PDA

View Full Version : Heat Pumps


under55
09-08-2017, 07:59 AM
I think our heat pump is not large enough.

Curious while looking at all the units in the new neighborhood we moved into I noticed that Munns installs 2.5 ton units.

Sunshine installs 3 ton units. I have talked with a couple of the other owners with the 2.5 units and everyone says the same thing. The rooms the farthest from the Air Handler are harder to get cooled down. I have not had a chance to talk with the owner of a 3 ton.

When I talked with the builder he said it is all figured out differently for each house. But it seems weird that every house that has a Munns unit they are 2.5 and every house that has a 3 ton unit are Sunshine.

retiredguy123
09-08-2017, 08:19 AM
A rough rule of thumb is that you need at least a ton of a.c. for every 600 square feet of space. But, installing additional insulation in the attic will help to improve the cooling ability. Also, adding power ventilation in the attic will help.

under55
09-08-2017, 08:23 AM
Kind of not my point why is Sunshine installing 3 ton and Munns 2.5 on the same houses? These are all new homes closed on in the last couple of months all the same size.

graciegirl
09-08-2017, 08:37 AM
Kind of not my point why is Sunshine installing 3 ton and Munns 2.5 on the same houses? These are all new homes closed on in the last couple of months all the same size.

I don't know, just hope it is there on Tuesday.

THE VERY SAME HOUSE? THE SAME SIZE? ARE YOU SURE? That doesn't sound like anything the management would contract for differently.

Warranty would be the right people to consult.

Hope it is a worrisome thing on Tuesday. It pales in comparison to other things looming just now.

autumnspring
09-08-2017, 08:40 AM
Kind of not my point why is Sunshine installing 3 ton and Munns 2.5 on the same houses? These are all new homes closed on in the last couple of months all the same size.

It is all a balancing act. A major issue is removal of humidity.
A too large unit will not only cost you more to run but will run less so will not remove the humidity as well. The result is you will have a home that is too cold and too damp.

You say you have one section that does not cool well. That is a distribution problem. Remember your ducts pass through your HOT attic. You should check that first of all the vent is fully open. You should also check that your ducts are properly insulated and properly connected in your attic. Have you changed the filter?

billethkid
09-08-2017, 08:46 AM
I suspect when a heat gain/loss is done for each design the results are affected by even the slightest differences in layout.

The results are probably in a range of ratings like 2.5-3.0, etc.

Most likely a function of current inventory and experience of the different providers.

When it comes to HVAC it does not necessarily follow that more is better.

Just thinking out loud.

autumnspring
09-08-2017, 08:51 AM
Kind of not my point why is Sunshine installing 3 ton and Munns 2.5 on the same houses? These are all new homes closed on in the last couple of months all the same size.

The Villages runs a tight ship. They do use different contractors frankly to spread the business around. If they used only one, there would be only one and they would have all of us by the ........

If, you have a certain model there is a spec on what size AC the contractor must install.

If, you have an issue and it is a new home, you have a FIVE YEAR WARRANTY. Call the company that put it in.
Like anything else there are some defective units. I know someone who had the compressor, outside unit, replaced for FREE.

under55
09-08-2017, 08:53 AM
All of the above has been checked in the last couple of days. Two of the exact same house models EXACTLY THE SAME. Side by Side. Munns installs a 2.5 ton unit and Sunshine a 3 ton unit. Same thing across the street. Two exact house right next to each other. Munns unit 2.5 Sunshine 3 ton. Are you starting to get my point.

tuccillo
09-08-2017, 09:05 AM
Hopefully some HVAC folks will chime in if I deviate too far from reality. In Florida, a so-called "Manual J" computation is required. This is a heat load calculation for the house and considers a large number of different variables such as orientation of the house, the size, location, number, and quality of the windows, the wall and roof insulation, the area you live in, etc. This computation, which by the way is available on-line for your house on one of The Villages or County websites, specifies the heat load in units of BTUs/hour assuming a certain outside temperature and humidity and a desired inside temperature and humidity. Next, a duct work design must be done to make sure that a sufficient amount of airflow can be delivered to each room. When it comes to the actual equipment selection, the cooling losses with the duct work and other inefficiencies must be considered. One "ton" of AC is 12,000 BTUs/hour. A system that is factory rated for 3 tons (36,000 BTUs/hour) may not be sufficient for a house with a heat load of 36,000 BTUs/hour because of cooling losses associated with the duct work and the fact that factory ratings of cooling power may not be achievable in the field. A system factory rated at 3.5 tons may be required for a house with a Manual J calculation of 3 tons, as an example.

