PDA

View Full Version : Seco Surge Protector?


roadrnnr
06-28-2024, 02:26 PM
We just bought a new house and Seco inquired whether I wanted a Surge Protector they attach to the meter.

Anybody have one of these, are they a good idea?

I come from a state we never really worried about lightning strikes to much

Thanks

retiredguy123
06-28-2024, 02:30 PM
I don't have one. In my opinion, it is a waste of money. Also, in most cases, it won't protect your house from lightning. It is an electrical surge protector, not a lightning protector.

villagetinker
06-28-2024, 02:37 PM
We have one, the house next-door had a close in lightning strike, it did $7000 in damage, ours had no damage. Think the lightning hit a sign pole at the back of their yard, this was about 150 feet from our house. I will mention the comcast cable failed about 18 months later and in discussion with the tech, he stated that failure may have been due to the strike.
IMHO, these are effective for the close in strikes, they will do nothing for a direct strike. Also, these will not protect EXTERNAL wiring, landscape lights, pool controls, and other wiring that goes outside the house.

retiredguy123
06-28-2024, 03:00 PM
Here is what the SECO warranty says about lightning:

"Under no circumstances will MTI guarantee performance due to a lightning strike not carried down the utility power lines and through the utility transformer and then the SPD to the residence."

Bill14564
06-28-2024, 04:28 PM
Here is what the SECO warranty says about lightning:

"Under no circumstances will MTI guarantee performance due to a lightning strike not carried down the utility power lines and through the utility transformer and then the SPD to the residence."

Sure. If the strike does not travel through the protector then it cannot provide protection.

You will never know if the device works, only if it doesn’t. VT’s experience makes me glad I have one.

retiredguy123
06-28-2024, 04:40 PM
Sure. If the strike does not travel through the protector then it cannot provide protection.

You will never know if the device works, only if it doesn’t. VT’s experience makes me glad I have one.
Apparently, the lightning must also travel through the nearest transformer, which probably already has a surge protector.

Dusty_Star
06-28-2024, 05:20 PM
We just bought a new house and Seco inquired whether I wanted a Surge Protector they attach to the meter.

Anybody have one of these, are they a good idea?

I come from a state we never really worried about lightning strikes to much

Thanks

Here is a detailed discussion from last year when a house in DeLuna was struck. https://www.talkofthevillages.com/forums/villages-florida-general-discussion-73/lightning-strikes-home-deluna-342541/index4.html?highlight=surge+protection

If I may be allowed to paraphrase JRef, then lightning protection is a phased approach. Use all of them. The best is to get lightning rods. He recommends (strongly) using a certified installer & he supplies contact names.
Next up is a whole house surge protector as in the Eaton, installed by electricians at the breaker box. Next is point of use surge protectors at your electronics, computers, TVs, unfortunately most appliances nowadays have a electronic panel, ie: fridge, washer, dryer, microwave, garage door opener, etc. so all of them. Finally the SECO surge mitigator. If you have the financial resources to do all at once, then that is the answer. Otherwise, proceed as you can. Keeping the ultimate goal in mind.
The reasons are: the lightning rods protect your house & your life. The cost is the highest, several thousand dollars. But the likelihood of getting hit is relatively low. The risk is unimaginably high.
The whole house surge protector protects your major appliances. Cost moderate, & likelihood of surges greater. Risk: pretty high if you lose AC, fridge, etc.
The point of use surge protectors may help. No use in a big surge. But many tiny surges may be why your TVs, etc. just stop working someday. Worthwhile.
Seco surge mitigator helps with surges from SECOs power, but the likelihood of getting hit is in the 20% range.
JRef, please correct, amend, add on. Thank you as always.

Altavia
06-28-2024, 06:18 PM
The electrical code now requires surge protection in new homes that is intended to protect surges induced into the house wiring by a nearby lightening strike or generated inside the home. The Villages is installing this via a "Class 2" device that looks like a circuit breaker in your panel. So you may one of these all ready but the warranty is very limited.

There is an Eaton "Class 2" protector that has much higher protection capacity than the circuit breaker like device. On paper, the warranty looks much better. It that can be installed by companies like Pikes electric for about the same price as the SECO protector

[https://www.talkofthevillages.com/forums/contractors-services-91/final-week-whole-home-surge-protection-special-pricing-350976/

The SECO device is 'Class 1" designed to protect from surges on the power line, the warranty excludes most everything in the home.

For maximum protection, it's recommended to use local protectors for expensive devices like garage door openers, fridge, microwave, dishwasher, stove, HVAC, SPA, TV, WIFI, etc.

If you're a belt and suspenders person, you can use any combination or all for more protection.

Altavia
06-28-2024, 06:31 PM
Apparently, the lightning must also travel through the nearest transformer, which probably already has a surge protector.

Incorrect guess...

Altavia
06-28-2024, 06:36 PM
I don't have one. In my opinion, it is a waste of money. Also, in most cases, it won't protect your house from lightning. It is an electrical surge protector, not a lightning protector.

They do reduce risk from surges induced by lightening into the wiring in your house. Which are the most frequent cause of lightening induced damage and why protection is now required by the electrical code.

bmcgowan13
06-28-2024, 08:15 PM
Here is what the SECO warranty says about lightning:

"Under no circumstances will MTI guarantee performance due to a lightning strike not carried down the utility power lines and through the utility transformer and then the SPD to the residence."

We purchased a whole-house protector for our home in Orlando. The company installed it in the main electrical panel in the garage told me the "fuse" (could it be made of epoxy?) was only good for one strike. Most likely the equipment on that circuit would get "zapped" but the rest of the house was protected.

The way he explained it the DUKE energy protector was installed outside of the home (where the meter is) and ONLY protected from lighting coming into the house from the electrical feed from DUKE (like hitting a transformer or coming in on the overhead electrical lines). Those types of strikes are not very common as their equipment is pretty well protected.

He explained that the overwhelming majority of lighting strikes in Florida are related to ground strikes or direct home strikes. The lighting hits a pole, your eave or tree in the backyard, travels down to the ground and radiates out and then "jumps" into your house via an exterior wall outlet, metal pipe, light fixture or switch. Then it goes into your house through that circuit and into the main electrical panel and the surge will then fry all the other lines.

