Fire Rated Attic Stairs

Reply
Thread Tools
  #1  
Old 02-27-2024, 09:58 AM
jrref jrref is offline
Senior Member
Join Date: May 2021
Posts: 412
Thanks: 192
Thanked 317 Times in 149 Posts
Default Fire Rated Attic Stairs

Since I've been living in the Villages and visiting neighbors and friends who live here, I've noticed that some have no attic stairs but just a thin piece of plywood over the access to their attic over the garage. Also, If they do have attic stairs, none or very few are of the fire rated type.

That said, is there a building code here in the the Villages for fire the rating of the garage. For example, the ceiling should be at least 5/8 inch sheetrock, there should be a fire rated garage access door, etc, to delay the spread of fire for I believe 1 hr, in case of a fire in your garage.

Also, the Garage attic is not separated from the living space attic. And I also see some people who have a vent in their garage door and a fan in the garage ceiling that will turn on when the temperature reaches a certain point. This device would probably acceletate the spread of fire and smoke in a fire in the garage I would think.

In doing some research, It appears that there is no building code for this.

Any thoughts or additional information on the matter?

In some ways when I look at the build of a typical home in the Villages, I'm relatively impressed with the engineering that went into many parts of the design but Fire safety, I'm not sure what to think. Yes in a Block Home, the only way for the fire to spread from the garage would be through the ceilint and the hole for the attic stairs may not be significant unless the whole garage were on fire and at that point the fire rating of the garage stairs may be moot.
  #2  
Old 02-27-2024, 10:16 AM
BigDawgInLakeDenham BigDawgInLakeDenham is offline
Senior Member
Join Date: Jan 2024
Posts: 105
Thanks: 2
Thanked 157 Times in 53 Posts
Default

Quote:
Originally Posted by jrref View Post
Since I've been living in the Villages and visiting neighbors and friends who live here, I've noticed that some have no attic stairs but just a thin piece of plywood over the access to their attic over the garage. Also, If they do have attic stairs, none or very few are of the fire rated type.

That said, is there a building code here in the the Villages for fire the rating of the garage. For example, the ceiling should be at least 5/8 inch sheetrock, there should be a fire rated garage access door, etc, to delay the spread of fire for I believe 1 hr, in case of a fire in your garage.

Also, the Garage attic is not separated from the living space attic. And I also see some people who have a vent in their garage door and a fan in the garage ceiling that will turn on when the temperature reaches a certain point. This device would probably acceletate the spread of fire and smoke in a fire in the garage I would think.

In doing some research, It appears that there is no building code for this.

Any thoughts or additional information on the matter?

In some ways when I look at the build of a typical home in the Villages, I'm relatively impressed with the engineering that went into many parts of the design but Fire safety, I'm not sure what to think. Yes in a Block Home, the only way for the fire to spread from the garage would be through the ceilint and the hole for the attic stairs may not be significant unless the whole garage were on fire and at that point the fire rating of the garage stairs may be moot.
I wonder what Fire Marshall Bill would say before he started a fire
  #3  
Old 02-27-2024, 10:19 AM
retiredguy123 retiredguy123 is online now
Sage
Join Date: Feb 2016
Posts: 14,259
Thanks: 2,348
Thanked 13,739 Times in 5,253 Posts
Default

Yes, there is a building code for separation of the garage and the living area. I think it is a one-hour fire rating, and the plywood at the ceiling probably complies with the code. However a non-fire damper ceiling fan that exhausts air into the attic is definitely a code violation. Most of these exhaust fans deliver the air through the roof, not into attic.
  #4  
Old 02-27-2024, 12:24 PM
vintageogauge vintageogauge is offline
Sage
Join Date: Aug 2016
Location: village of Fenney, Ford City, Pa., and Hudson, Ohio
Posts: 4,164
Thanks: 6
Thanked 4,340 Times in 1,448 Posts
Default

If it's a violation I would guess at least half of the homes here would be in violation of the code.
  #5  
Old 02-27-2024, 12:53 PM
Altavia Altavia is online now
Sage
Join Date: Jun 2019
Posts: 3,407
Thanks: 1,442
Thanked 2,784 Times in 1,246 Posts
Default

