Three-Way Switch Wiring

Closed Thread
Thread Tools
  #16  
Old 06-21-2021, 04:13 PM
Ksfirefighter Ksfirefighter is offline
Member
Join Date: Aug 2015
Posts: 54
Thanks: 74
Thanked 45 Times in 14 Posts
Default

You might try this reference
Attached Thumbnails
The Villages Florida: Click image for larger version

Name:	7213F315-234C-4BF8-8CF2-2B0E915467FD.jpg
Views:	175
Size:	61.8 KB
ID:	89905   The Villages Florida: Click image for larger version

Name:	9FF82560-7510-437E-82E6-73B4960845F2.jpg
Views:	128
Size:	61.0 KB
ID:	89906   The Villages Florida: Click image for larger version

Name:	CE8A1DD4-6172-4C14-A62B-954B932214D3.jpg
Views:	142
Size:	62.7 KB
ID:	89907   The Villages Florida: Click image for larger version

Name:	F4820823-CC0D-471C-8F27-3C0AC9DD098E.jpg
Views:	168
Size:	60.6 KB
ID:	89908  
  #17  
Old 06-22-2021, 07:33 AM
Joeint Joeint is offline
Senior Member
Join Date: Jul 2014
Location: Village of DeSoto
Posts: 196
Thanks: 1,193
Thanked 114 Times in 65 Posts
Default

Don't do it you'll burn your house down and your insurance won't cover it!!! Stick to plumbing at least you won't take the chance of killing yourself or someone else. Don't play with electricity...
  #18  
Old 06-22-2021, 08:46 AM
villagetinker's Avatar
villagetinker villagetinker is online now
Sage
Join Date: Sep 2013
Location: Village of Pinellas
Posts: 9,676
Thanks: 2
Thanked 6,156 Times in 2,250 Posts
Default

OP, the box you are looking for is the one where the wires from the breaker box goes to. The 'best way' IMHO to determine this will be to turn OFF the breaker. Go to one of the switch boxes, disconnect the all of BLACK wires and LABEL where they were installed. Make sure that and you are clear of the wires and turn on the breaker, then using a voltmeter determine which wire (there should only be ONE) is energized. If you get more than one black wire energized you are in the wrong box. Repeat above in the other box. Once you get to the correct box with ONE and only ONE energized black wire, your can go and install the new switch.
Now have stated the above, I strongly suggest you get at a minimum a handy man knowledgeable in this area or a licensed electrician to do your project.
Please be careful.
__________________
Pennsylvania, for 60+ years, most recently, Allentown, now TV.
  #19  
Old 06-22-2021, 01:49 PM
Blueblaze Blueblaze is offline
Veteran member
Join Date: Feb 2021
Posts: 549
Thanks: 1
Thanked 1,089 Times in 297 Posts
Default

Quote:
Originally Posted by Wrhobson View Post
The online description of the switch specifically says it is for a 3-way circuit (I'm not quite that dense) BUT it doesn't say that it can only be installed in the "LOAD" box and therein lies my confusion. Your post mentions which "end" of the circuit the box is on and that's what I am trying to clarify. Apparently one end is considered the "Line" end and the other is considered the "Load" end. From what I've read, it appears to me that the box I would like to install it in is a "LINE" box (in their language). This is based on its proximity to the breaker panel plus I don't see enough wires for this box to feed the light being controlled. I have ordered a three-way motion-sensing switch from a different manufacturer to see if it has such a restriction. I understand single pole, double throw switches but it is the definitions (by the switch maker) that confused me. Thanks to all who posted helpful replies.
If the switch must be installed at the "load" end, VillageTinker's instructions tell you how to find the "line" (hot) wire, not the "load". "Load" means the light bulb. "Line" means the source of the power -- the panel. Whichever switch box did NOT have a hot wire connected to the original switch is the "load" side of the circuit, and that's apparently where your motion detector wants to be installed (although I can't think of a reason it would matter).

Here's a picture of a 3-way circuit, to help you understand how it works. See the two wires labeled "travelers"? The power travels from the panel to the lightbulb over one or the other depending on the position of the two switches. In the drawing, the light bulb is off. As you can see, if you flick either switch, the power finds a path over one of the two travelers to the light bulb.

But we haven't talked about "neutrals", which are the white wires. They are the return path from the light bulb to the panel (which I haven't shown in my drawing). Motion detectors normally need a neutral as well as a Line and Load because the gadget that detects the motion needs a return current path itself. If you mistakenly connect a hot wire (whether line or load) directly to a neutral (which would happen if you connected a white wire to the wrong lug on your motion detector) that's a "short circuit", which will trip a breaker and make sparks when you turn the circuit back on. If you accidentally did that when the power was already on (because you turned off the wrong breaker) , it would blow up in your face and the hot flying metal could ruin your eyes. Getting electrocuted is not the only way you can get hurt playing amateur electrician.

Like I said, I think you should get an electrician, but if you want to attach a picture of the instructions and the device, I'll see if I can decipher it for you.
Attached Thumbnails
The Villages Florida: Click image for larger version

Name:	3way.png
Views:	58
Size:	4.8 KB
ID:	89914  
  #20  
Old 06-22-2021, 02:43 PM
Bill14564 Bill14564 is offline
Sage
Join Date: Nov 2020
Location: Village of Hillsborough
Posts: 4,889
Thanks: 1,311
Thanked 5,390 Times in 2,068 Posts
Default

Quote:
Originally Posted by Wrhobson View Post
The instructions (Chinglish) for installing my new motion-sensing switch in a three-way circuit suggest "Determine which electrical box as a LOAD connection". The box where I would prefer to install this motion-sensing switch has two blacks, a red and a ground. Can anybody determine, from that wiring, whether this is the LOAD or the LINE box in a three-way circuit? (I realize I could call a qualified electrician, so please don't suggest the obvious.) I was unaware there was a difference, but this switch, in Chinglish, seems to say that it can apparently only be installed in the LOAD side and that box is blocked by our dryer so it would be ineffective if installed there. Thanks for the help.
Did the switch come with a wiring diagram that you could copy here or could you post the manufacturer and part number?
__________________
Why do people insist on making claims without looking them up first, do they really think no one will check? Proof by emphatic assertion rarely works.
Confirmation bias is real; I can find any number of articles that say so.


Victor, NY
Randallstown, MD
Yakima, WA
Stevensville, MD
Village of Hillsborough
  #21  
Old 06-23-2021, 05:15 AM
Nick B Nick B is offline
Senior Member
Join Date: Dec 2015
Posts: 291
Thanks: 327
Thanked 162 Times in 84 Posts
Default

Quote:
Originally Posted by Wrhobson View Post
The instructions (Chinglish) for installing my new motion-sensing switch in a three-way circuit suggest "Determine which electrical box as a LOAD connection". The box where I would prefer to install this motion-sensing switch has two blacks, a red and a ground. Can anybody determine, from that wiring, whether this is the LOAD or the LINE box in a three-way circuit? (I realize I could call a qualified electrician, so please don't suggest the obvious.) I was unaware there was a difference, but this switch, in Chinglish, seems to say that it can apparently only be installed in the LOAD side and that box is blocked by our dryer so it would be ineffective if installed there. Thanks for the help.
No white?
Closed Thread

Tags
switch, box, load, three-way, motion-sensing


You are viewing a new design of the TOTV site. Click here to revert to the old version.

All times are GMT -5. The time now is 10:53 AM.