I just purchased a used 2008 Club Car DS. In reading the documentation that came with it, in the Charger manual, it states:
"DANGER!"
"The charging area must be ventilated. Hydrogen level in the air must never exceed 2%. The total volume of air in the charging area must be changed 5 times per hour. Exhaust fans should be located at the highest point of the roof."

This concerns me because the brilliant designers of my brand new Courtyard Villa installed fixed windows in the garage. With the garage door down, there is no ventilation whatsoever.

Have you ever heard of a charger causing some sort of safety problem because there wasn't adequate ventilation in the garage?
  #2  
Old 03-02-2012, 04:37 PM
StarbuckSammy StarbuckSammy is offline
Senior Member
Join Date: Mar 2010
Posts: 191
Thanks: 0
Thanked 0 Times in 0 Posts
Default

I always keep my garage door up about 2-3' while I am charging.
  #3  
Old 03-02-2012, 06:46 PM
RichieLion's Avatar
RichieLion RichieLion is offline
Sage
Join Date: Jan 2009
Location: grew up in NYC and lived my adult life in Northern NJ; and now a resident of TV in Bonita
Posts: 5,997
Thanks: 0
Thanked 1 Time in 1 Post
Send a message via AIM to RichieLion
Default

Quote:
Originally Posted by TomSpasm View Post
I just purchased a used 2008 Club Car DS. In reading the documentation that came with it, in the Charger manual, it states:
"DANGER!"
"The charging area must be ventilated. Hydrogen level in the air must never exceed 2%. The total volume of air in the charging area must be changed 5 times per hour. Exhaust fans should be located at the highest point of the roof."

This concerns me because the brilliant designers of my brand new Courtyard Villa installed fixed windows in the garage. With the garage door down, there is no ventilation whatsoever.

Have you ever heard of a charger causing some sort of safety problem because there wasn't adequate ventilation in the garage?
I've never had any problem in 3 years with charging. My garage is bigger than a villa garage, though. I have an expanded 2 car garage, so I'm not sure if that's a factor.
__________________
"They that can give up essential liberty to obtain a little temporary safety deserve neither liberty nor safety." -- Benjamin Franklin, Historical Review of Pennsylvania (1759)
  #4  
Old 03-02-2012, 10:24 PM
Frank7's Avatar
Frank7 Frank7 is offline
Eternal Member
Join Date: Jan 2009
Location: Village of Caroline
Posts: 871
Thanks: 0
Thanked 0 Times in 0 Posts
Default Garage ventilation

It is always necessary for ventilation to be available when charging batteries.

I also hold a State Certified Contractores licence and have never built a House without garage steps into the house and along with vents in garage doors at the bottom. These codes were inforced for auto fumes but also apply to both gas and electric golf carts.

I suggest you make some changes and for now charge your cart with the garage door open a bit.
  #5  
Old 03-03-2012, 12:38 AM
CarGuys's Avatar
CarGuys CarGuys is offline
Gold member
Join Date: Dec 2010
Posts: 1,348
Thanks: 0
Thanked 0 Times in 0 Posts
Default Venting

Quote:
Originally Posted by Frank7 View Post
It is always necessary for ventilation to be available when charging batteries.

I also hold a State Certified Contractores licence and have never built a House without garage steps into the house and along with vents in garage doors at the bottom. These codes were inforced for auto fumes but also apply to both gas and electric golf carts.

I suggest you make some changes and for now charge your cart with the garage door open a bit.
Agree, If a battery(s) outgases for what ever reason the fumes are pretty noxious! I believe the new battery tenders or "smart chargers" will prevent this.
  #6  
Old 03-03-2012, 08:58 AM
getdul981's Avatar
getdul981 getdul981 is offline
Platinum member
Join Date: May 2010
Location: Roanoke, VA - Pennecamp - St. James
Posts: 1,929
Thanks: 0
Thanked 1 Time in 1 Post
Default

If you have stairs going to the attic in the garage, pull that down. The hydrogen gas will go out the roof vents. Also wouldn't hurt to open the garage door just a bit to let the air circulate.
__________________
Greg

A pessimist is an optimist with experience.

"In my many years I have come to a conclusion that one useless man is a shame, two is a law firm and three or more is a congress." - John Adams