Fastskiguy 10-09-2021 09:06 PM

2 Attachment(s)
Quote:

Originally Posted by Fastskiguy (Post 2015488)
I'm gonna look...

Nope, same. White wires not going anywhere the same as in the other switch. Does this help us?

Fastskiguy 10-09-2021 09:17 PM

1 Attachment(s)
Quote:

Originally Posted by Malsua (Post 2015445)
So what you've done is that you have voltage on your ground leg.

While the neutral and the ground are bonded in the panel, they are not the same. A ground should never be carrying any voltage.

Here's the directions....I have (well..."had", now I have the black wires hooked up, the other wires are just sitting there disconnected until I...er..."we"...figure this out) it hooked up like in the lower picture 3B. In my case as in the picture I put the bare ground wires together along with the white wire from the new switch. I don't have the red wire connected to anything (you can see it capped off and not connected in the second picture in the first post)

So neutral and ground on the switch were connected to ground in the wall.

Does this change anything? Does that mean I connected voltage to my ground in the house?

Fastskiguy 10-10-2021 05:25 AM

1 Attachment(s)
Quote:

Originally Posted by villagetinker (Post 2015455)
IMHO, I think you bought the wrong switch, you needed one for a TWO switch arrangement, then the instructions would have indicated what to do with the extra wires. I would eliminate the second switch and place the the motion detector switch ion the location that would provide the best operation. Other option, go back to the original switches and wiring, and replace the LIGHT blub/housing with a motion sensing unit. Then you simply leave the switch(es) in the ON position and let the motion detection control the light.
Using any light control device designed for a single switch installation on a 2 switch installation is usually asking for a lot of trouble.

You know....this is starting to make some sense. This switch on amazon has a red wire on it....just like the original switch that I removed had on it.

But it requires a neutral....which I don't (obviously) have....although there are those white wires in both boxes not connected to each other.

Here's the 3 way motion switch

https://www.amazon.com/ECOELER-Singl...99&s=hi&sr=1-4

rsmurano 10-10-2021 05:27 AM

Quote:

Originally Posted by Fastskiguy (Post 2015492)
Here's the directions....I have (well..."had", now I have the black wires hooked up, the other wires are just sitting there disconnected until I...er..."we"...figure this out) it hooked up like in the lower picture 3B. In my case as in the picture I put the bare ground wires together along with the white wire from the new switch. I don't have the red wire connected to anything (you can see it capped off and not connected in the second picture in the first post)

So neutral and ground on the switch were connected to ground in the wall.

Does this change anything? Does that mean I connected voltage to my ground in the house?

I think it’s time for an electrician to be called. You need a switch that can be used with that traveler wire. I installed a motion sensor in my old laundry room that was a 3 way switch configuration, best thing I did. You come home with your hands full and the light automatically turns on.
The other thing you have to do is program the switch once it’s installed, you set the sensitivity and length of time being on.

chenault55 10-10-2021 05:30 AM

Quote:

Originally Posted by Fastskiguy (Post 2015546)
You know....this is starting to make some sense. This switch on amazon has a red wire on it....just like the original switch that I removed had on it.

But it requires a neutral....which I don't (obviously) have....although there are those white wires in both boxes not connected to each other.

Here's the 3 way motion switch

https://www.amazon.com/ECOELER-Singl...99&s=hi&sr=1-4

We don’t know much about electrical wiring so to be safe we call an electrician.

Malsua 10-10-2021 05:53 AM

Quote:

Originally Posted by Toymeister (Post 2015475)
It's been national code for ten years, 2011 or 12. Some states required it well before that

Assuming that something was done to code is not a safe assumption.

I've been inside a lot of switch and outlet boxes in TV and, just like his, they are all covered with spackle or some other white, chalky substance.

In his picture, I see a couple whites stuffed at the back of the box but they could be not white if they are just coated with white spackle. Should there be a white in there? Definitely. Is it? Probably. Do we know for sure? No. This is why I asked.

Something I've also found in a lot of TV boxes? Grounds not attached to anything. I've found loose wires behind patched drywall. Sure, it had wire nuts on it. That's not code.

I've also found a metric ton of push in connectors on everything. Yes, they are legal. No professional electrician I've known would ever use those. "oh, but it's easier". Sure it is. It's also led to house fires and callbacks.

I've also done electric work in equipment bound for Germany and the German electricians, who are required to go through anything we've done, pull off wire nuts and install WAGOs, but those are not $1.10 electrical switches. They are high quality push in connectors rated for the load; Typically 380(it's 400/50 in Germany) 3 phase.

