Pipe dope around the threads is also acceptable.
  #17  
Old 05-18-2021, 07:10 AM
villagetinker's Avatar
villagetinker villagetinker is offline
Sage
Join Date: Sep 2013
Location: Village of Pinellas
Posts: 9,677
Thanks: 2
Thanked 6,157 Times in 2,251 Posts
Default

Lowe's, Home Depot, and I believe ACE all see water pressure gauges which you can screw on to a hose bib to read your normal house water pressure. Then you may need to borrow an air compressor and a tire gauge. You will find a shrader valve (looks like a tire valve) on the top of the new expansion tank. Connect the compressor tire fill adapter for a few seconds and the check the pressure in the tank until you get to your measured water pressure, then install.
__________________
Pennsylvania, for 60+ years, most recently, Allentown, now TV.
  #18  
Old 05-18-2021, 07:15 AM
DangeloInspections's Avatar
DangeloInspections DangeloInspections is offline
TOTV SPONSOR
Join Date: Oct 2012
Posts: 723
Thanks: 14
Thanked 282 Times in 95 Posts
Default

Quote:
Originally Posted by Tom52 View Post
Thanks for the information, so if replacing an expansion tank, should the tank be charged to 60 psi or 40 psi? I don't see an easy way to determine the system pressure to be able to match it in the expansion tank.
In The Villages your water pressure varies. We check this on every inspection. You can use a pressure gauge on one of your hose bibs.
Most of The Villages around the middle and upper part the water pressure is typically around 50 psi.
In the newer areas, (like Fenney, DeSoto, etc.), it is about 70 psi. In the newest areas, like Bradford, Chitty Chatty, etc it is a bit closer to 60 psi.

Hope this helps!
__________________
Florida licensed Home Inspector #HI688. (352) 250-7818
  #19  
Old 05-18-2021, 07:36 AM
PompeyKing PompeyKing is offline
Member
Join Date: Apr 2020
Posts: 46
Thanks: 130
Thanked 85 Times in 15 Posts
Default

Good advice, or as I did, call your brother-in-law!!
  #20  
Old 05-18-2021, 07:41 AM
Brad-tv Brad-tv is offline
Senior Member
Join Date: Mar 2016
Posts: 173
Thanks: 1
Thanked 55 Times in 38 Posts
Default

Quote:
Originally Posted by Tom52 View Post
Thanks for the information, so if replacing an expansion tank, should the tank be charged to 60 psi or 40 psi? I don't see an easy way to determine the system pressure to be able to match it in the expansion tank.

As Frank said you can put a pressure gauge on your hose bib and you can increase the pressure in the expansion tank with a compressor or go down to a gas station and try to match or set just below your house pressure reading.

And if you have someone replace the tank for you make sure they set the tank pressure correct during installation.
  #21  
Old 05-18-2021, 07:43 AM
DangeloInspections's Avatar
DangeloInspections DangeloInspections is offline
TOTV SPONSOR
Join Date: Oct 2012
Posts: 723
Thanks: 14
Thanked 282 Times in 95 Posts
Default

Quote:
Originally Posted by PompeyKing View Post
Good advice, or as I did, call your brother-in-law!!
. I'm thinking that you are referring to someone else, as I only have one brother in law, who is a fiber optic installer 1300 miles away....lol.
__________________
Florida licensed Home Inspector #HI688. (352) 250-7818
  #22  
Old 05-18-2021, 08:19 AM
HJBeck's Avatar
HJBeck HJBeck is offline
Senior Member
Join Date: Jan 2020
Location: The Villages
Posts: 167
Thanks: 6
Thanked 57 Times in 40 Posts
Default

I've found it easy to check by turning off the main water supply valve to the house. If the water still runs out of any faucet for 5-10 seconds when you turn one on the expension tank is working.
  #23  
Old 05-18-2021, 10:56 AM
Michigan Farmer Michigan Farmer is offline
Senior Member
Join Date: Nov 2014
Posts: 136
Thanks: 0
Thanked 105 Times in 55 Posts
Default expansion tank

Quote:
Originally Posted by dewilson58 View Post
Google is your friend
Tank is located above the hot water heater. There is a bladder inn the middle of the tank, the bottom full of water, the top full of air. If the top sounds solid when you strike it with your finger nail the bladder has failed. If it sounds hollow it's fine. For now.
  #24  
Old 05-18-2021, 11:23 AM
Brad-tv Brad-tv is offline
Senior Member
Join Date: Mar 2016
Posts: 173
Thanks: 1
Thanked 55 Times in 38 Posts
Default

Quote:
Originally Posted by Michigan Farmer View Post
Tank is located above the hot water heater. There is a bladder inn the middle of the tank, the bottom full of water, the top full of air. If the top sounds solid when you strike it with your finger nail the bladder has failed. If it sounds hollow it's fine. For now.