Pull down ladder in a fire ceiling | Honest Home Inspections

Our garage has a drop-down ladder in the ceiling, providing access to a storage area in the attic. When we bought the house, our home inspector informed us that this was a violation of the firewall between the garage and the house. Is there a reasonable way to correct this problem and still retain storage access from the garage? —Gene


Dear Gene,
Wall surfaces that separate a garage from a dwelling are required to comply with one-hour fire-rated construction standards. This requirement is intended to slow the spread of a garage fire into the residential areas of the building. When this firewall does not extend into the attic, that is, when the garage attic is not separated from the house attic, then the garage ceiling becomes part of the required garage firewall. Homeowners, typically unaware of such requirements, often violate this fire separation by installing a folding ladder as an attic access. Such fire safety violations are commonly disclosed by home inspectors. Fortunately, there are three practical solutions to the problem:

1) You can eliminate the access by covering the opening with 5/8-inch fire-rated drywall. Unfortunately, this also eliminates the valuable storage space in the garage attic.

2) You can construct a firewall in the attic, separating the garage attic from the house attic. In most cases, the framing for this wall is already partially or completely in place. Once the framing is complete, just apply 5/8inch fire-rated drywall then mud and tape the joints.

3) The manufacturers of some folding ladders make kits for retrofitting their ladders to comply with fire separation requirements. Just check the label on the ladder and contact the manufacturer to see if a fire door upgrade kit is available. Or installing a new pull down that is fire rated may be the best way to go.
  #6  
Old 02-27-2024, 01:01 PM
retiredguy123 retiredguy123 is online now
Sage
Join Date: Feb 2016
Posts: 14,259
Thanks: 2,348
Thanked 13,739 Times in 5,253 Posts
Default

Quote:
Originally Posted by Altavia View Post
Pull down ladder in a fire ceiling | Honest Home Inspections

Our garage has a drop-down ladder in the ceiling, providing access to a storage area in the attic. When we bought the house, our home inspector informed us that this was a violation of the firewall between the garage and the house. Is there a reasonable way to correct this problem and still retain storage access from the garage? —Gene


Dear Gene,
Wall surfaces that separate a garage from a dwelling are required to comply with one-hour fire-rated construction standards. This requirement is intended to slow the spread of a garage fire into the residential areas of the building. When this firewall does not extend into the attic, that is, when the garage attic is not separated from the house attic, then the garage ceiling becomes part of the required garage firewall. Homeowners, typically unaware of such requirements, often violate this fire separation by installing a folding ladder as an attic access. Such fire safety violations are commonly disclosed by home inspectors. Fortunately, there are three practical solutions to the problem:

1) You can eliminate the access by covering the opening with 5/8-inch fire-rated drywall. Unfortunately, this also eliminates the valuable storage space in the garage attic.

2) You can construct a firewall in the attic, separating the garage attic from the house attic. In most cases, the framing for this wall is already partially or completely in place. Once the framing is complete, just apply 5/8inch fire-rated drywall then mud and tape the joints.

3) The manufacturers of some folding ladders make kits for retrofitting their ladders to comply with fire separation requirements. Just check the label on the ladder and contact the manufacturer to see if a fire door upgrade kit is available. Or installing a new pull down that is fire rated may be the best way to go.
I find it difficult to believe that any commercially available folding attic stair assembly would not comply with the building code. Retrofitting the attic space between the garage attic and the living space attic to create a firewall would be very difficult and expensive mostly because of the lack of access to the attic. Also, you would most likely end up with gaps that would defeat the purpose.
  #7  
Old 02-27-2024, 01:40 PM
Altavia Altavia is online now
Sage
Join Date: Jun 2019
Posts: 3,407
Thanks: 1,442
Thanked 2,784 Times in 1,246 Posts
Default

Quote:
Originally Posted by retiredguy123 View Post
I find it difficult to believe that any commercially available folding attic stair assembly would not comply with the building code. Retrofitting the attic space between the garage attic and the living space attic to create a firewall would be very difficult and expensive mostly because of the lack of access to the attic. Also, you would most likely end up with gaps that would defeat the purpose.
Look for certification/label it meets minimum 3/8-inch (9.53 mm) (nominal) fire-retardant-treated structural panel is deemed to meet the 20-minute thermal barrier test based on ASTM E 119, Test Methods for Fire Tests of Building Construction and Materials, or deemed to have the fire resistance of or equivalent to ½-inch (12.7 mm) gypsum wall board.
  #8  
Old 02-27-2024, 01:55 PM
metoo21 metoo21 is offline
Senior Member
Join Date: Jul 2021
Posts: 356
Thanks: 8
Thanked 260 Times in 110 Posts
Default