Malsua 10-10-2021 06:12 AM

Quote:

Originally Posted by Fastskiguy (Post 2015491)
Nope, same. White wires not going anywhere the same as in the other switch. Does this help us?

Just some basics here.

A switch typically only switches the black wire.

A 3-way has two black wires and a red wire. The red wire goes to a different switch to allow either switch to turn on or off the item.

Your motion light is a device that requires power so it needs the black and white(Hot/neutral) and also needs to be grounded(bare).

First things first, you need to wire your motion switch into a white wire. THIS MUST HAPPEN. Do not leave the white wire attached to the ground(bare) wire.

As it appears you did not get a 3-way capable motion switch you're out of luck with the red wire. Either get one or cap the red off and abandon using the other switch.

Luggage 10-10-2021 06:14 AM

Personally I would have put in a skylight

nick demis 10-10-2021 06:16 AM

Quote:

Originally Posted by Fastskiguy (Post 2015412)
OK all of you Iris owners, you know where I'm coming from! You walk in from the garage and turn on the light to the laundry room, take 2 steps, then turn it off again. On and off all day long. Well I thought...let's replace one of these switches with a motion sensing switch and all will be well with the universe.

Instructions couldn't be more simple.....black to black, bare wire to bare wire, and white to white....er....what is this pink / purple wire??!! What??

Well white to pink / purple didn't work but white and bare to bare worked fine except now there is a slight hum to the light fixture (LED) that wasn't there before.

Does any of this look remotely right? Any comments you have would be most appreciated :)

Joe

But a $5.00 plug in light sensor from Home Depot. We have several so when we get up in the middle of the night. We can go to the kitchen or bathroom without disturbing one another.

MandoMan 10-10-2021 06:21 AM

2 Attachment(s)
Quote:

Originally Posted by Malsua (Post 2015445)
So what you've done is that you have voltage on your ground leg.

While the neutral and the ground are bonded in the panel, they are not the same. A ground should never be carrying any voltage.

The problem, as I see it here, is that you've got a switch that was switching the black leg but your sensor switch needs actual voltage to work which means it needs a supply black, a supply neutral and the switched black.

The red wire is used with a 3 way switch configuration or the 3rd leg for a fan/light. It may not be connected to anything. If it goes into the same wire sheath as the switched black, it's probably up in the ceiling with a wire nut on it.

I see whites in your box, tucked away. The white wire must go to that and not to the ground. When a GFI senses voltage on a ground leg it'll trip. Code also requires that grounds do not carry any voltages and now it does. That needs to change.

This is puzzling. There should be a green ground wire coming from the switch, but I don’t see it. The bare wire coming from the switch housing is grounding the housing, but you need the green wire to ground the switch itself. A three-way switch is necessary here. This looks more like a three-way with the green ground missing than like a two way. I’ll attach Lutron directions for a 3-way switch and a 2-way. But this one is different because it’s missing the green wire. Unless this is a new model with a combined ground, in which case this IS a 3-way and should probably be connected any black to any black, any black, to any black, white from switch to red, and ground to ground. But the directions show a blue wire from the switch, not white. A white wire would never be used for a ground wire! Check the wiring diagram that came with the switch. It may be a newer model. (While I’ve wired and rewired houses I’ve owned, I’m not an electrician, so don’t trust me on this.)

butlerism 10-10-2021 06:27 AM

Hello.

Go find a plug in light with a motion detector.

Those detectors installed in a multi-way configuration is not a good application.

Typically motion detectors are end of the "branch circuit" application.
For instance I have a singular switch supplying power out to my back light, out back the motion detector turns the light on and off.

My other observation, how bad is the internal lighting in your home. During the day I never flip on lights.
All these windows and the skylight, everything is well lit.

Another fact, I shut off all the lights on the garage door opener. Why?

15 feet away outside I have a lamp pole that provides enough light in the garage, add in the headlights, no issues.

Sometimes we just have to think out of the box

rcsnr1 10-10-2021 07:21 AM

We replaced ours with a motion sensor light bulb. Goes off after 45 seconds if no activity.

JMintzer 10-10-2021 07:28 AM

Quote:

Originally Posted by Toymeister (Post 2015456)
Serious, hasn't anyone done house wiring here?

Bueller? Bueller?

I try not to. I've accidentally "let the smoke out" of too many things... :1rotfl:

Now plumbing, drywall, carpentry, tile work? I'm your guy!

ellenwelsh 10-10-2021 07:53 AM

I have an LED nightlight in there for night and a solar tube for days. I don’t think I’ve turned the light on in there for years.

jimkerr 10-10-2021 08:51 AM

A solar tree be is a good solution but for the price you’re better off with your motion sensor. I just installed one in my garage and love it.