Sounding hollow is ok but that’s only the first test.
The next step is to take a tire gauge and check the pressure in the tank and make sure it’s close to your house pressure. If the pressure is low or zero the tank needs to be replaced. There is a valve at the top of the tank underneath a cap and you can check the pressure.
If the tank is mounted so close to the ceiling that you can’t get the tire gauge on it then you can’t accurately determine if the tank is functional.
I have seen many hollow sounding tanks that had little or no pressure in them.

I have seen only a small percentage of tanks that tested good after 5 years. Keep in mind if the tank fails (and it will eventually )it can cause damage to your hot water tank, damage to your valves in plumbing fixtures, joints in supply pipes and major leaks.
Check those tanks and replace them if there old!!
  #25  
Old 05-18-2021, 12:44 PM
retiredguy123 retiredguy123 is offline
Sage
Join Date: Feb 2016
Posts: 14,259
Thanks: 2,348
Thanked 13,739 Times in 5,253 Posts
Default

Quote:
Originally Posted by Brad-tv View Post
As Frank said you can put a pressure gauge on your hose bib and you can increase the pressure in the expansion tank with a compressor or go down to a gas station and try to match or set just below your house pressure reading.

And if you have someone replace the tank for you make sure they set the tank pressure correct during installation.
You can also use a regular bicycle pump to pressurize the expansion tank.
  #26  
Old 05-18-2021, 04:03 PM
NoMoSno NoMoSno is offline
Gold member
Join Date: Mar 2013
Posts: 1,280
Thanks: 180
Thanked 344 Times in 216 Posts
Default

Quote:
Originally Posted by Brad-tv View Post
Sounding hollow is ok but that’s only the first test.
The next step is to take a tire gauge and check the pressure in the tank and make sure it’s close to your house pressure. If the pressure is low or zero the tank needs to be replaced. There is a valve at the top of the tank underneath a cap and you can check the pressure.
If the tank is mounted so close to the ceiling that you can’t get the tire gauge on it then you can’t accurately determine if the tank is functional.
I have seen many hollow sounding tanks that had little or no pressure in them.

I have seen only a small percentage of tanks that tested good after 5 years. Keep in mind if the tank fails (and it will eventually )it can cause damage to your hot water tank, damage to your valves in plumbing fixtures, joints in supply pipes and major leaks.
Check those tanks and replace them if there old!!
One of my homes has a 21 year old HW heater.
Never had an expansion tank.
Never had any issues you speak of in 21 years.
  #27  
Old 05-18-2021, 05:05 PM
Brad-tv Brad-tv is offline
Senior Member
Join Date: Mar 2016
Posts: 173
Thanks: 1
Thanked 55 Times in 38 Posts
Default

Yes
Not all homes have them
In that case they have a Thermal Expansion Valve . I believe around 2000 all homes started using them here in the villages unless you have a tankless water heater. I was told by a local plumbing company here that it’s now Florida Code and all homes require a expansion tank.
So most homes north of 466 do not have expansion tanks. Up north we never had expansion tanks either.
  #28  
Old 05-18-2021, 05:07 PM
Brad-tv Brad-tv is offline
Senior Member
Join Date: Mar 2016
Posts: 173
Thanks: 1
Thanked 55 Times in 38 Posts
Default

BTW
Thermal expansion valves can fail and can raise the pressure in your pipes also
  #29  
Old 05-18-2021, 05:07 PM
dewilson58's Avatar
dewilson58 dewilson58 is offline
Sage
Join Date: May 2013
Location: South of 466a, if you don't like me.......I live in Orlando.
Posts: 11,597
Thanks: 851
Thanked 9,778 Times in 3,645 Posts
Default

Or call Mike Scott Plumbing.
__________________
Identifying as Mr. Helpful
  #30  
Old 05-19-2021, 08:57 AM
davidh0430 davidh0430 is offline
Junior Member
Join Date: Feb 2010
Posts: 2
Thanks: 0
Thanked 0 Times in 0 Posts
Default

How did you know the Blatter was bad? I have a slight noise in the master bathroom when the water is running anywhere in the house. Dave