AeroEngRetired 01-25-2013 10:25 AM

Quote:

Originally Posted by aljetmet (Post 605838)
So are you saying my $1,500 budget for a lighting rod is a bit much?

In no way. Installing a multi-ground rod system will protect you from a lightning strike (if installed correctly). Installing extra grounding will help ground out your meter and a big plus for surge protection devices inside the home.

Ooper 01-25-2013 10:54 AM

Here is a link to the Ufer grounding system. It is commonly used in Floria or other sandy soil areas...
The Ufer Ground

gustavo 01-25-2013 01:39 PM

Quote:

Originally Posted by 2 Oldcrabs (Post 606064)
The ground rod I am talking about is for the electrical panel box. If you are having Lightning Protection installed on your roof, they will install several ground rods where the ground wire comes down from the roof. Just make sure they "meggar" the rods for 25ohms or less.

A "megger" test is a term used for megohm meter test. It is used to measure the effectiveness of insulation when exposed to a high voltage, typically 500 volts. the 25 ohms or less resistance check would be done with a regular continuity tester or if looking for really low resistance a micro ohm meter.

2 Oldcrabs 01-26-2013 07:58 AM

Ground rods
 
South of CR466a seems to have clay about 3' deep. 10 homes installed 5/8 x 8' copper clad ground rods. Neighbor is using Ham Radio and no one has tripped a breaker. TV grounding may meet the NEC code for the area, but it is not very effective!:(

Lightning 04-20-2013 08:03 PM

The ufer grounding system is for electrical safety to prevent electrical shock - and is not designed to handle an indirect and certainly not a direct lightning strike. If lightning is your concern then you should have a lightning protection system installed by a UL listed installer. Door-to-door sales installers are not UL listed so you will have no idea if the system was installed to NFPA780, the national standard on lightning. Listed installers will drive a sufficient number of ground rods to the proper depth - usually 8 ft. copper clad rods (not rebar) 2 ft below grade beyond the drip line from the roof. In some cases they may need to go as deep as 30 ft. - but thats the installers problem - not yours.

graciegirl 04-21-2013 12:08 AM

Quote:

Originally Posted by Lightning (Post 663382)
The ufer grounding system is for electrical safety to prevent electrical shock - and is not designed to handle an indirect and certainly not a direct lightning strike. If lightning is your concern then you should have a lightning protection system installed by a UL listed installer. Door-to-door sales installers are not UL listed so you will have no idea if the system was installed to NFPA780, the national standard on lightning. Listed installers will drive a sufficient number of ground rods to the proper depth - usually 8 ft. copper clad rods (not rebar) 2 ft below grade beyond the drip line from the roof. In some cases they may need to go as deep as 30 ft. - but thats the installers problem - not yours.

This man knows what he is talking about and he does not sell lightning protection and does not recommend anyone unless they are a UL listed installer..

He and his partner speak to groups here and he is an expert.

He has a column in the POA newsletter.

You can count on him for honest and helpful answers.

Fourpar 04-21-2013 04:00 PM

Quote:

Originally Posted by graciegirl (Post 663449)
This man knows what he is talking about and he does not sell lightning protection and does not recommend anyone unless they are a UL listed installer..

He and his partner speak to groups here and he is an expert.

He has a column in the POA newsletter.

You can count on him for honest and helpful answers.

...what Gracie said:BigApplause:

shcisamax 04-21-2013 04:34 PM

We have a ham radio next door and breakers were tripping all day long. Finally, after reading on here that others installed grounding rods, we suggested that to the electrical company and were "poopooed" initially but eventually they actually put in a grounding rod. No more breakers breaking! That said, I have been told separately that it really doesn't do anything for lightening and you would have to put in a lot of them and very deep. And it isn't worth it.
I really do not understand anything about electricity and I don't want to.; I have to understand far too many other things. My brain's hard drive has just so much space and I try to prioritize what I really do need to know. So I am just repeating what I have been told and what I know works for our breakers issue.