Default Unsafe at any speed electrician

Just had our AFCI breakers swapped out last week. I cringed when I observed him pop out the old breaker then use a cordless drill to both unscrew the hot and neutral leads and then install the new breakers still using the drill. The drill clutch was on full drill, no slip. I questioned him on his unique technique. He told me that he knows his drill and how would I do it. Told him by hand both for safety and workmanship reasons. He didn't agree, he knows his drill. Never in my 45 year working career have I observed any electrician do something so stupid. Not only could he have over tightened the screws, he may also have slipped with his drill and landed straight into the buss bar. Is this a Florida thing or what ?
  #2  
Old 01-04-2016, 02:14 PM
karostay's Avatar
karostay karostay is offline
Sage
Join Date: Sep 2011
Location: Conn/Maine /
Posts: 2,794
Thanks: 134
Thanked 1,349 Times in 521 Posts
Default

Quote:
Originally Posted by RickeyD View Post
Just had our AFCI breakers swapped out last week. I cringed when I observed him pop out the old breaker then use a cordless drill to both unscrew the hot and neutral leads and then install the new breakers still using the drill. The drill clutch was on full drill, no slip. I questioned him on his unique technique. He told me that he knows his drill and how would I do it. Told him by hand both for safety and workmanship reasons. He didn't agree, he knows his drill. Never in my 45 year working career have I observed any electrician do something so stupid. Not only could he have over tightened the screws, he may also have slipped with his drill and landed straight into the buss bar. Is this a Florida thing or what ?
Now go and check using a screw driver the screws in the hinges on your homes doors
You'll be surpised how many were stripped when they were origionaly installed by the contractor using a 18 volt cordless
__________________
Don't take life Too Serious ..It isn't permanent
  #3  
Old 01-04-2016, 02:17 PM
RickeyD's Avatar
RickeyD RickeyD is offline
Soaring Eagle member
Join Date: Sep 2014
Posts: 2,404
Thanks: 0
Thanked 5 Times in 5 Posts
Default

Quote:
Originally Posted by karostay View Post
Now go and check using a screw driver the screws in the hinges on your homes doors

You'll be surpised how many were stripped when they were origionaly installed by the contractor using a 18 volt cordless

Using a drill for wood is understandable and common practice. But a circuit breaker ?
  #4  
Old 01-04-2016, 02:22 PM
Chatbrat Chatbrat is offline
Sage
Join Date: Sep 2014
Posts: 4,410
Thanks: 0
Thanked 987 Times in 384 Posts
Default

The the screws on newer circuit breakers are designed for square drive heads-also the breakers are designed for certain torque settings--call the company, speak to his supervisor, I really doubt he knows the true torque settings-When I was in business I had my employees use Milwaukee electric screw drivers.
  #5  
Old 01-04-2016, 02:23 PM
chuckinca's Avatar
chuckinca chuckinca is offline
Sage
Join Date: Aug 2007
Posts: 4,904
Thanks: 0
Thanked 2 Times in 2 Posts
Default

All of our interior plastic electrical box plates are deformed because the installer(s) tightened the screws too much.

.
__________________
Da Chicago So Side; The Village of Park Forest, IL; 3/7 Cav, 3rd Inf Div, Schweinfurt, Ger 65-66; MACV J12 Saigon 66-67; San Leandro, Hayward & Union City, CA (San Francisco East Bay Area) GO DUBS ! (aka W's)
  #6  
Old 01-04-2016, 02:26 PM
Villager Joyce Villager Joyce is offline
Soaring Eagle member
Join Date: Aug 2013
Location: The Villages
Posts: 2,003
Thanks: 0
Thanked 6 Times in 6 Posts
Default

What makes you suggest it is a Florida thing? I haven't had a Floridian do one thing in our house. Everyone is a retired "whatever" from New York or New Jersey.
__________________
When all else fails, take a nap
Carrie Sue Day Snelgrove
  #7  
Old 01-04-2016, 02:27 PM
RickeyD's Avatar
RickeyD RickeyD is offline
Soaring Eagle member
Join Date: Sep 2014
Posts: 2,404
Thanks: 0
Thanked 5 Times in 5 Posts
Default

Quote:
Originally Posted by Villager Joyce View Post
What makes you suggest it is a Florida thing? I haven't had a Floridian do one thing in our house. Everyone is a retired "whatever" from New York or New Jersey.

