Talk of The Villages Florida - Rentals, Entertainment & More
Talk of The Villages Florida - Rentals, Entertainment & More
|
||
|
||
![]()
Heat pump outside unit not coming on. Air coming out of vent is 66 degrees even though thermostat is set at 74. Thinking it may be a breaker issue,. Garage main panel breaker is fine. Are there other breakers in the chain and if so where?
|
|
|
||
|
||
![]() Quote:
Only one breaker. Check to make sure the condensate drain is not clogged. |
|
||
|
||
![]() Quote:
If the inside unit is running but not the outside unit it could be the capacitor in the outside unit. Fairly simple to replace and see if that was the issue if you have a spare available but the OP probably does not.
__________________
Why do people insist on making claims without looking them up first, do they really think no one will check? Proof by emphatic assertion rarely works. Confirmation bias is real; I can find any number of articles that say so. Victor, NY - Randallstown, MD - Yakima, WA - Stevensville, MD - Village of Hillsborough |
|
||
|
||
![]()
There is a shutoff switch on the outside near the outside unit. This is required as a safety measure. There should be a small box on the exterior wall that you open and pull the handle on the switch. However, I doubt that is the problem. A bad capacitor is more likely, but usually, the outside fan will run, but the compressor will not.
|
|
||
|
||
![]()
Are you sure the breaker in the main panel is on? It is a 2-step process. You push it all the way to the "off" position and then back to the "on" position. Just a thought.
|
|
||
|
||
![]() Quote:
- I haven't heard of sensors in the blower unit that would shut off the outside unit in the case of low air flow. Plus, if those sensors did exist it makes sense that they would shut off the blower unit too. - If the filter is dirty enough to block the airflow sufficiently to be a problem then it needed to be changed long ago - Could it have been cycling the breakers that solved the problem; did you try putting the filter back in? I had a similar problem during the cooling season. Blower fan was running, outside unit was making a soft humming sound, but fan was not running. I cycled the breakers just to see if it would help and it did. (I later replaced the capacitor just in case) - Amazon has filters in that size. MERV 8 and MERV 11 are typical.
__________________
Why do people insist on making claims without looking them up first, do they really think no one will check? Proof by emphatic assertion rarely works. Confirmation bias is real; I can find any number of articles that say so. Victor, NY - Randallstown, MD - Yakima, WA - Stevensville, MD - Village of Hillsborough |
|
||
|
||
![]()
I use the "Filterbuy" Merv 11 filters from Amazon. The standard filter is Merv 8, but I have found that the Merv 11 filters make the house less dusty and more quiet. You can also buy a filter at ACE Hardware, but it will be a Merv 8.
|
|
||
|
||
![]()
In my opinion, that tech is wrong. I get plenty of air flow with Merv 11 filters.
|
|
|
Thread Tools | |
|