Chirping Smoke / CO alarms

Closed Thread
Thread Tools
  #1  
Old 01-16-2022, 07:29 AM
fcgiii fcgiii is offline
Senior Member
Join Date: Dec 2020
Posts: 130
Thanks: 2
Thanked 72 Times in 44 Posts
Default Chirping Smoke / CO alarms

On Tuesday at 2:30 AM one of my ceiling-mounted smoke and CO monitors started chirping 5 times every minute. I got a ladder and pushed the button. Two days later it repeated the event, now joined by another unit, at almost exactly the same time. Someone on this forum said replace the batteries. They are hardwired with backup batteries. I replaced them in both units. When I pushed the button they chirped then gave the five chirp salute. Ah. They recognize my effort.

This morning they started chirping again. I resisted attacking the damn things with a hammer, but did push the button to give me some rest.

I understand now that I need to replace these two as well as the other three that are chuckling away in silence waiting to torment me.

Issue is: these appear to be wired into the house current. In the electrical box there is a breaker marked low volt panel. I presume that services the alarms and the door bell.

Now, to replace these I have to climb up on a ladder, trust that my deduction about the breaker is correct, and replace these and rewire them. Or, rather, in my advanced age, hire an electrician to do this.

I assume that many of the homes in the Villages have the same system. We live in Lake Deaton.

Any suggestions before I get my hammer?
  #2  
Old 01-16-2022, 08:08 AM
Dana1963 Dana1963 is offline
Gold member
Join Date: Jan 2019
Posts: 1,295
Thanks: 3,174
Thanked 1,445 Times in 580 Posts
Default

Quote:
Originally Posted by fcgiii View Post
On Tuesday at 2:30 AM one of my ceiling-mounted smoke and CO monitors started chirping 5 times every minute. I got a ladder and pushed the button. Two days later it repeated the event, now joined by another unit, at almost exactly the same time. Someone on this forum said replace the batteries. They are hardwired with backup batteries. I replaced them in both units. When I pushed the button they chirped then gave the five chirp salute. Ah. They recognize my effort.

This morning they started chirping again. I resisted attacking the damn things with a hammer, but did push the button to give me some rest.

I understand now that I need to replace these two as well as the other three that are chuckling away in silence waiting to torment me.

Issue is: these appear to be wired into the house current. In the electrical box there is a breaker marked low volt panel. I presume that services the alarms and the door bell.

Now, to replace these I have to climb up on a ladder, trust that my deduction about the breaker is correct, and replace these and rewire them. Or, rather, in my advanced age, hire an electrician to do this.

I assume that many of the homes in the Villages have the same system. We live in Lake Deaton.

Any suggestions before I get my hammer?
Different Types of Beeps and Chirps:

It is time to replace the batteries in your carbon monoxide detector. 5 Beeps Every Minute: End of Life. This type of chirp indicates it is time to replace your carbon monoxide alarm.
My system is wited to household current tired into the master bath/closet lighting. Waiting provided a messenger circuit to active all alarms when needed
Detectors have a life of about 8 -10 years. The best deal I found to replace units is Amazon. Contractor bulk purchase Home Depot, Lowes.
I have 3 CO and 3 smoke/fire detectors.
I believe Fire Dept will replace units purchased if ladders are an issue. The service is offered Monday through Friday from 8 a.m. to 5 p.m. on a first come first serve basis by calling The Villages Public Safety Department at (352) 205-8280 during normal business hours.
  #3  
Old 01-16-2022, 08:11 AM
CWGUY CWGUY is offline
Sage
Join Date: Aug 2012
Posts: 3,879
Thanks: 4,279
Thanked 1,661 Times in 727 Posts
Default

Quote:
Originally Posted by fcgiii View Post
On Tuesday at 2:30 AM one of my ceiling-mounted smoke and CO monitors started chirping 5 times every minute. I got a ladder and pushed the button. Two days later it repeated the event, now joined by another unit, at almost exactly the same time. Someone on this forum said replace the batteries. They are hardwired with backup batteries. I replaced them in both units. When I pushed the button they chirped then gave the five chirp salute. Ah. They recognize my effort.

This morning they started chirping again. I resisted attacking the damn things with a hammer, but did push the button to give me some rest.

I understand now that I need to replace these two as well as the other three that are chuckling away in silence waiting to torment me.

Issue is: these appear to be wired into the house current. In the electrical box there is a breaker marked low volt panel. I presume that services the alarms and the door bell.

Now, to replace these I have to climb up on a ladder, trust that my deduction about the breaker is correct, and replace these and rewire them. Or, rather, in my advanced age, hire an electrician to do this.