The protector that he installed was the same type Verizon uses on their cell phone towers. He had already installed several.

Not being an electrician or engineer it sounded good to me but I was told by several other companies that the protector from DUKE (with a monthly fee) was basically protecting *their* equipment and really only addressed a small fraction of the usual strikes.

This one is good for one shot---if we take a lightning strike that epoxy block needs to be replaced.

So far so good...

bopat
06-28-2024, 08:33 PM
I think ours is outside with the meter? I know SECO is replacing the meters at some point, will we need another when they do that?

Altavia
06-28-2024, 09:44 PM
I think ours is outside with the meter? I know SECO is replacing the meters at some point, will we need another when they do that?

The SECO protector stays.

Rwirish
06-29-2024, 05:29 AM
Nope, not one house in The Villages has one.

Can you say Lightening Capital?

rsmurano
06-29-2024, 06:00 AM
Good insurance getting the surge protection device at the meter. It costs $6 a month and if anything happens to it you call the utility. You have it done by an electrician then you call them for a large fee to come out and replace it. In the past I’ve had friends lose heating units and kitchen ranges with the new digital front ends to surges.

Also you need to protect your rg6 cable coming into your house if you have spectrum or xfinity.

MandoMan
06-29-2024, 06:05 AM
We just bought a new house and Seco inquired whether I wanted a Surge Protector they attach to the meter.

Anybody have one of these, are they a good idea?

I come from a state we never really worried about lightning strikes to much

Thanks

Your home electronics are much more likely to be fried from a power surge from a lightning strike a block away than by a direct strike. I consider the SECO surge protector money well spent. (Hey, people pay for termite contracts when we’ve had almost no termite damage here except in one small area, and they pay for electronic surveillance and ADT when we have almost no break-ins.). Note that you should also use better quality surge protectors when connecting your television and computer. The combination is well worth the money.

banjobob
06-29-2024, 06:23 AM
We just bought a new house and Seco inquired whether I wanted a Surge Protector they attach to the meter.

Anybody have one of these, are they a good idea?

I come from a state we never really worried about lightning strikes to much

Thanks
WE have one cheap insurance, although you still need surge protectors on you electronics.

ronda
06-29-2024, 06:36 AM
I don't have one. In my opinion, it is a waste of money. Also, in most cases, it won't protect your house from lightning. It is an electrical surge protector, not a lightning protector.

You are 1/2 right

Here is the deal. There are 2 different threats. 1) Lightning strikes that damage the physical structure of your home 2) Ground lightening that causes surges in the electrical system and can damage anything that's plugged in.

The surge protecter will do nothing for 1), but is designed to mitigate 2). Obviously, nothing is 100%, but I think the surge protector is worth the money. It also comes with a warranty, that if you have a surge that damages something electrical in your house, you can make a claim for reimbursement.

So, Yes I have the surge protector, and also have protectors that I plug into the outlets. Double protected.

retiredguy123
06-29-2024, 06:40 AM
You are 1/2 right

Here is the deal. There are 2 different threats. 1) Lightning strikes that damage the physical structure of your home 2) Ground lightening that causes surges in the electrical system and can damage anything that's plugged in.

The surge protecter will do nothing for 1), but is designed to mitigate 2). Obviously, nothing is 100%, but I think the surge protector is worth the money. It also comes with a warranty, that if you have a surge that damages something electrical in your house, you can make a claim for reimbursement.

So, Yes I have the surge protector, and also have protectors that I plug into the outlets. Double protected.
I would suggest that you read the SECO warranty online, especially the exclusions clause. It covers almost nothing.

Berwin
06-29-2024, 06:44 AM
People here are talking like a lightning strike is the only threat. Several years ago in Virginia where we lived, our A/C went out. The repair guy said the condenser capacitor had given out - probably because of small power spikes over the years. He said if there was a thunderstorm to turn the A/C off. I don't know how effective this strategy is but there is another consideration. Back in the 20th century, I was an IT guy. Whole-house surge suppressors were advertised as paying back their cost over several years by stopping short over-voltages and therefore the amount of power your house was using thus saving you a couple of pennies every month.

Altavia
06-29-2024, 06:54 AM
I would suggest that you read the SECO warranty online, especially the exclusions clause. It covers almost nothing.

True, but it still reduces the risk.

The Eaton warranty looks much better. Not sure if they back it up but if installed by someone like Pike, they might help if you need to submit a claim.

HORNET
06-29-2024, 06:54 AM
Like Chicken Soup, it won’t hurt!

retiredguy123
06-29-2024, 07:24 AM
Good insurance getting the surge protection device at the meter. It costs $6 a month and if anything happens to it you call the utility. You have it done by an electrician then you call them for a large fee to come out and replace it. In the past I’ve had friends lose heating units and kitchen ranges with the new digital front ends to surges.

Also you need to protect your rg6 cable coming into your house if you have spectrum or xfinity.
Note that the SECO warranty would not cover the digital panel on a kitchen range because it has a microchip, which is excluded from coverage in the exclusion clause of the warranty. It would also not cover the rg6 cable. It won't even cover regular electrical wiring or a duplex outlet that is damaged by a surge.

I think the warranty was written by a team of Philadelphia lawyers.

ronda
06-29-2024, 07:29 AM
We have one, the house next-door had a close in lightning strike, it did $7000 in damage, ours had no damage. Think the lightning hit a sign pole at the back of their yard, this was about 150 feet from our house. I will mention the comcast cable failed about 18 months later and in discussion with the tech, he stated that failure may have been due to the strike.
IMHO, these are effective for the close in strikes, they will do nothing for a direct strike. Also, these will not protect EXTERNAL wiring, landscape lights, pool controls, and other wiring that goes outside the house.

I hadn't thought about EXTERNAL wiring. That's a great point. If the ground lightening is picked up by that wiring, the surge protector will not help. Nothing is 100%. I would think lightning striking in your property is far less likely than it striking somewhere along the electrical grid serving your house. I wonder if the power co can tell the difference and not pay on warranty claims for this situation?

