  #16  
Old 03-29-2019, 12:17 PM
photo1902 photo1902 is offline
Sage
Join Date: Nov 2014
Posts: 3,214
Thanks: 1,607
Thanked 1,745 Times in 706 Posts
Default

Quote:
Originally Posted by rexxfan View Post
I agree that if I removed the duct, the water would show up elsewhere, but I wouldn't go so far as saying the duct has nothing to do with the problem. I think it is whats ferrying the water to my laundry room ceiling. But that's the engineer in me being picayune, please forgive me for that ;-)
--
bc
You'd just have a leak in a different part of the house
  #17  
Old 03-29-2019, 12:21 PM
rexxfan rexxfan is offline
Senior Member
Join Date: Mar 2015
Posts: 393
Thanks: 2
Thanked 4 Times in 3 Posts
Default

Quote:
Originally Posted by photo1902 View Post
You'd just have a leak in a different part of the house
Agreed.
--
bc
  #18  
Old 03-29-2019, 12:25 PM
photo1902 photo1902 is offline
Sage
Join Date: Nov 2014
Posts: 3,214
Thanks: 1,607
Thanked 1,745 Times in 706 Posts
Default

Quote:
Originally Posted by rexxfan View Post
Agreed.
--
bc
Sounds like you'll get it fixed. Good luck, and stay dry
  #19  
Old 03-29-2019, 12:28 PM
villagetinker's Avatar
villagetinker villagetinker is offline
Sage
Join Date: Sep 2013
Location: Village of Pinellas
Posts: 11,060
Thanks: 3
Thanked 8,145 Times in 2,968 Posts
Default

OK, here is a real "out there" idea, what if there is a leak on one of the round roof vents, and the previous owner installed this tubing as a drain? Who knows, maybe they had a bucket at the other end of the vent! You should be able to test this idea with a volunteer and a hose. Go up in the attic with a really good flashlight, and have your volunteer aim the hose to rain on the vents, do not spray directly on them spray above and let the water fall on them like rain. Then look in the attic for water dripping.

Good luck, hope this helps.
__________________
Pennsylvania, for 60+ years, most recently, Allentown, now TV.
  #20  
Old 03-29-2019, 12:52 PM
rexxfan rexxfan is offline
Senior Member
Join Date: Mar 2015
Posts: 393
Thanks: 2
Thanked 4 Times in 3 Posts
Default

Interesting thought but beyond my capabilities to test. My duct theory seems possible, but I'll admit, a bit unlikely. It seems there ought to be a simpler explanation, but I just can't come up with one. As an aside, how are gas hot water heaters supposed to be vented, anyway? Is it even possible that it what the duct is for?
--
bc
  #21  
Old 03-29-2019, 12:57 PM
photo1902 photo1902 is offline
Sage
Join Date: Nov 2014
Posts: 3,214
Thanks: 1,607
Thanked 1,745 Times in 706 Posts
Default

Quote:
Originally Posted by rexxfan View Post
Interesting thought but beyond my capabilities to test. My duct theory seems possible, but I'll admit, a bit unlikely. It seems there ought to be a simpler explanation, but I just can't come up with one. As an aside, how are gas hot water heaters supposed to be vented, anyway? Is it even possible that it what the duct is for?
--
bc
Electric HW heaters are not vented. Natural Gas HW heaters are generally vented by a rigid vent pipe through the roof. It depends on the layout of your house, but as a rule, this is the norm. Tankless HW heaters require a larger diameter vent than standard tanks.
  #22  
Old 03-29-2019, 01:01 PM
rexxfan rexxfan is offline
Senior Member
Join Date: Mar 2015
Posts: 393
Thanks: 2
Thanked 4 Times in 3 Posts
Default

Not to belabor this, but I just took a much closer look at the duct in question and I now believe it is the venting duct for our gas furnace and not for the water heater. The two are fairly close together in the garage and there's lots of blown-in insulation in the attic covering everything so it was difficult to see exactly where the duct ended. The duct coming out of the furnace also looks like the right diameter, whereas the vent from the water heater is narrower and does appear to go straight up (we have gas for the dryer and heat so the now missing water heater was in all likelihood gas as well).
--
bc
  #23  
Old 03-29-2019, 03:04 PM
Topspinmo's Avatar
Topspinmo Topspinmo is offline
Sage
Join Date: Dec 2012
Location: Somewhere over the rainbow
Posts: 15,101
Thanks: 7,589
Thanked 6,239 Times in 3,215 Posts
Default