I assume that many of the homes in the Villages have the same system. We live in Lake Deaton.

Any suggestions before I get my hammer?
Public Safety Smoke Detector Program
  #4  
Old 01-16-2022, 08:32 AM
retiredguy123 retiredguy123 is offline
Sage
Join Date: Feb 2016
Posts: 14,241
Thanks: 2,342
Thanked 13,707 Times in 5,240 Posts
Default

5 chirps means that your detector has reached the end of life, based on time. It has nothing to do with the battery. So, you need to replace all of the detectors.

I would remove the batteries, turn off a few breakers, one at a time, and press the test button on the detectors to see if the power is off. Also, the green light should be off. If that doesn't work, and you can replace the detectors with the same type of plug in (not touching the bare wires), I would feel safe doing that. But, it is not the recommended method.
  #5  
Old 01-16-2022, 08:58 AM
Malsua Malsua is offline
Veteran member
Join Date: Jun 2019
Posts: 683
Thanks: 46
Thanked 910 Times in 329 Posts
Default

Quote:
Originally Posted by fcgiii View Post
On Tuesday at 2:30 AM one of my ceiling-mounted smoke and CO monitors started chirping 5 times every minute. I got a ladder and pushed the button. Two days later it repeated the event, now joined by another unit, at almost exactly the same time. Someone on this forum said replace the batteries. They are hardwired with backup batteries. I replaced them in both units. When I pushed the button they chirped then gave the five chirp salute. Ah. They recognize my effort.

This morning they started chirping again. I resisted attacking the damn things with a hammer, but did push the button to give me some rest.

I understand now that I need to replace these two as well as the other three that are chuckling away in silence waiting to torment me.

Issue is: these appear to be wired into the house current. In the electrical box there is a breaker marked low volt panel. I presume that services the alarms and the door bell.

Now, to replace these I have to climb up on a ladder, trust that my deduction about the breaker is correct, and replace these and rewire them. Or, rather, in my advanced age, hire an electrician to do this.

I assume that many of the homes in the Villages have the same system. We live in Lake Deaton.

Any suggestions before I get my hammer?
As noted above, the detectors are end of life and need replaced.

I would only add that if they are the same brand, you can likely re-use the mounting plate and electrical plug. Meaning, you don't have to turn off the power, just unclip the AC plug from the back of the alarm. Unless the wire nuts have pulled free, there's no risk of you shocking yourself. Most just have you squeeze either side of the plug and it comes right off. It's all plastic, there's no exposed metal on the supply side, and when the plug is clear, the leads in the detector are not engergized.
  #6  
Old 01-16-2022, 09:20 AM
villagetinker's Avatar
villagetinker villagetinker is offline
Sage
Join Date: Sep 2013
Location: Village of Pinellas
Posts: 9,670
Thanks: 2
Thanked 6,151 Times in 2,249 Posts
Default

OP, most detectors actually PLUG in at the box on the wall or ceiling. If you twist the existing detector, it will come off the wall, the connector will unplug from the back of the detector. If you get the same make and model, then you simply reverse the procedure. I would strongly suggest you replace ALL of the detectors at this time. Also, the detectors outside the bedrooms are typically CO2 detectors, make sure you get the same type for these. Any handyman will be able to help you if you do not want to climb the ladder, and electrician is not required.
If you decide to change brands, you may need to change the connector, which will require the power to be turned off and will require more time to remove the original connector and install the new connector. As far as I know you cannot mix and match different detectors.
__________________
Pennsylvania, for 60+ years, most recently, Allentown, now TV.
  #7  
Old 01-16-2022, 10:17 AM
MrFlorida MrFlorida is offline
Platinum member
Join Date: Feb 2021
Posts: 1,521
Thanks: 93
Thanked 2,191 Times in 761 Posts
Default

Just so you know, even if it's hard wired, it will still chirp when the back up battery is low...
  #8  
Old 01-16-2022, 11:14 AM
SIRE1 SIRE1 is offline
Senior Member
Join Date: Oct 2013
Posts: 431
Thanks: 1
Thanked 547 Times in 174 Posts
Default

I had the same problem with my CO detector. I found the model number of the existing unit, went to ACE hardware, and bought the replacement model. (could have ordered from Amazon but it was quick and easy to get from ACE). When I looked at the existing unit on the wall, I saw that the backing plate had wires attached to contacts. So all I had to do was to unsnap the front part of the detector from the backing plate. Then inserted the front part of the newly purchased detector to the old backing plate. The contacts on the old backing plate matched the contacts on the new detector. So no wiring was required. If you are comfortable climbing a ladder, the fix to replace one of those alarms was not as difficult as it might seem. Needless to say, I was sure relieved that it turned out to be relatively easy.
  #9  
Old 01-16-2022, 11:39 AM
spk7951's Avatar
spk7951 spk7951 is offline
Gold member
Join Date: Aug 2008
Posts: 1,272
Thanks: 7
Thanked 31 Times in 18 Posts
Default

Smoke detectors should be replaced after 10yrs of use.