OK, so that is the basics. I believe you have a reasonable expectation that the variation in temperature across the house should be no more than a couple of degrees. Assuming you are seeing larger variations than this, your HVAC contractor may be able to modify the duct work to provide more air flow, and subsequent cooling, to the impacted room(s). Regarding the size of your system, I would first check out the Manual J calculation for your house. I don't recall the website but you should be able to find it with some googling. Since the orientation of your house (north/south or east/west orientation) may be different than your neighbors, the heat load calculation, and the selected equipment size, may be different. Also, keep in mind that with the mostly single zone installations and a centrally located thermostat, it can be difficult to maintain completely uniform temperatures across the house. If you have a warm room with southwest facing windows and no window coverings, maintaining a desired temperature may be difficult. Ideally, the Manual J calculation and subsequent duct work design would provide the necessary air flow for southwest facing rooms as that is part of the design process but window coverings, or lack there of, may not be accurately accounted for. I also suggest you discuss your concerns with your HVAC contractor and open a ticket with the Warranty Department. This way you will start a paper trail. Ultimately, I believe some possible rework of the duct work and/or window treatments will be your solution. I believe they are reasonably accurate about equipment sizing. Also, oversizing of the equipment is not a good thing as it may impact humidity control by having the system not run long enough. I hope this helps.





I think our heat pump is not large enough.

Curious while looking at all the units in the new neighborhood we moved into I noticed that Munns installs 2.5 ton units.

Sunshine installs 3 ton units. I have talked with a couple of the other owners with the 2.5 units and everyone says the same thing. The rooms the farthest from the Air Handler are harder to get cooled down. I have not had a chance to talk with the owner of a 3 ton.

When I talked with the builder he said it is all figured out differently for each house. But it seems weird that every house that has a Munns unit they are 2.5 and every house that has a 3 ton unit are Sunshine.

retiredguy123
09-08-2017, 09:09 AM
All of the above has been checked in the last couple of days. Two of the exact same house models EXACTLY THE SAME. Side by Side. Munns installs a 2.5 ton unit and Sunshine a 3 ton unit. Same thing across the street. Two exact house right next to each other. Munns unit 2.5 Sunshine 3 ton. Are you starting to get my point.
On my street, the 2-bedroom courtyard villas have 2.5 ton units, but the 3-bedroom villas have 3 ton units. All were installed by Munn's.

cmj1210
09-08-2017, 02:15 PM
I think our heat pump is not large enough.



Curious while looking at all the units in the new neighborhood we moved into I noticed that Munns installs 2.5 ton units.



Sunshine installs 3 ton units. I have talked with a couple of the other owners with the 2.5 units and everyone says the same thing. The rooms the farthest from the Air Handler are harder to get cooled down. I have not had a chance to talk with the owner of a 3 ton.



When I talked with the builder he said it is all figured out differently for each house. But it seems weird that every house that has a Munns unit they are 2.5 and every house that has a 3 ton unit are Sunshine.



We recently sold a Gardenia & purchased another Gardenia. The house we sold was standard with no stretches & no radiant roof barrier. My new Gardenia has stretches & a radiant roof barrier. We had a 3 ton unit in the one we sold & we now have a 2.5 ton unit in the new home. Our current home because of the radiant roof barrier, the cooling load in the house is not as great.


Sent from my iPhone using Tapatalk Pro

Bog99
09-16-2017, 11:44 AM
Munn's charged me $300+ to basically change an AC capacitor.


71466

Wiotte
09-16-2017, 11:50 AM
Munn's charged me $300+ to basically change an AC capacitor.





71466



This is the OEM Carrier dual capacitor
https://uploads.tapatalk-cdn.com/20170916/330df1bd2b277496d1c36ca3a7712831.png




Sent from my iPhone using Tapatalk

Bog99
09-16-2017, 12:04 PM
Thank you Wiotte

Sorry to original posting; I know this is off topic therefrom; to others, please continue with 2.5 ton vs. 3.0 ton units.

Meanwhile: they showed up within in an hour of my discovering the emergency, and they had the part. Should I complain to them about the size of the bill? Everyone else says "$130-ish is the going rate". Does withing-the-hour service count for more than 2x the going rate, I wonder?

Wiotte
09-16-2017, 12:08 PM
Thank you Wiotte



Sorry to original posting; I know this is off topic therefrom; to others, please continue with 2.5 ton vs. 3.0 ton units.



Meanwhile: they showed up within in an hour of my discovering the emergency, and they had the part. Should I complain to them about the size of the bill? Everyone else says "$130-ish is the going rate". Does withing-the-hour service count for more than 2x the going rate, I wonder?



Just be glad they showed up and fixed it. I'd let it go. It's high but not astronomical [emoji6]


Sent from my iPhone using Tapatalk

Bog99
09-16-2017, 12:10 PM
This is the OEM Carrier dual capacitor
https://uploads.tapatalk-cdn.com/20170916/330df1bd2b277496d1c36ca3a7712831.png




Sent from my iPhone using Tapatalk

Thank you Wiotte

Sorry to original posting; I know this is off topic therefrom; to others, please continue with 2.5 ton vs. 3.0 ton units.

Meanwhile: they showed up within in an hour of my discovering the emergency, and they had the part. Should I complain to them about the size of the bill? Everyone else says "$130-ish is the going rate". Does withing-the-hour service count for more than 2x the going rate, I wonder?

