Talk of The Villages Florida - View Single Post - Breaker/wiring problem
View Single Post
 
Old 07-02-2025, 02:26 PM
Topspinmo's Avatar
Topspinmo Topspinmo is offline
Sage
Join Date: Dec 2012
Location: Somewhere over the rainbow
Posts: 15,113
Thanks: 7,598
Thanked 6,250 Times in 3,222 Posts
Default

Quote:
Originally Posted by Maker View Post
Ground and neutral should be tied together somewhere upstream. Seeing 5.3vac says the neutral wire is disconnected somewhere before being reaching this outlet. Likely that voltage is more like a static reading because the meter has a very high input impedance. If you put a 3-way outlet adapter in, with the tester and then your meter, I bet the voltages goes close to zero. Or to 117vac, depending on how that tester is set up. (or use a load without a ground lead)
Next step is to look at other outlets located between this one and the breaker. Check the white wires for a bad wirenut, open junction, loose white wire, etc.
Do not tie the white to the ground.
Looks like that outlet is in concrete block. Garage maybe? There could be an outlet on that circuit in the attic too.
Is the breaker tripping a GFCI ?? Power flowing from outlet hot to a device and returning via ground will trip a GFCI.

I had go somewhere and haven’t check see it 5Vs still there. The dim red light out now. I’ll Check see if I still have ghost voltage in outlet?