06-07-2025, 03:44 PM
|
Senior Member
|
Join Date: Feb 2025
Location: Earth
Posts: 107
Thanks: 104
Thanked 64 Times in 40 Posts
|
|
Quote:
Originally Posted by jrref
Generally, you need 20 BTU for every square foot of space in your home. The chart below can guide your BTU choice:
Home Square Footage BTU (British Thermal Unit) Tonnage
600 – 1,000 18,000 1.5
1,000 – 1,300 24,000 2
1,300 – 1,600 30,000 2.5
1,600 – 1,900 36,000 3
1,900 – 2,200 42,000 3.5
2,200 – 2,600 48,000 4
2,600 – 3,200 60,000 5
The larger your home, the higher BTU you’ll need to support your comfort. One of the most accurate ways to measure the right size AC for your home is with a Manual J calculation.
So you AC is sized correctly.
|
We're at 1967 sq feet which is 3.5 tons according to your chart. It would likely strain if we added another 300 square feet (the lanai space) for a total of 2267 which is 4 tons according to this chart.
That stated, I went to the site you referenced and it seems the year of construction (2025) is weighs more heavily than our post code (34762) so it does indeed recommend a 3 ton.
|