Bog99
09-16-2017, 12:17 PM
Just be glad they showed up and fixed it. I'd let it go. It's high but not astronomical [emoji6]


Sent from my iPhone using Tapatalk

I suppose -- seems like every encounter with a Villages contractor is a screwing of some kind. I new and absentee and I'm thinking "are these the abuses you have to experience and learn to deal with as a Villages newbie?"

Wiotte
09-16-2017, 12:22 PM
I suppose -- seems like every encounter with a Villages contractor is a screwing of some kind. I new and absentee and I'm thinking "are these the abuses you have to experience and learn to deal with as a Villages newbie?"



I have a list of reputable people you can deal with. I'll PM you with the list. It was given to me by my former home watch.


Sent from my iPhone using Tapatalk

Wiotte
09-16-2017, 12:25 PM
I suppose -- seems like every encounter with a Villages contractor is a screwing of some kind. I new and absentee and I'm thinking "are these the abuses you have to experience and learn to deal with as a Villages newbie?"



Sent, check your PM box


Sent from my iPhone using Tapatalk

Chatbrat
09-16-2017, 12:42 PM
the capacitor shown is a 440 v unit, wouldn't the model we would need be a 240v one ?

Wiotte
09-16-2017, 12:45 PM
the capacitor shown is a 440 v unit, wouldn't the model we would need be a 240v one ?



Up to and including 440V Also applicable for 277 & 460 single phase.


Sent from my iPhone using Tapatalk

graciegirl
09-16-2017, 01:56 PM
Always get three bids from contractors who have been recommended by someone you know who is satisfied with their service, THEN. check with Crimes Against Seniors to see that they have no misconduct.

Do not pay more than $3.00-$4.00 per linear foot for a French Drain. Nor more than fifty dollars a month for grass cutting.(We pay less than that) I trust Sunshine Air. I trust 48 Hour Blinds. I trust M&M for Downspouts, I trust Desmond Harris for dryer vent cleaning. I trust Tim Miller The Toolman for attic stairs. I trust T&D for pools and pool baths.

Others can add to this list

rjm1cc
09-16-2017, 05:16 PM
The directions of windows, trees etc and affect the heat load so two home that are alike can need different capacity.

Carl in Tampa
09-16-2017, 05:25 PM
I think our heat pump is not large enough.

Curious while looking at all the units in the new neighborhood we moved into I noticed that Munns installs 2.5 ton units.

Sunshine installs 3 ton units. I have talked with a couple of the other owners with the 2.5 units and everyone says the same thing. The rooms the farthest from the Air Handler are harder to get cooled down. I have not had a chance to talk with the owner of a 3 ton.

When I talked with the builder he said it is all figured out differently for each house. But it seems weird that every house that has a Munns unit they are 2.5 and every house that has a 3 ton unit are Sunshine.

No one has asked the obvious question.

Does your air conditioner fail to keep your house cool in summer or warm in winter?

If not....................it's all you need.

Now, if there is uneven heating or cooling distribution through the house, that is a matter of properly adjusting the vent openings in each room. That can take some time and experimentation. In very long houses there have even been cases where a booster fan installed in the air duct might help, but that is unlikely in most The Villages houses.

under55
09-16-2017, 05:37 PM
There are 10 homes on a street in The Villages. They are all Designer Homes with almost the exact square footage.

Seven of the homes Munn's installs 2.5 ton units.
The other 3 Sunshine installs 3 ton units.

In walking around several blocks all the units installed by Munn's are 2.5. Sunshine are 3 ton.

Every home with a Sunshine sticker has 3 ton. Every home with a Munn's has 2.5 ton.

Carl in Tampa
09-16-2017, 05:51 PM
There are 10 homes on a street in The Villages. They are all Designer Homes with almost the exact square footage.

Seven of the homes Munn's installs 2.5 ton units.
The other 3 Sunshine installs 3 ton units.

In walking around several blocks all the units installed by Munn's are 2.5. Sunshine are 3 ton.

Every home with a Sunshine sticker has 3 ton. Every home with a Munn's has 2.5 ton.

Just as a matter of curiosity, what is the square footage?

Wiotte
09-16-2017, 06:14 PM
There are 10 homes on a street in The Villages. They are all Designer Homes with almost the exact square footage.

Seven of the homes Munn's installs 2.5 ton units.
The other 3 Sunshine installs 3 ton units.

In walking around several blocks all the units installed by Munn's are 2.5. Sunshine are 3 ton.

Every home with a Sunshine sticker has 3 ton. Every home with a Munn's has 2.5 ton.

And your point ? :a20:

Wiotte
09-16-2017, 06:19 PM
Does the home reach heating/cooling setpoint ? If it does, don't sweat the details. We have a 2050 sq ft designer with a 2.5T unit. It reaches our summer setpoint of 73 degrees. SECO bill is less than our old home of 1900 sq ft that had a 3.0T unit. IT WORKS