Quote:
Originally Posted by retiredguy123 View Post
I find it difficult to believe that any commercially available folding attic stair assembly would not comply with the building code. Retrofitting the attic space between the garage attic and the living space attic to create a firewall would be very difficult and expensive mostly because of the lack of access to the attic. Also, you would most likely end up with gaps that would defeat the purpose.
That "plywood" the OP posted about probably is the sheetrock panel that was removed when the opening was created unless someone damaged it and replaced with a sheet of plywood.

The less expensive commercially available folding attic stairs do meet code when used inside a building - but not in the garage. The garage is a different matter due to the storage of cars, lawnmowers and potentially gas cans.

From what I found when I was looking to put stairs in my garage, the ones that meet code for a garage start in the $450 + range. They will have this label.
Attached Thumbnails
The Villages Florida: Click image for larger version

Name:	D-Blaze Fire Retardant Label.jpg
Views:	1472
Size:	47.4 KB
ID:	103078  
  #9  
Old 02-27-2024, 02:10 PM
retiredguy123 retiredguy123 is online now
Sage
Join Date: Feb 2016
Posts: 14,259
Thanks: 2,348
Thanked 13,739 Times in 5,253 Posts
Default

Quote:
Originally Posted by Altavia View Post
Look for certification/label it meets minimum 3/8-inch (9.53 mm) (nominal) fire-retardant-treated structural panel is deemed to meet the 20-minute thermal barrier test based on ASTM E 119, Test Methods for Fire Tests of Building Construction and Materials, or deemed to have the fire resistance of or equivalent to ½-inch (12.7 mm) gypsum wall board.
Interesting. My attic opening, installed by the builder is drywall, not plywood. But, it looks like you can buy a fire-rated or and a non-fire rated folding attic stair. If you are installing it in the garage, you would need to use a stair assembly that provides a one-hour fire rating to comply with the building code for the garage ceiling. But, if you are installing the stair inside the living space, the ceiling does not need to be fire rated, so, I assume you could use a non-fire rated stair assembly. Good to know if you plan to add an attic stair in your garage.
  #10  
Old 02-27-2024, 10:22 PM
dhdallas's Avatar
dhdallas dhdallas is offline
Senior Member
Join Date: Oct 2020
Posts: 448
Thanks: 54
Thanked 1,120 Times in 246 Posts
Default

Quote:
Originally Posted by jrref View Post
Since I've been living in the Villages and visiting neighbors and friends who live here, I've noticed that some have no attic stairs but just a thin piece of plywood over the access to their attic over the garage. Also, If they do have attic stairs, none or very few are of the fire rated type.

That said, is there a building code here in the the Villages for fire the rating of the garage. For example, the ceiling should be at least 5/8 inch sheetrock, there should be a fire rated garage access door, etc, to delay the spread of fire for I believe 1 hr, in case of a fire in your garage.

Also, the Garage attic is not separated from the living space attic. And I also see some people who have a vent in their garage door and a fan in the garage ceiling that will turn on when the temperature reaches a certain point. This device would probably acceletate the spread of fire and smoke in a fire in the garage I would think.

In doing some research, It appears that there is no building code for this.

Any thoughts or additional information on the matter?

In some ways when I look at the build of a typical home in the Villages, I'm relatively impressed with the engineering that went into many parts of the design but Fire safety, I'm not sure what to think. Yes in a Block Home, the only way for the fire to spread from the garage would be through the ceilint and the hole for the attic stairs may not be significant unless the whole garage were on fire and at that point the fire rating of the garage stairs may be moot.
Yes, I have some thoughts on this matter. I could care less what other people are doing to their garages.
  #11  
Old 02-27-2024, 10:34 PM
metoo21 metoo21 is offline
Senior Member
Join Date: Jul 2021
Posts: 356
Thanks: 8
Thanked 260 Times in 110 Posts
Default

Quote:
Originally Posted by jrref View Post
Yes in a Block Home, the only way for the fire to spread from the garage would be through the ceilint and the hole for the attic stairs may not be significant unless the whole garage were on fire and at that point the fire rating of the garage stairs may be moot.
This isn't exactly correct. The blocks are the outside perimeter - not in the wall between the garage and interior of the home. That is a standard stud (could be metal or wood) wall with sheetrock. Still a fire barrier but not block. Nothing is necessarily fire proof but there is a rating such that fire shouldn't penetrate for X amount of time. Hopefully enough time for the fire department to arrive and put out the fire before it spreads to the rest of the home.

