ronda |
07-01-2024 06:11 AM |
Fla/rla
Quote:
Originally Posted by Altavia
(Post 2345889)
What's the stall current of that motor?
Stall current will be significantly higher. This can happen of the screen jams, operating in higher winds or when the tracks need cleaning/lubricating.
If the motor's shaft is prevented from turning, no eddy currents are created (the armature must be moving in the magnetic field). The only limit to the current flow is the Series Resistance of the windings in the motor.
|
Yes, there are 2 current draws Full Load Amps (FLA)/Starting current and Running Load Amps (RLA). Getting both numbers would be great, but the point I was making was don't assume you need a new circuit. There are motors that draw <2 amps that power big screens. As far as FLA is concerned, it is often not listed for small motors under reasonable loads because the difference between RLA and FLA is negligible. For a 1.6A motor I would expect this to be the case, but unless we have the data, we can't say for sure.
Bottom line. Don't assume you need a new ckt. Also, you will likely run only 1 motor at a time, so you don't need to add the 3 motors specs together. IMHO, from what I know, without knowing the specs of these specific motors, I think there is a very good chance a separate ckt is not warranted. It's worth the effort to get the specs on the motors.
|