One thing I know that works is unplugging things. I am a snowbird. When I leave for the season, I unplug everything I can, including all appliances. So, nothing is 100%, you have to have risk mitigation strategies.

Wondering
06-29-2024, 07:51 AM
We just bought a new house and Seco inquired whether I wanted a Surge Protector they attach to the meter.

Anybody have one of these, are they a good idea?

I come from a state we never really worried about lightning strikes to much

Thanks
Get it for peace of mind. Buy it with no installation charge and warranty is for 10 years. Then replace it after ten years. Cheaper than renting it from SECO.

DonnaNi4os
06-29-2024, 08:00 AM
Yes! We are in the lightning capital of the world and surges can fry thousands of dollars of electrical appliances like your air conditioner, garage door opener, tv’s, phones, computers, refrigerator…. You get the picture. Not only do I have a whole house protector but I also have surge protectors on everything that plugs in, including in the ceiling in the garage for my opener. The more protection you have the better. And even with all of that there is no guarantee that a strong surge won’t do damage. Welcome to Florida

jrref
06-29-2024, 08:00 AM
Here is a detailed discussion from last year when a house in DeLuna was struck. https://www.talkofthevillages.com/forums/villages-florida-general-discussion-73/lightning-strikes-home-deluna-342541/index4.html?highlight=surge+protection

If I may be allowed to paraphrase JRef, then lightning protection is a phased approach. Use all of them. The best is to get lightning rods. He recommends (strongly) using a certified installer & he supplies contact names.
Next up is a whole house surge protector as in the Eaton, installed by electricians at the breaker box. Next is point of use surge protectors at your electronics, computers, TVs, unfortunately most appliances nowadays have a electronic panel, ie: fridge, washer, dryer, microwave, garage door opener, etc. so all of them. Finally the SECO surge mitigator. If you have the financial resources to do all at once, then that is the answer. Otherwise, proceed as you can. Keeping the ultimate goal in mind.
The reasons are: the lightning rods protect your house & your life. The cost is the highest, several thousand dollars. But the likelihood of getting hit is relatively low. The risk is unimaginably high.
The whole house surge protector protects your major appliances. Cost moderate, & likelihood of surges greater. Risk: pretty high if you lose AC, fridge, etc.
The point of use surge protectors may help. No use in a big surge. But many tiny surges may be why your TVs, etc. just stop working someday. Worthwhile.
Seco surge mitigator helps with surges from SECOs power, but the likelihood of getting hit is in the 20% range.
JRef, please correct, amend, add on. Thank you as always.

You summarized it very well. To add, Induced power surges, according to a Levitton study occur approximately 20% from the utility power feed and 80% from everywhere else. The Seco surge protector that they install on your meter basically is designed to stop and or reduce a power surge coming from the utility. How does this happen if the utility has lightning protection and all kinds of grounding? When lightning strikes near your home, the induced EMI pulse can couple to the utilitie's transformer and or lines creating a power surge in your home. It's also possible to get an unintended power surge from work being done on the power system or an accident knocking down a power line, etc.. The surge protection circuitry in this Type-1 device is slightly different than a Type-2 protector that is installed at your circuit breaker panel. The surge protector installed at your circuit breaker panel such as the Eaton Ultra is designed to shunt (stop) and or reduct power surges coming from the power feed from the utility AND the branch circuits connected to the circuit breaker box as well. This is why it's sometimes called a "whole house" protector. It adequately protects your appliances, HVAC and any devices where it's not easy to install a point of use surge protector. This is why the Surge Protector at your meter's warrenty does not cover any device with an electronic chip but the Eaton Ultra does. The point of use surge protectors which are you power strips, power cubes, etc., installed at your TV, computer, and other sensitive devices is your final layer of defense.

What many don't realise is power surges can also come into your home through your cable line and or your irregation system. If you have conventional cable from Xfinity or Spectrum for example, you can purchase a surge protection device that can be installed at the main splitter from Amazon. There are no protectors for the irregation system that I know of. If you have Fiber internet, then there is nothing to worry about becasue they use a non-conductive glass fiber cable coming to you house vs a copper cable.

So as discussed, surge protection is a layerd system. Personally, I would recommend getting the surge protector such as the Eaton Ultra installed by an electrician at your circuit breaker panel first along with making sure your point of use surge protectors are in place. Then when you can, either rent or purchase the Seco surge protector at the meter. For installing the Eaton Ultra call Lenhart Electric since if you mention you read this post they were giving a $100 discount on the install. I understand there might be a wait give the number of people installing this type of surge protection with all the storms we have been having recently.

There was some mention that surge protectors need to be replaced every 5 years. I'm not so sure this is necessary if you have a surge protector from a reputable company such as Eaton, Siemens, Tripp-lite, Belkin and others. As long as the lights on the protector are ON, showing a working state you should be fine as long as you have a layered surge protection system in place. The reason for this is because with a layered system, day-to-day surges that "wear down" the surge protector circuitry will be reduced by all the surge protectors vs your point of use protector handling all the surges.

As a final note, there are many Type-2 surge protection devices in the market that can be installed at your circuit breaker panel. They all work but the cost can vary a lot. The reason why I personally talk about the Eaton Ultra is because I've had a lot of personal experience with this device and the cost is reasonable. It has also been around for many years and has excellent reviews. My personal opinion is I don't believe you are getting significantly more protection with a more expensive Type-2 protector for the extra cost because their specifications are very close. The UL specifications is what you need to go by. You also have to consider if you ever have to collect on the insurance I would believe it's easier to collect from a large company such as Eaton, Siemens and other's vs a small privately owned company. Finally cost is always the final gate when implementing a layered surge protection system in your home. Most people here in the Villages want and will install the most cost effective devices vs being un-protected.

I'm working on reviewing some of the other Type-2 surge protectors such as the PSP Vortex and will get back to everyone interested on this site.

Hope this all helps.

CybrSage
06-29-2024, 08:10 AM
I had lightning strike a tree 10 feet or so from my old house in PA. I tasted the lightning as my main breaker tripped in the house. I also had an Eaton surge protector in the breaker box and it tripped as well.
No damage to anything in my house, but the large chunks of tree that blew off shredded several screens and slightly damaged my grill.
The boom was so loud I was sure it had struck the house

I replaced the Eaton, happily. Eaton is a major electrical parts company. I am very confident they would honor warranties.