Most smoke detectors work best with Duracell batteries. Our house is 4 months old and one of the detectors started flashing recently. I replaced the no name battery with a Duracell and problem solved.

Another option for the smoke detectors is to replace them with 10yr lithium battery backup style detectors. With these type detector there is no need to replace the batteries every year. When the detector reaches its end of life cycle it will let you know it is time to replace it.
  #10  
Old 01-16-2022, 12:13 PM
retiredguy123 retiredguy123 is offline
Sage
Join Date: Feb 2016
Posts: 14,241
Thanks: 2,342
Thanked 13,707 Times in 5,240 Posts
Default

Quote:
Originally Posted by spk7951 View Post
Smoke detectors should be replaced after 10yrs of use.

Most smoke detectors work best with Duracell batteries. Our house is 4 months old and one of the detectors started flashing recently. I replaced the no name battery with a Duracell and problem solved.

Another option for the smoke detectors is to replace them with 10yr lithium battery backup style detectors. With these type detector there is no need to replace the batteries every year. When the detector reaches its end of life cycle it will let you know it is time to replace it.
Or, you can just replace the alkaline battery with a 10 year lithium battery. No need to replace the detector.
  #11  
Old 01-16-2022, 12:18 PM
twoplanekid's Avatar
twoplanekid twoplanekid is offline
Platinum member
Join Date: Oct 2014
Location: born Urbana,Il lived in Urbana Ohio for 65 years a house in Lake Deaton
Posts: 1,981
Thanks: 6
Thanked 690 Times in 282 Posts
Default

Quote:
Originally Posted by fcgiii View Post


I assume that many of the homes in the Villages have the same system. We live in Lake Deaton.

Any suggestions before I get my hammer?
From my thread last November, 2021 "Every unit on my street failed at about the same time"
in Lake Deaton
Every unit on my street failed at about the same time
  #12  
Old 01-16-2022, 12:19 PM
Cobh521's Avatar
Cobh521 Cobh521 is offline
Senior Member
Join Date: Mar 2013
Location: Village of Hillsborough. (Past) Gilbertsvile, PA and Philadelphia, PA
Posts: 480
Thanks: 1
Thanked 65 Times in 21 Posts
Default

No need to turn off the electric. If you purchase the same devices, look at model number on unit. You can buy them in bulk on Amazon. You do not need to remove the plates, just unplug the old unit and plug in the new unit. I changed all of mine last year.
__________________
Anne.
  #13  
Old 01-16-2022, 12:45 PM
Bilyclub's Avatar
Bilyclub Bilyclub is offline
Platinum member
Join Date: Aug 2019
Posts: 1,751
Thanks: 476
Thanked 1,203 Times in 569 Posts
Default

I prefer FireX detectors. When the First Alert detectors went bad last year I replaced them with FireX ones by changing out the connecters. A 5 minute job for each unit.
  #14  
Old 01-16-2022, 03:02 PM
Stu from NYC Stu from NYC is offline
Sage
Join Date: Feb 2020
Posts: 12,580
Thanks: 1,165
Thanked 14,043 Times in 5,334 Posts
Default

This happened to us about a year ago. Was not sure it was the detector so wound up calling fire dept.

They came out quickly and told us two detectors needed to be replaced.

Purchased new ones and a very nice young lady from fire dept came out and put them back in place when I felt uncomfortable climbing my ladder to do so.
  #15  
Old 01-16-2022, 03:29 PM
JoelJohnson JoelJohnson is offline
Veteran member
Join Date: Jun 2012
Location: Lady Lake, FL
Posts: 881
Thanks: 675
Thanked 442 Times in 205 Posts
Default

I replaced all 5 of my detectors. The plug was not compatible, so shut the power off and just replaced the plug one wire at a time (white to white, black to black and the red to the last wire, red or yellow). I used 10 year units, meaning they have a ten year built in battery. Now as I get older I won't have to worry about getting up on a latter for ten years, at which point I'll hire someone to place them then.
Closed Thread

Tags
replace, chirping, button, breaker, batteries