rjn5656 05-27-2022 06:05 AM

Mitsubishi mini split
 
Looking to put a Mitsubishi Mitsubishi ceiling cassette in enclosed lanai in my Gardenia (10 x 28). One conractor recommended 1 ton unit, another 1.5 unit. Anyone with a Gardenia that has done it?

retiredguy123 05-27-2022 06:21 AM

One ton should be plenty large enough for 280 square feet, especially if the windows are double pane glass. If there is no insulation above the ceiling, I would definitely have at least six inches of blown-in insulation added.

Brwne 05-27-2022 06:34 AM

Lanai Mini Split
 
Quote:

Originally Posted by rjn5656 (Post 2099470)
Looking to put a Mitsubishi Mitsubishi ceiling cassette in enclosed lanai in my Gardenia (10 x 28). One conractor recommended 1 ton unit, another 1.5 unit. Anyone with a Gardenia that has done it?

We have a 254 sq ft, double pane enclosed lanai with additional insulation blown in. Installed in May, 2020, we went with Mitsubishi 1 ton and the ceiling cassette. We use the lanai daily, year around, and it's all working perfectly!

TrapX 05-27-2022 06:42 AM

1 ton is more than enough. Perhaps still too big.
https://learnmetrics.com/ac-tonnage-calculator

biker1 05-27-2022 06:50 AM

Go with the larger size. My Gardenia has a bigger lanai (450 sq. ft.) and a 2 ton unit. These systems have variable speed compressors. For example, mine can ramp down to 0.5 tons and I suspect it does most of the time but can ramp up when needed.


Quote:

Originally Posted by rjn5656 (Post 2099470)
Looking to put a Mitsubishi Mitsubishi ceiling cassette in enclosed lanai in my Gardenia (10 x 28). One conractor recommended 1 ton unit, another 1.5 unit. Anyone with a Gardenia that has done it?


laboutj 05-27-2022 09:15 AM

Quote:

Originally Posted by rjn5656 (Post 2099470)
Looking to put a Mitsubishi Mitsubishi ceiling cassette in enclosed lanai in my Gardenia (10 x 28). One conractor recommended 1 ton unit, another 1.5 unit. Anyone with a Gardenia that has done it?

Who have you gotten from? Wondering as we are thinking of doing the same. I have read good things on TOTV about Kalos and Munns.

GpaVader 05-27-2022 09:34 AM

I put mine in the Garage but we went with Munns, they did a great job! They were also the best price.

Happydaz 05-27-2022 10:00 AM

We had a Mitsubishi 1 ton split AC put in nine years ago in our Gardenia, 300 square foot, glassed in lanai. Works great and cools the lanai down quickly. Sometimes we turn it on in the afternoon for five hours or so. In the winter the heater works well. We had T&D install the ten heavy duty, well insulated, vinyl clad glass doors.

La lamy 05-28-2022 05:34 AM

1 Attachment(s)
I thought you meant one of these! Didn't know they made them that heavy. :icon_wink: :1rotfl:

ithos 05-28-2022 06:00 AM

Quote:

Originally Posted by biker1 (Post 2099482)
Go with the larger size. My Gardenia has a bigger lanai (450 sq. ft.) and a 2 ton unit. These systems have variable speed compressors. For example, mine can ramp down to 0.5 tons and I suspect it does most of the time but can ramp up when needed.

Very good advice. And pay up for the extended warranty if it is an option.

talonip 05-28-2022 06:45 AM

One ton is fine
 
We had 280 square ft single pain lanai. Morning sun only. One ton was fine. Even on hottest day it would get cold. We added insulation in the ceiling. As a heater it was awesome. Best thing we aver did. The lanai was our go to place all year around.

KALOS did ours. Great people.

mkjelenbaas 05-28-2022 06:53 AM

Consider Sun Kool as they are highly recommended!!

Randyj66 05-28-2022 07:00 AM

Why don't you ask them for a manual J printout? Hopefully there capable of providing that! Guessing does not work in the trade! Only in cards!
A manual J is a specific formula to calculate heat and cooling loads!
Every house is different! Too small is sometimes better than too much! A/C is more about humidity control than cooling! Without lower humidity you will never feel comfortable, just cooler.

Wildbill50 05-28-2022 07:03 AM

What are you be quoted for cost?
 
What has anyone paid for this?

retiredguy123 05-28-2022 07:12 AM

If you need 1.5 tons of cooling for a 280 square foot room, that means that you would need a 10 ton unit for an 1800 square foot house. Most 1800 square foot houses have a unit that is less than 4 tons.

jimkerr 05-28-2022 07:16 AM

We keep our sliders open 24x7 and use our mini split to also cool our family room!

mtdjed 05-28-2022 07:45 AM

Quote:

Originally Posted by rjn5656 (Post 2099470)
Looking to put a Mitsubishi Mitsubishi ceiling cassette in enclosed lanai in my Gardenia (10 x 28). One conractor recommended 1 ton unit, another 1.5 unit. Anyone with a Gardenia that has done it?