It was a warranty issue, otherwise I would have done it myself. The service electrician was a local.
  #8  
Old 01-04-2016, 02:32 PM
Chatbrat Chatbrat is offline
Sage
Join Date: Sep 2014
Posts: 4,410
Thanks: 0
Thanked 987 Times in 384 Posts
Default

Eaton says 28-32 inch/pounds for the wire size that would attached to a 20 amp AFCI
  #9  
Old 01-04-2016, 02:36 PM
RickeyD's Avatar
RickeyD RickeyD is offline
Soaring Eagle member
Join Date: Sep 2014
Posts: 2,404
Thanks: 0
Thanked 5 Times in 5 Posts
Default

Quote:
Originally Posted by Chatbrat View Post
Eaton says 28-32 inch/pounds for the wire size that would attached to a 20 amp AFCI

I know what 3 ft lbs sounds like on a drill. His wrist spun when it landed. Will bring down my small torque wrench next trip. Thanks for the info.
  #10  
Old 01-05-2016, 08:30 AM
mulligan mulligan is offline
Sage
Join Date: Sep 2008
Posts: 2,989
Thanks: 17
Thanked 348 Times in 155 Posts
Default

You will also find that a lot of the "electricians" that show up to do service work are not licensed. The requirement seems to be that as long as an employee in the office holds a license, they are covered.
__________________
........American by birth....Union by choice
  #11  
Old 01-05-2016, 09:41 AM
village dreamer village dreamer is offline
Veteran member
Join Date: Jul 2014
Posts: 966
Thanks: 0
Thanked 503 Times in 180 Posts
Default

Quote:
Originally Posted by mulligan View Post
You will also find that a lot of the "electricians" that show up to do service work are not licensed. The requirement seems to be that as long as an employee in the office holds a license, they are covered.
thats true in all the trades
  #12  
Old 01-05-2016, 09:50 AM
mulligan mulligan is offline
Sage
Join Date: Sep 2008
Posts: 2,989
Thanks: 17
Thanked 348 Times in 155 Posts
Default

That's how everybody gets away with cheap help. Right to work states are wonderful.
__________________
........American by birth....Union by choice
  #13  
Old 01-05-2016, 10:52 AM
Topspinmo's Avatar
Topspinmo Topspinmo is offline
Sage
Join Date: Dec 2012
Location: Somewhere over the rainbow
Posts: 14,883
Thanks: 7,463
Thanked 6,140 Times in 3,157 Posts
Default

I don't understand why he at least didn't put the drill in clutch slip setting. I never us my drill on full lockout unless I am drilling in metal or wood. I've been mechanic for 48 years and can torque stuff based on size and materials. But, even I would not of done that especially on someone else's property. Sometimes I just can't watch some one else work!
  #14  
Old 01-05-2016, 10:55 AM
Sandtrap328's Avatar
Sandtrap328 Sandtrap328 is offline
Eternal Member
Join Date: Oct 2014
Posts: 5,349
Thanks: 0
Thanked 5 Times in 4 Posts
Default

Definitely, verify if ANY workers on your property are covered by workers comp insurance.

IF that electrician ( tree trimmer, handyman, etc) gets injured on your property, he can sue you and win.

Check with Seniors vs Crime for full details. In fact, check with them before having work performed to see if you are dealing with a reputable person.
Closed Thread

Tags
drill, observed, told, electrician, breakers, agree, working, life, safety, year, reasons, workmanship, tightened, bar, buss, straight, thing, florida, landed, hand, screws, slipped, stupid, technique, pop


You are viewing a new design of the TOTV site. Click here to revert to the old version.

All times are GMT -5. The time now is 11:00 AM.