I would just look in the attic the next heavy rain storm and see if you can see where the water coming from. Even after the heavy rain you should see wetness. Especially how it’s getting down into the wash room.
  #24  
Old 03-29-2019, 03:43 PM
rexxfan rexxfan is offline
Senior Member
Join Date: Mar 2015
Posts: 393
Thanks: 2
Thanked 4 Times in 3 Posts
Default

Quote:
Originally Posted by Topspinmo View Post
I would just look in the attic the next heavy rain storm and see if you can see where the water coming from. Even after the heavy rain you should see wetness. Especially how it’s getting down into the wash room.
I'll do that the next time that happens in the daytime. I'm not really a get up in the middle of the night person.
--
bc
  #25  
Old 03-29-2019, 04:21 PM
rexxfan rexxfan is offline
Senior Member
Join Date: Mar 2015
Posts: 393
Thanks: 2
Thanked 4 Times in 3 Posts
Default

Quote:
Originally Posted by rexxfan View Post
Not to belabor this, but I just took a much closer look at the duct in question and I now believe it is the venting duct for our gas furnace and not for the water heater.
One other question occurred to me. How are vents for gas furnaces supposed to be done, anyway?
--
bc

Last edited by rexxfan; 03-29-2019 at 04:40 PM.
  #26  
Old 03-29-2019, 06:08 PM
rexxfan rexxfan is offline
Senior Member
Join Date: Mar 2015
Posts: 393
Thanks: 2
Thanked 4 Times in 3 Posts
Default

Ok, nevermind about the furnace questions. I braved the attic one more time and had a much longer look at everything and its clear now the duct I was referring to is from the master bathroom, probably the exhaust fan vent.

I came to that conclusion after I observed that there's another identical duct at the other side of the house where the guest bath is that leads up to the same area. I simply hadn't noticed it before. I've attached a picture. Interestingly, the duct for the guest bath runs all the way up into the space just below the circular vent whereas the one for the master bath does not, it is just hanging in space several feet below. That should probably be fixed, but I can't imagine how anyone would get up in there to do that, especially with all the blown in insulation lying about. The master bath duct does pass over the area above the laundry ceiling and the place where the two sections of it is joined is right there, so it could still be involved I suppose.

On the other hand I also noticed this time that there's a large metal pipe in roughly the same area that leads up to the roof. It is the topmost gooseneck vent in the original picture (the lower one being the dryer vent). I'm not sure what that could be for. Could it be for the kitchen oven? That's right on the other side of the laundry room wall. I'm fairly certain that the roofer who was here in January worked on that area already, but perhaps it needs more attention. Maybe the vent just needs to be replaced. Upon further reflection, this seems somewhat more likely than the somewhat far-fetched master bath duct theory.

Though I was an engineer, I'm not the handyman type (bet you couldn't tell ).

We'll see what they say next week. Thanks for bearing with me ...
--
bc

P.S. For the record, the second and third pictures are of the actual leak and the water on the floor after the storm earlier in the week. It's clearly not a huge leak, but has to be fixed regardless.
Attached Thumbnails
The Villages Florida: Click image for larger version

Name:	IMG_20190329_182830.jpg
Views:	211
Size:	57.0 KB
ID:	79092   The Villages Florida: Click image for larger version

Name:	MVIMG_20190327_091841.jpg
Views:	175
Size:	79.0 KB
ID:	79093   The Villages Florida: Click image for larger version

Name:	MVIMG_20190327_091829.jpg
Views:	165
Size:	62.0 KB
ID:	79094  

Last edited by rexxfan; 03-29-2019 at 06:16 PM.
  #27  
Old 03-31-2019, 05:07 PM
CFrance's Avatar
CFrance CFrance is offline
Sage
Join Date: Dec 2011
Location: Tamarind Grove/Monpazier, France
Posts: 14,705
Thanks: 390
Thanked 2,131 Times in 877 Posts
Default

Quote:
Originally Posted by rjm1cc View Post
My guess is that water is getting in the duck through the roof vent. I had this problem and we changed the angle of the vents exhaust on the roof and that worked.