I also use APC UPSs (battery backups) for my main TV and Internet router, as well as one for my desktop PC. They allow the devices to stay running after a power loss so you can gracefully turn things off, but they also have great surge protection AND they smooth out the small spikes and drops in the electric line. It is great to still have Internet access during a blackout.
APC is a great company.

roadrnnr
06-29-2024, 08:16 AM
Ok Thanks everyone
You sure educated me on this
I am gonna get the whole house protector installed and some point of appliance ones for the receptacles>

Are there ones for the outlets that are not strips?

Thanks

jrref
06-29-2024, 08:32 AM
Ok Thanks everyone
You sure educated me on this
I am gonna get the whole house protector installed and some point of appliance ones for the receptacles>

Are there ones for the outlets that are not strips?

Thanks

Yes Levitton makes them. https://www.amazon.com/Leviton-5280-W-Suppressor-Receptacle-Industrial/dp/B0006I33Y6/ref=sr_1_3?dib=eyJ2IjoiMSJ9.7-vnVPT4J9VDc5LKllWNVdQCPXCuJrfYij5KgZ0qMgyidrIN9ayM lIK-Rb7DZWqGxCE5qOSiFvkWiGoUEDeDr1CNJyJbiabnCukeZSKUIm 3ljy5FT8DcGtGXZ2fEQ2yohZh-FQEcMgD1QbKeb9vqEJI_pcn3Qk67Qjr6X3-VJH4YTlfLMnLJDztsFr00cqKdUr90kKHE5wg2HCPeF3rqYTOPA cnmrPQ8kZyqQfY7NzY.yvQPJQbVpfJN0LfE0Z-eiO4rZ-I7AVZNHAgdHK8qhBg&dib_tag=se&keywords=duplex%2Boutlet%2Bsurge%2Bprotectors&qid=1719667794&sr=8-3&th=1

For your microwave, refrigerator or dishwasher where the recepticle is not in open view you can get this protector since it has a beeper to tell you that it failed in addition to the lights.
Amazon.com (https://www.amazon.com/Leviton-7380-W-Suppressor-Receptacle-Industrial/dp/B0039UUMVA/ref=sr_1_8?dib=eyJ2IjoiMSJ9.7-vnVPT4J9VDc5LKllWNVdQCPXCuJrfYij5KgZ0qMgyidrIN9ayM lIK-Rb7DZWqGxCE5qOSiFvkWiGoUEDeDr1CNJyJbiabnCukeZSKUIm 3ljy5FT8DcGtGXZ2fEQ2yohZh-FQEcMgD1QbKeb9vqEJI_pcn3Qk67Qjr6X3-VJH4YTlfLMnLJDztsFr00cqKdUr90kKHE5wg2HCPeF3rqYTOPA cnmrPQ8kZyqQfY7NzY.yvQPJQbVpfJN0LfE0Z-eiO4rZ-I7AVZNHAgdHK8qhBg&dib_tag=se&keywords=duplex+outlet+surge+protectors&qid=1719667794&sr=8-8)

Donegalkid
06-29-2024, 08:42 AM
We have one, the house next-door had a close in lightning strike, it did $7000 in damage, ours had no damage. Think the lightning hit a sign pole at the back of their yard, this was about 150 feet from our house. I will mention the comcast cable failed about 18 months later and in discussion with the tech, he stated that failure may have been due to the strike.
IMHO, these are effective for the close in strikes, they will do nothing for a direct strike. Also, these will not protect EXTERNAL wiring, landscape lights, pool controls, and other wiring that goes outside the house.

I agree with Village Tinker (Again! Thank you for good information). We also added surge protector electrical outlets on all internal circuits supplying electrical power to major appliances. And, we have lightning rods installed proper to the electrical code. So, SECO external surge protector, internal circuit surge protectors, roof mounted rods per the code. Above was done after consulting with family electrician who knows the trade. Note: neighbor across the street has had two lightning strikes in 20 years, neighbor down the street had their house destroyed (now rebuilt) by a strike. TV is the place for lightning!

jrref
06-29-2024, 08:46 AM
I had lightning strike a tree 10 feet or so from my old house in PA. I tasted the lightning as my main breaker tripped in the house. I also had an Eaton surge protector in the breaker box and it tripped as well.
No damage to anything in my house, but the large chunks of tree that blew off shredded several screens and slightly damaged my grill.
The boom was so loud I was sure it had struck the house

I replaced the Eaton, happily. Eaton is a major electrical parts company. I am very confident they would honor warranties.

I also use APC UPSs (battery backups) for my main TV and Internet router, as well as one for my desktop PC. They allow the devices to stay running after a power loss so you can gracefully turn things off, but they also have great surge protection AND they smooth out the small spikes and drops in the electric line. It is great to still have Internet access during a blackout.
APC is a great company.
There you go!
Thanks for sharing your experience.

Singerlady
06-29-2024, 10:02 AM
We just bought a new house and Seco inquired whether I wanted a Surge Protector they attach to the meter.

Anybody have one of these, are they a good idea?

I come from a state we never really worried about lightning strikes to much

Thanks
We have one and had an indirect lightning strike 3 years ago. Almost all of our electronics were fried. We called SECO and here’s what they told us….’ The surge protector only covers damage to items with motors and compressors’. We were out of luck. And, when they do cover something, they only repair and don’t replace.
We still have ours because we’re concerned that next time we might need the protector. Hmmmmm…..

jrref
06-29-2024, 10:46 AM
We have one and had an indirect lightning strike 3 years ago. Almost all of our electronics were fried. We called SECO and here’s what they told us….’ The surge protector only covers damage to items with motors and compressors’. We were out of luck. And, when they do cover something, they only repair and don’t replace.
We still have ours because we’re concerned that next time we might need the protector. Hmmmmm…..
The reason why you had this experience is because the induced surge didn't come in through the power line so the Seco protector did nothing and will continue to do nothing if the same thing happens again.

