally Posted by ronda View Post
Yes, there are 2 current draws Full Load Amps (FLA)/Starting current and Running Load Amps (RLA). Getting both numbers would be great, but the point I was making was don't assume you need a new circuit. There are motors that draw <2 amps that power big screens. As far as FLA is concerned, it is often not listed for small motors under reasonable loads because the difference between RLA and FLA is negligible. For a 1.6A motor I would expect this to be the case, but unless we have the data, we can't say for sure.

Bottom line. Don't assume you need a new ckt. Also, you will likely run only 1 motor at a time, so you don't need to add the 3 motors specs together. IMHO, from what I know, without knowing the specs of these specific motors, I think there is a very good chance a separate ckt is not warranted. It's worth the effort to get the specs on the motors.
Best answer yet! Also, check the circuit breaker amperage on the existing outlet.
Our outdoor circuits are all 20 amps, which should be plenty, and only an outlet change is necessary