In my research about stairs for the garage, I did read some reports of insurance companies not paying claims because the fire spread into the home through the attic stairway and the attic stairs were not properly fire rated.
  #12  
Old 02-28-2024, 04:28 AM
AZ SLIM AZ SLIM is offline
Senior Member
Join Date: Nov 2021
Posts: 165
Thanks: 3
Thanked 210 Times in 72 Posts
Default

Our house was built in 2022 in the Village of Deluna. There is no fire wall in the attic between the garage and the rest of the house, the attic access hole was covered with a piece of drywall, not plywood.

We installed a drop-down ladder from a local company that installs gutters and ladders. There is no fire code sticker on it. The seam around it is as tight or tighter than the original cover. I didn't think to ask about compliance with fire code, maybe I should have. I don't plan to buy an EV (yes, I know gas cars can catch fire too).

The man door between the garage and house is solid wood, but not metal as required by the four other states we lived in. It did not have self-closing hinges like is required in other places. I did change one of the hinges to a self-closing type. That's handy for convenience as well.

The building department in the county building in Wildwood on Powell road (same building as the library) is easy to access and was helpful with another issue we had. You can just walk in and ask if you have questions. They are nice.
  #13  
Old 02-28-2024, 04:44 AM
Normal's Avatar
Normal Normal is offline
Gold member
Join Date: Jun 2021
Location: Earth
Posts: 1,412
Thanks: 3,450
Thanked 1,045 Times in 536 Posts
Default The Villages

Quote:
Originally Posted by Altavia View Post
Pull down ladder in a fire ceiling | Honest Home Inspections

Our garage has a drop-down ladder in the ceiling, providing access to a storage area in the attic. When we bought the house, our home inspector informed us that this was a violation of the firewall between the garage and the house. Is there a reasonable way to correct this problem and still retain storage access from the garage? —Gene


Dear Gene,
Wall surfaces that separate a garage from a dwelling are required to comply with one-hour fire-rated construction standards. This requirement is intended to slow the spread of a garage fire into the residential areas of the building. When this firewall does not extend into the attic, that is, when the garage attic is not separated from the house attic, then the garage ceiling becomes part of the required garage firewall. Homeowners, typically unaware of such requirements, often violate this fire separation by installing a folding ladder as an attic access.
There is an attic ladder pull down on our new construction home purchased straight from The Villages. So are you saying they are breaking the law each and every time they do this? It would be a huge problem for the homeowners and the Developer. The ladder is mounted on thick painted plywood.
__________________
Everywhere

“ There are those who believe something, and therefore will tolerate nothing; and on the other hand, those who tolerate everything, because they believe nothing.” - Robert Browning
  #14  
Old 02-28-2024, 06:45 AM
REDCART REDCART is offline
Platinum member
Join Date: Mar 2007
Posts: 1,879
Thanks: 116
Thanked 194 Times in 93 Posts
Default

We had an exhaust fan installed in our garage ceiling by the Solar Guys. The fan had fire protection included via a metal band that would melt and turn the fan off in the event of a fire.
  #15  
Old 02-28-2024, 06:49 AM
Altavia Altavia is online now
Sage
Join Date: Jun 2019
Posts: 3,407
Thanks: 1,442
Thanked 2,784 Times in 1,246 Posts
Default

Quote:
Originally Posted by Normal View Post
There is an attic ladder pull down on our new construction home purchased straight from The Villages. So are you saying they are breaking the law each and every time they do this? It would be a huge problem for the homeowners and the Developer. The ladder is mounted on thick painted plywood.
They are probably fire rated stairs as mentioned in other posts...
Reply

Tags
fire, garage, attic, stairs, rated