Thread: Vacuum Breaker
View Single Post
 
Old 10-03-2024, 10:57 AM
retiredguy123 retiredguy123 is online now
Sage
Join Date: Feb 2016
Posts: 17,499
Thanks: 3,063
Thanked 16,663 Times in 6,593 Posts
Default

Quote:
Originally Posted by rhood View Post
I live North of 466 and have a pressure vacuum breaker (pvb) on my irrigation system which I believe is code
My question is if there is another vacuum breaker for the rest of the house and if there is, where would it be located?
Or, are the vacuum breakers on the hose bibbs all that are needed. The hose bibbs are the only spots where contaminated water might enter the system.
Thanks
There may be a check valve on the county side of the water meter to prevent your house water from backflowing into the main water system. Other than that, vacuum breakers are required, by the current code, on exterior hose bibbs and on the irrigation system that uses potable water.

If the sanitary manhole cover in the street is at a lower elevation than your house floor level, a backflow preventer is not allowed to be installed on the sanitary drainage system by code. Some people, who had a basement in their northern house, may have had a backflow preventer in the basement.