Were the red lights on the Seco protector still ON after the strike?

philoret
06-29-2024, 02:25 PM
Repeated talks and articles report how the geography here, winds from two coasts, create the most thunderstorms and a lightning capital of the world -- two houses damaged just last week. Not only a surge protector but lightning rods are advised -- there is always some house getting damaged from a strike. Use only UL approved supplier like A1 Lightning. Houses with natural gas supply extra need because of gas lines in the attic.

jrref
06-29-2024, 02:55 PM
If you want the cadillac of this type of surge protector get this. It has status lights letting you know if its working.

https://www.homedepot.com/p/Eaton-Surge-Protection-Protects-2-Quad-Shield-Cables-CHSPCABLE/203024610?source=shoppingads&locale=en-US&srsltid=AfmBOoo_evUxNDdIBBgiV0ivM8A8u63lpqKGT5VLLM Mff9QK8_jOHUtASrE

jrref
06-29-2024, 02:58 PM
You can avoid this problem by getting Fiber internet if your area has it.

Altavia
06-29-2024, 03:24 PM
You can avoid this problem by getting Fiber internet if your area has it.

Not aware of anyone yet running fiber to the house?

Just checked new construction and they ran fiber to the post and coax from the post to the house.

mtdjed
06-29-2024, 08:00 PM
You are 1/2 right

Here is the deal. There are 2 different threats. 1) Lightning strikes that damage the physical structure of your home 2) Ground lightening that causes surges in the electrical system and can damage anything that's plugged in.

The surge protecter will do nothing for 1), but is designed to mitigate 2). Obviously, nothing is 100%, but I think the surge protector is worth the money. It also comes with a warranty, that if you have a surge that damages something electrical in your house, you can make a claim for reimbursement.

So, Yes I have the surge protector, and also have protectors that I plug into the outlets. Double protected.

I have lightning Rods, a whole house surge protector, and individual surge protectors for sensitive equipment. I have had damage three separate times. The lightning Rods, have never been contacted that I know. I doubt that any surge has been from my electrical supply lines. What I do know is that my cable line has been zapped twice and my phone line once.

The cable line surge fried the outside line requiring replacement both times. It also damaged the TV Modem requiring replacement. The last incident several years ago was a bright flash outdoors and instantaneous thunder indicating a close encounter. We immediately went outside, and found the ball on top of our flagpole about 40 feet from the house blown off and a slight bulge on the flag pole between sliding sections. we noted jagged muddy lines from the flagpole radiating toward the house and a muddy hole about 3 to 4 feet from the house and a splatter of mud on the house. The hole was where the surge met the cable. Apparently, the pole was the lightning rod. Cable had to be replaced plus some inside comcast equipment. That jagged muddy line change to a fried grass jagged line over the next several days.

Bottom line is that surge can be introduced by any conducting outside source.

retiredguy123
06-29-2024, 10:47 PM
Incorrect guess...
I assume you are saying that the transformer doesn't have a surge protector. But, why does the lightning need to travel through a transformer to be covered by the SECO warranty? As I read the warranty, if the lightning strikes the power line between the nearest transformer and your house and travels through the SECO surge protector, there is no warranty coverage. In order to get coverage, the lightning needs to actually travel through a transformer. Why?

biker1
06-29-2024, 11:03 PM
CenturyLink (aka QuantumFiber) has fiber to the house. The ONT is either in a box on the side of the house or in the low-voltage panel in the garage. I believe they started with houses south of 466A. I have had it over 10 years.

Not aware of anyone yet running fiber to the house?

Just checked new construction and they ran fiber to the post and coax from the post to the house.

Altavia
06-30-2024, 06:08 AM
I assume you are saying that the transformer doesn't have a surge protector. But, why does the lightning need to travel through a transformer to be covered by the SECO warranty? As I read the warranty, if the lightning strikes the power line between the nearest transformer and your house and travels through the SECO surge protector, there is no warranty coverage. In order to get coverage, the lightning needs to actually travel through a transformer. Why?

It can strike or be induced into the wire between the transformer and the house.

But most damage is due to the electromagnetic pulse (EMP) inducing transient voltage and current surges from the strike. Not from the power line. As others noted here, damage occurs even several homes away from the strike.

EMP Protection - How Do You Protect Your Assets from EMPs (https://lightningmaster.com/emp-protection/)


The SECO will reduce the risk from power line damage but the warranty is not very helpful for electronic devices likely to be damaged by an EMP. This is why protection is also recommended at the device.

Surge suppression was added to the national electrical code over five years ago and finally adopted by Florida this year.

ronda
06-30-2024, 07:17 AM
I would suggest that you read the SECO warranty online, especially the exclusions clause. It covers almost nothing.

Thanks for the great advice. It's been a while since I read it. There are some very important clauses in the warranty.

" Standard residential equipment is defined as "white appliances" such as HVAC, clothes washers and dryers, refrigerators, dishwashers, electric ranges and other major home appliances. If an appliance is not listed above, then the general determination for warranty coverage is that the appliance must be a motor-driven load within the residence. MTI will make the final determination. "

So home electronics and low voltage control panels (i.e., Irrigation controller) are not covered.

I also use this lug in Belkin surge suppresser, which also has a warranty.

Belkin 1-Outlet SurgeCube Portable Wall Tap with Ground & Protected Light Indicators - For Home, Office, Travel

Amazon.com (https://www.amazon.com/gp/product/B00006BBAB/ref=ppx_yo_dt_b_search_asin_title?ie=UTF8&th=1)

What can I say, we can only do so much. The rest is beyond our control.