We have a 15 by 28 enclosed with double pane windows last fall and installed a 1.5 ton unit Mitsubishi 1.5 Ton GL18 20.5 SEER system. Note that the window installer recommended that we wait a year or two and experience just with the sliding doors open. At my age , I decided to invest now to enjoy the benefit. Glad I did because I can now enjoy all of the time. Without the unit on, the temp can get up to mid 80's on a 90 F plus day. I suppose I could open bedroom sliders and LR sliders to cool off more. Note we have 3 overhead fans in the sunroom and installed the unit on the house wall nearest the window side of living area. The unit has directional vanes to force airflow in proper manner and ceiling fans provide even more mixing and cooling.

Found dollar variation for unit and install not that significant to choose smaller size or lesser model (not worth any compromise after undergoing the total enclosure time, effort and cost experience). Not sure the real advantage of ceiling cassette. In my case, I finished the ceiling in Knotty Pine and with the fans, felt that I did not want to center the unit in the ceiling and thus get airflow, onto our lounging area. Also, concerned some what over any maintenance issue in the future. i.e. condensation drain line maintenance etc.

PM me if you wish.

MandoMan 05-28-2022 08:15 AM

Quote:

Originally Posted by La lamy (Post 2099956)
I thought you meant one of these! Didn't know they made them that heavy. :icon_wink: :1rotfl:

It’s not the cassette that is so heavy. It’s the music on it.

go4fpsb 05-28-2022 09:07 AM

Get a bid from Daniels HVAC in Inverness. We got three bids they were the best.

TrapX 05-28-2022 10:12 AM

There are 2 pieces to sizing.
Obtaining desired temperature is only half of the story. Run time short or long will cool temperature. Longer runtime will improve the evenness because more time to circulate. Short runtime starts to short cycle the compressor, leading to unnecessary wear.
You must also reduce humidity to feel comfortable. That happens from run time. Longer run times from a smaller unit will drop humidity most effectively. Short runtimes from an oversized unit will leave you cool and sticky. That's awful.
This is not like a car where a big engine will get things done quicker. Don't be tempted to "go a little bigger" because it's not a lot of more money. It does not scale like that. You will pay more for worse results.

snbrafford 05-28-2022 12:03 PM

How big of AC unit
 
Quote:

Originally Posted by rjn5656 (Post 2099470)
Looking to put a Mitsubishi Mitsubishi ceiling cassette in enclosed lanai in my Gardenia (10 x 28). One conractor recommended 1 ton unit, another 1.5 unit. Anyone with a Gardenia that has done it?

It doesn't matter the model of home - it's how many square feet. You can find some good information on the internets. I found -
A common rule of thumb is to assume that a standard HVAC unit can cool around 400 square feet of residential space per ton of cooling capacity. When calculating the power you need to cool your home, you can assign 12,000BTUs that need to be cooled per 400 square feet of property. So determine the square feet of you area. If answer comes to over one ton, I would round up to 1.5 as I suspect the area may not be well insulated causing heat to build up more rapidly than in "regular" rooms. Also, I assume the calculation above is for a standard eight foot ceiling. I did not see any calculation for cooling needed for cubic feet which would have been more helpful.

Multiply your cubic foot measurement by 1,027 to convert to British thermal units. For example, a 50-cubic foot room multiplied by 1,027 equals 51,350 British thermal units.
Step 3

Divide your British thermal units number by 12,000 to convert to tons. For example, a room that requires 513,500 British thermal units per hour to cool would require a 4.3 ton air conditioning system.

nancyre 05-28-2022 05:09 PM

Quote:

Originally Posted by retiredguy123 (Post 2099473)
One ton should be plenty large enough for 280 square feet, especially if the windows are double pane glass. If there is no insulation above the ceiling, I would definitely have at least six inches of blown-in insulation added.

Don't forget the baffles so that the soffits still draft

biker1 05-28-2022 05:23 PM

None of that thinking applies to these mini-splits. My Mitsubishi has a variable speed compressor and can ramp down to as low as 25% of the nominal capacity. This means it runs all the time but can ramp up as needed. It appears to run at the 25% level, as far as I can tell, most of the time. I doubt it cycles off at all. It is too bad The Villages didn't choose Carrier systems for the house with variable speed compressors. It is better for the system to run continuously at a lower compressor speed then to cycle on and off.

Quote:

Originally Posted by TrapX (Post 2100120)
There are 2 pieces to sizing.
Obtaining desired temperature is only half of the story. Run time short or long will cool temperature. Longer runtime will improve the evenness because more time to circulate. Short runtime starts to short cycle the compressor, leading to unnecessary wear.
You must also reduce humidity to feel comfortable. That happens from run time. Longer run times from a smaller unit will drop humidity most effectively. Short runtimes from an oversized unit will leave you cool and sticky. That's awful.
This is not like a car where a big engine will get things done quicker. Don't be tempted to "go a little bigger" because it's not a lot of more money. It does not scale like that. You will pay more for worse results.


frose 05-28-2022 06:08 PM

600 sq ft per ton is what is scheduled.