If the vent is not use let it drain into a dish pan at the point it leaks until you figure out the answer.
Ditto in our designer (when new). It took a year of roofer vs plumber arguments, but finally warranty stepped in and made someone come out and fix it. The vent angle needed to be changed. That solved the problem.
__________________
It's harder to hate close up.
  #28  
Old 03-31-2019, 05:28 PM
retiredguy123 retiredguy123 is offline
Sage
Join Date: Feb 2016
Posts: 17,359
Thanks: 3,037
Thanked 16,561 Times in 6,533 Posts
Default

Quote:
Originally Posted by rexxfan View Post
Ok, nevermind about the furnace questions. I braved the attic one more time and had a much longer look at everything and its clear now the duct I was referring to is from the master bathroom, probably the exhaust fan vent.

I came to that conclusion after I observed that there's another identical duct at the other side of the house where the guest bath is that leads up to the same area. I simply hadn't noticed it before. I've attached a picture. Interestingly, the duct for the guest bath runs all the way up into the space just below the circular vent whereas the one for the master bath does not, it is just hanging in space several feet below. That should probably be fixed, but I can't imagine how anyone would get up in there to do that, especially with all the blown in insulation lying about. The master bath duct does pass over the area above the laundry ceiling and the place where the two sections of it is joined is right there, so it could still be involved I suppose.

On the other hand I also noticed this time that there's a large metal pipe in roughly the same area that leads up to the roof. It is the topmost gooseneck vent in the original picture (the lower one being the dryer vent). I'm not sure what that could be for. Could it be for the kitchen oven? That's right on the other side of the laundry room wall. I'm fairly certain that the roofer who was here in January worked on that area already, but perhaps it needs more attention. Maybe the vent just needs to be replaced. Upon further reflection, this seems somewhat more likely than the somewhat far-fetched master bath duct theory.

Though I was an engineer, I'm not the handyman type (bet you couldn't tell ).

We'll see what they say next week. Thanks for bearing with me ...
--
bc

P.S. For the record, the second and third pictures are of the actual leak and the water on the floor after the storm earlier in the week. It's clearly not a huge leak, but has to be fixed regardless.
It looks like the builder ran the two bathroom exhaust ducts to the area just under the roof vents. This is probably okay, but, In the newer houses, they run the bathroom vent to the outside soffit and connect them to a hole that they cut into the soffit. I have even seen older houses that just vent the bathrooms into the attic space, and depend on evaporation to eliminate the moisture. But, it could be that your master bath duct has a low point above the laundry room, and the ceiling leak could be just an accumulation of moisture in the duct from the master bathroom exhaust fan that runs down to the low point and creates a leak. If that is the case, then you need to eliminate the low point by possibly installing a hanger to lift up the duct. This is just my opinion about what could be happening. Another solution could be to reroute the master bath duct to the nearest soffit location with hopefully a shorter run. Good luck.

Last edited by retiredguy123; 03-31-2019 at 05:37 PM.
  #29  
Old 03-31-2019, 05:52 PM
retiredguy123 retiredguy123 is offline
Sage
Join Date: Feb 2016
Posts: 17,359
Thanks: 3,037
Thanked 16,561 Times in 6,533 Posts
Default

One other point is that, if the bathroom exhaust duct is a long run, then the exhaust fan may not be strong enough to push the damp air to the end of the duct. In that case, all of the moisture from the bathroom will stay in the duct and run to the low point. This problem could be worse when it rains because of the increase in humidity in the attic.

Last edited by retiredguy123; 03-31-2019 at 06:04 PM.
  #30  
Old 03-31-2019, 11:07 PM
Topspinmo's Avatar
Topspinmo Topspinmo is offline
Sage
Join Date: Dec 2012
Location: Somewhere over the rainbow
Posts: 15,101
Thanks: 7,589
Thanked 6,239 Times in 3,215 Posts
Default

The bathroom ceiling fans ducts are probably venting the the odors to the attic when you turn the fan on, I doubt the are attached to anything? In older home they don’t have ducts in attic the just vent up there.