Byte1
06-30-2024, 11:51 AM
I have one and SECO would not cover the damages when the house two down from us took a lightening strike and it caused a surge to our home through the power line. It took out our TV, DVD player, Modem and Cat6 card in my desktop computer. They said they only covered motorized equipment taken out by the surge.

dadspet
06-30-2024, 12:48 PM
I had the surge protection installed at the Box in the garage instead of the SECO outside at the meter. It was 10 years ago and can't exactly remember all the details but one was no monthly charge (12x$6? = $72/yr x 10 years - $720) and to be honest I couldn't determine the SECO solution was better. Fair disclosure > I'm a Electrical Engineer but probably don't know much more about lighting strikes than anyone else except if you get hit you have a problem. BTW I didn't like the lighting rod idea for a few reason: I wasn't crazy about attracting lighting to MY house and I didn't need any more holes in my roof or wires running around. I do tend to research things a lot- I only wish I could remember the information I learned and if you ask my wife she will verify I'm not always right.

jrref
06-30-2024, 01:27 PM
I had the surge protection installed at the Box in the garage instead of the SECO outside at the meter. It was 10 years ago and can't exactly remember all the details but one was no monthly charge (12x$6? = $72/yr x 10 years - $720) and to be honest I couldn't determine the SECO solution was better. Fair disclosure > I'm a Electrical Engineer but probably don't know much more about lighting strikes than anyone else except if you get hit you have a problem. BTW I didn't like the lighting rod idea for a few reason: I wasn't crazy about attracting lighting to MY house and I didn't need any more holes in my roof or wires running around. I do tend to research things a lot- I only wish I could remember the information I learned and if you ask my wife she will verify I'm not always right.


In many areas of the country there is no surge protector to install on the meter. In these cases installing a Type-2 such as an Eaton Ultra at the circuit breaker panel is your first line of defense from a surge coming from the power lines and from induced surges coming from the branch circuits. That said, you don't necessarily need the Type-1 proctector from Seco if you have a very good Type-2 protector at your circuit breaker panel. But here in the Villages we get so much more lightning than most of the country, adding the Seco protector can help by adding an extra layer of protection. When I live in NY, I only had the Eaton Ultra and while my neighbor who had no surge protection was hit and had damage several times, I had none.

And Lightning Rods don't attract lightning. They may get hit more if they are on a very high building or tower way above all other structures and even then they don't draw the lightning towards them. That's not how it works.

pikeselectric
07-01-2024, 08:36 AM
Hi Roadrnnr, This is Casandra at Pike's Electric. We are offering our whole home type 2 Eaton Ultra CHSPT2ULTRA for the promotional price of $515.00 installed, ending today. Here's some information on it on this Facebook video we made about it:

Log into Facebook | Facebook (https://www.facebook.com/share/v/HVedH1ssrjC2MiYX/)

Log into Facebook | Facebook (https://www.facebook.com/profile.php?id=100058747974078)

I just made a new forum about it today as well.
Hope to speak to you if it is of interest of you! 352-748-6251

pikeselectric
07-01-2024, 08:44 AM
We have one and had an indirect lightning strike 3 years ago. Almost all of our electronics were fried. We called SECO and here’s what they told us….’ The surge protector only covers damage to items with motors and compressors’. We were out of luck. And, when they do cover something, they only repair and don’t replace.
We still have ours because we’re concerned that next time we might need the protector. Hmmmmm…..

Hi Singerlady. This is sad to hear. This is why we at Pike's Electric recommend having a type 2 device installed on your home's panel, such as our Eaton Ultra CHSPT2ULTRA. We are offering it installed at $515.00. Mention you saw us on TOTV today if you call and we can get you scheduled. Here's information on its limited lifetime, $75,000 warranty: https://www.eaton.com/content/dam/eaton/products/backup-power-ups-surge-it-power-distribution/complete-home-surge-protection/surge-protection-warranty.pdf

deej012160
07-01-2024, 05:15 PM
I had read numerous posts about people experiencing electronics failures in their TV homes, so we went ahead and obtained a surge protector as proactive protection. We also have plugged in most of our electronics into small surge protectors that plug into the electrical outlets. Just my two cents...

Altavia
07-01-2024, 06:12 PM
Hi Roadrnnr, This is Casandra at Pike's Electric. We are offering our whole home type 2 Eaton Ultra CHSPT2ULTRA for the promotional price of $515.00 installed, ending today. Here's some information on it on this Facebook video we made about it:

Log into Facebook | Facebook (https://www.facebook.com/share/v/HVedH1ssrjC2MiYX/)

Log into Facebook | Facebook (https://www.facebook.com/profile.php?id=100058747974078)

I just made a new forum about it today as well.
Hope to speak to you if it is of interest of you! 352-748-6251

Nicely done Casandra!

pikeselectric
07-02-2024, 06:37 AM
Thank you so much Altavia :bigbow:

pikeselectric
07-02-2024, 06:39 AM
I had read numerous posts about people experiencing electronics failures in their TV homes, so we went ahead and obtained a surge protector as proactive protection. We also have plugged in most of our electronics into small surge protectors that plug into the electrical outlets. Just my two cents...

Hi Deej, this is a good way to locally protect electronics. I always suggest, if you are home and able, to completely unplug anything you would not want to risk surge damage to. This is the best way to prevent loss. Our Eaton Ultra CHSPT2ULTRA whole home protector has coverage for your electronics and TVs as well as your major appliances. They have a $75,000 reimbursement for damages if a surge occurs with the unit. We are here for you for any electrical needs you may have at Pike's Electric.
352-748-6251
-Casandra

jrref
07-02-2024, 09:09 AM
I had read numerous posts about people experiencing electronics failures in their TV homes, so we went ahead and obtained a surge protector as proactive protection. We also have plugged in most of our electronics into small surge protectors that plug into the electrical outlets. Just my two cents...

These "point-of-use" protectors are absolutely necessary but they can get overwhelmed with a very large power surge. This is why you really need a Primary, Type-2 surge protector installed in addition at the circuit breaker panel. This surge protector will significantly reduce and or block a large power surge so the Type-3, point-of-use surge protectors can handle the surge.

Dusty_Star
07-02-2024, 12:03 PM
These "point-of-use" protectors are absolutely necessary but they can get overwhelmed with a very large power surge. This is why you really need a Primary, Type-2 surge protector installed in addition at the circuit breaker panel. This surge protector will significantly reduce and or block a large power surge so the Type-3, point-of-use surge protectors can handle the surge.

Is it correct to say the more point-of-use surge protectors you have the better?

Altavia
07-02-2024, 01:09 PM
Is it correct to say the more point-of-use surge protectors you have the better?

Yes, especially if the device has embedded electronics as most appliances have now days contain.

CoachKandSportsguy
07-02-2024, 06:41 PM
These "point-of-use" protectors are absolutely necessary but they can get overwhelmed with a very large power surge. This is why you really need a Primary, Type-2 surge protector installed in addition at the circuit breaker panel. This surge protector will significantly reduce and or block a large power surge so the Type-3, point-of-use surge protectors can handle the surge.

Totally agree and Primary, Type-2 should be in everyone's home as well as surge protectors for the major electronics. . .

keepsake
07-02-2024, 08:09 PM
We own our place outright so we don't have to carry windstorm insurance coverage. But we do have lightning coverage in the basic homeowner policy.

jrref
07-03-2024, 06:54 AM
We own our place outright so we don't have to carry windstorm insurance coverage. But we do have lightning coverage in the basic homeowner policy.

I believe most or all policies have lightning coverage in the basic homeowners policy. The problem is first, you need to make sure your dwelling coverage it correct since many are under-insured and 2) dealing with the insurance company after a large fire resulting from a lightning strike can be a major job.

jrref
07-03-2024, 07:12 AM
Is it correct to say the more point-of-use surge protectors you have the better?

Just to review, surge protection is a layered system. That means installing a Type-2 surge protector such as the Eaton Ultra at the circuit breaker panel and Type-3 point-of-use protectors on all sensitive electronic devices such as TVs and computers. If you have cable, you should install a surge protector in the garage where the cable comes into the house.

If you can afford it, finally get the Seco surge protector which is a Type-1 at the meter but this would be the lowest priority given the Type-2 will also protect you from power surges coming from the utility.

I agree, every home here in the Villages should have a Type-2 surge protector such as the Eaton Ultra installed at the circuit breaker panel.

Pikes and Lenhart electric install these. I believe Pikes is having a sale and Lenhart will give you a discount if you tell them you heard about them here on Talk of the Villages or attended one of the Villages Lightning Study Group's talk on Lightning. I'm not sure how long these "specials" will last so I would reach out to one of these companies ASAP.

Finally, there are several other Type-2 surge protectors besides the Eaton Ultra available. I've done some preliminary research and I can say with good confidence that the specs on all of them are basically close enough to each other that the extra cost for some of them may not be worth it. Some use a gas discharge tube to extend the life of the MOV components, and some have thermally protected MOVs so they don't self sacrifice in the case of a overwhelming power surge but at of the day the extra couple hundred dollars for a Siemens or Vortex or EMP shield surgeprotector for example, over the Eaton Ultra is not buying you significant additional protection. If the Eaton Ultra fails, there is a limited life time warrenty. So all this said, given the expense, the Eaton Ultra is the most cost effective device and has been around for many years and is highly rated so everyone living here in the Villages should consider at least spending the money for this surge protector along with the Type-3 point-of-use protectors which they probably already have.

Altavia
07-03-2024, 01:10 PM
Here's a point of use option to provide protection for hard wired electrical devices such as HVAC, compressor, mini split, tankless hot water heater, pool/SPA pumps, etc.

These are devices that are also most likely to induce smaller surges into other sensitive electrical devices in your home that can degrade electronics over time.




https://a.co/d/04RV76ay

jrref
07-03-2024, 04:38 PM
Here's a point of use option to provide protection for hard wired electrical devices such as HVAC, compressor, mini split, tankless hot water heater, pool/SPA pumps, etc.

These are devices that are also most likely to induce smaller surges into other sensitive electrical devices in your home that can degrade electronics over time.




https://a.co/d/04RV76ay
Thanks for posting this. As part of the layered surge protection approach, you can also install these point-of-use protectors specifically designed for your HVAC and pool and spa systems. I have these installed at my home. What they do is if a power surge is induced into the power lines of your pool equipment for example, this protector will block it protecting the equipment and also prevent the surge from traveling back to your main circuit breaker panel and spreading to the rest of your home. It will also block any power surges created by the switching On and OFF of your HVAC compressor and pool and or spa motors, etc.

The ones that you show by Intermatic are very reasonable and work very well and you can get them on Amazon. Just they are sometimes tricky to install so an electrician can install them for you.

Altavia
07-03-2024, 07:05 PM
Thanks for posting this. As part of the layered surge protection approach, you can also install these point-of-use protectors specifically designed for your HVAC and pool and spa systems. I have these installed at my home. What they do is if a power surge is induced into the power lines of your pool equipment for example, this protector will block it protecting the equipment and also prevent the surge from traveling back to your main circuit breaker panel and spreading to the rest of your home. It will also block any power surges created by the switching On and OFF of your HVAC compressor and pool and or spa motors, etc.

The ones that you show by Intermatic are very reasonable and work very well and you can get them on Amazon. Just they are sometimes tricky to install so an electrician can install them for you.

Thanks!

If you can change a wall switch or outlet, you can probably do one of these.

But be aware the disconnect at the compressor outside also has an outlet connected to the outside GFI breaker circuit so that needs to be shut off also during an install.


I'll add surge protection devices"share" dissipation of the energy so the more you have, the better the protection.

djlnc
07-03-2024, 08:38 PM
But be aware the disconnect at the compressor outside also has an outlet connected to the outside GFI breaker circuit so that needs to be shut off also during an install.



I don't understand what you mean by this. The breaker box has a 200 amp breaker that disconnects all the circuits including the A/C.

Altavia
07-03-2024, 08:49 PM
I don't understand what you mean by this. The breaker box has a 200 amp breaker that disconnects all the circuits including the A/C.

Or you shut off the HVAC breaker and outside outlet breaker before opening the disconnect box at the HVAC.

retiredguy123
07-04-2024, 05:47 AM
I don't understand what you mean by this. The breaker box has a 200 amp breaker that disconnects all the circuits including the A/C.
True, but the HVAC shutoff located at the unit is a safety requirement so the installer can see and operate the shutoff switch where he/she is working. It ensures that someone in the house doesn't inadvertently turn on the breaker in the remote panel.

Spartan86
07-04-2024, 07:42 AM
Here's a point of use option to provide protection for hard wired electrical devices such as HVAC, compressor, mini split, tankless hot water heater, pool/SPA pumps, etc.

These are devices that are also most likely to induce smaller surges into other sensitive electrical devices in your home that can degrade electronics over time.




https://a.co/d/04RV76ay
So, are you/we saying one should add this device on A/C, mini-split, pool etc plus a breaker box solution such as the Eaton Ultra?

Altavia
07-04-2024, 09:00 AM
So, are you/we saying one should add this device on A/C, mini-split, pool etc plus a breaker box solution such as the Eaton Ultra?

Yes, these are for things direct weird that do not plug into an outlet .

Altavia
07-04-2024, 09:05 AM
True, but the HVAC shutoff located at the unit is a safety requirement so the installer can see and operate the shutoff switch where he/she is working. It ensures that someone in the house doesn't inadvertently turn on the breaker in the remote panel.

In recent construction, they also have a 120V GFI outlet under the cover of the disconnect box.

This power is still hot when pulling the disconnect and/or shutting off the breaker.

You need to also turn off the breaker that powers the outside GFI outlets before doing anything inside that box.

keepsake
07-04-2024, 09:37 AM
So much Eaton fine print to deny any benefit. You will have to prove you filed all other claims first. And 30 day window, no way other insurers will be processing that fast.

jrref
07-05-2024, 08:34 AM
So much Eaton fine print to deny any benefit. You will have to prove you filed all other claims first. And 30 day window, no way other insurers will be processing that fast.

We have talked about this a ton of times.

You don't install surge protection to collect on the insurance. The insurance is there for an extra benefit but my guess is rarely used because your homeowners is primary and if you have surge protection, you are not going to have a loss and if your do it's going to be very small.

If you read the "fine print" on surge protectors, except for the Type-1, Seco protector installed at your meter, they all read about the same. None make it easy to file a claim.

jrref
07-05-2024, 08:44 AM
So, are you/we saying one should add this device on A/C, mini-split, pool etc plus a breaker box solution such as the Eaton Ultra?

Surge protection is a layered system.

The Eaton Ultra will protect your HVAC, pool and other devices from a surge originating from a source travelling through your circuit breaker panel. But these point-of-use protectors will give you additional protection if the power surge is coupled externally at the HVAC, pool and or Spa equipment.

So yes, for the best protection I would do the following as you can afford:
1) Install the surge protector such as the Eaton Ultra at the circuit breaker panel.
2) Add any additional point-of-use protection at TVs, computer, and other sensitive equipment.
3) Install point-of-use surge protection at your HVAC, Pool and Spa equipment. These days, when this equipment is installed, surge protection is usually included.
4) Install the Seco Type-1 surge protector at the meter.

CoachKandSportsguy
07-05-2024, 08:49 AM
You don't install surge protection to collect on the insurance.

CORRECT, meaning installing a whole home surge protector, lightning rods and outlet local surge protectors is called self insured

You are personally insuring against the risk and aggravation of a random event AND the risk and aggravation of the insurance company's issues dealing with your scenario.

Same issue with home insurance and pro rated roof insurance. . the older the roof gets, the more you are self insured. . .

It's a bit more expensive living in an environment known for mother nature's disdain for building houses on farm land. .

Spartan86
07-05-2024, 05:10 PM
@jrref

Thank you for that. House had the Seco unit already and Sunshine installed a surge protector for the mini split on initial install. I’ll be adding the Eaton unit and I’ll look at adding another “at source” device at the exterior HVAC box and tankless water heater.

MrTwister
07-10-2024, 02:44 PM
It is a additional tool in your toolbox against lightning. I think ours is $5 a month on our bill. Very happy with it. We also put high end surge strips on tv’s , computers, and anything else we dont want fried. Tripplite makes good stuff. Walmart ones are just toys. You will never say to yourself you are glad you didn't get it. You will only be happy you did.

pikeselectric
07-10-2024, 02:57 PM
Hi jrref, your quote:

"Pikes and Lenhart electric install these. I believe Pikes is having a sale and Lenhart will give you a discount if you tell them you heard about them here on Talk of the Villages or attended one of the Villages Lightning Study Group's talk on Lightning. I'm not sure how long these "specials" will last so I would reach out to one of these companies ASAP." is correct :)

We are no longer in our promotion price ($515) after 7/1/24, however, we are heavily stocked with the CHSPT2ULTRA and ready to install, appointments available as early as next week. Anyone who calls me (Casandra here at Pike's) and mentions they see this post on Talk of the Villages will get a special discount with me here at Pike's Electric.
352-748-6251
My email also, if anyone would like to reach out and discuss via email: cnelson@pikeselectric.com :posting:

pikeselectric
07-10-2024, 02:58 PM
Hi Spartan, we would love to help you get the Eaton Ultra Type 2 CHSPT2ULTRA installed if you are considering it :)
- Casandra with Pike's Electric
cnelson@pikeselectric.com
352-748-6251

kp11364
07-10-2024, 06:25 PM
Rusty Nelson recently posted a video of his installation of a whole-home surge protector - his version was a PSP Products Series R Vortex. According to him, he picked it because of their $100K replacement warranty of any surge-damaged items.


https://www.youtube.com/watch?v=PzO4Ak5tVuY

jrref
07-11-2024, 07:50 AM
Rusty Nelson recently posted a video of his installation of a whole-home surge protector - his version was a PSP Products Series R Vortex. According to him, he picked it because of their $100K replacement warranty of any surge-damaged items.


https://www.youtube.com/watch?v=PzO4Ak5tVuY

Rusty did a great job with that video. Just want to point out that if you call Lenhart Electric they will give you a discount on the Eaton Ultra or the PSP Vortexx surge protectors. Both are excellent with ratings that are very similar. The Vortexx is significantly more expensive and I'm not sure it's worth the extra cost. As far as insurance. Remember, If you get damage from a power surge, your homeowners insurance is the primary and the surge protector insurance is secondary. Also to collect on the surge protector insurance the surge protector has to have failed. Most of the time if you have this level of surge protection and your home gets a surge even from a near by lightning strike, the damage, if any, will be minimal. So the point is although the surge protector insurance is good, very rarely is anyone able to use it.