Every unit on my street failed at about the same time

Closed Thread
Thread Tools
  #1  
Old 11-18-2021, 04:13 PM
twoplanekid's Avatar
twoplanekid twoplanekid is offline
Platinum member
Join Date: Oct 2014
Location: born Urbana,Il lived in Urbana Ohio for 65 years a house in Lake Deaton
Posts: 1,981
Thanks: 6
Thanked 690 Times in 282 Posts
Default Every unit on my street failed at about the same time

Having never lived in a community where houses on both sides of the street were built within months of each other, my friends and neighbors are all needing to replace their First Alert smoke detectors. It seems that after seven years, they all do fail and need replacement.

At first, I thought a simple battery replacement would do the trick. I should have listened to the beep code (five chirps) that was telling me a full replacement was needed. I then discussed my issue with several neighbors who told me that almost everyone on the street had recently replaced all of their units.

I seems that two models of First Alert smoke detectors (SC9120B – 9120B) are used with the SC9120B having a carbon monoxide alarm added. Both smoke alarms are AC powered interconnected with battery backup. I needed two SC9120B and two 9120B while my brother up the street needed two SC9120B and four 9120B. As I replaced my old First Alert units with new identical model units, all I had to do was twist the new units onto the original mounting brackets and plug in the existing quick connect clip to the new detector.

Some of my neighbors replaced all of their units with the carbon monoxide alarm added unit as the mounting brackets between the alarms are identical. The cost of the 9120B unit is around $18 and the other online is around $33.

While I did all of the work replacing the alarms this time, seven years in the future if I am still around I believe I will let the fire dept. do the installation work for me. You purchase the alarm and the Villages Fire Dept. will install for free. Hope this information helps others with chirping (five chirps) smoke detectors.

Last edited by twoplanekid; 11-18-2021 at 04:31 PM.
  #2  
Old 11-18-2021, 04:32 PM
JerryP JerryP is offline
Senior Member
Join Date: Feb 2012
Posts: 258
Thanks: 12
Thanked 125 Times in 38 Posts
Default

Quote:
Originally Posted by twoplanekid View Post
Having never lived in a community where houses on both sides of the street were built within months of each other, my friends and neighbors are all needing to replace their First Alert smoke detectors. It seems that after seven years, they all do fail and need replacement.

At first, I thought a simple battery replacement would do the trick. I should have listened to the beep code (five chirps) that was telling me a full replacement was needed. I then discussed my issue with several neighbors who told me that almost everyone on the street had recently replaced all of their units.

I seems that two models of First Alert smoke detectors (SC9120B – 9120B) are used with the SC9120B having a carbon monoxide alarm added. Both smoke alarms are AC powered interconnected with battery backup. I needed two SC9120B and two 9120B while my brother up the street needed two SC9120B and four 9120B. As I replaced my old First Alarm units with new identical model units, all I had to do was twist the new units onto the original mounting brackets and plug in the existing quick connect clip to the new detector.

Some of my neighbors replaced all of their units with the carbon monoxide alarm added unit as the mounting brackets between the alarms are identical. The cost of the 9120B unit is around $18 and the other online is around $33.

While I did all of the work replacing the alarms this time, seven years in the future if I am still around I believe I will let the fire dept. do the installation work for me. You purchase the alarm and the Villages Fire Dept. will install for free. Hope this information helps others with chirping (five chirps) smoke detectors.
It’s FREE for Villagers who are disabled or unable to climb a ladder. The resident is responsible for supplying the new batteries and/or detectors.
  #3  
Old 11-18-2021, 04:34 PM
New Englander New Englander is offline
Platinum member
Join Date: May 2017
Location: Massachusetts, Pinellas, Now Sanibel
Posts: 1,969
Thanks: 618
Thanked 1,254 Times in 425 Posts
Default

My house has 3 smoke detectors and 3 carbon/smoke detectors. All 3 of the carbon/smoke detectors have failed and I replaced them. These units were seven years old when they failed.
  #4  
Old 11-18-2021, 04:43 PM
Malsua Malsua is offline
Veteran member
Join Date: Jun 2019
Posts: 683
Thanks: 46
Thanked 910 Times in 329 Posts
Default

As a note, all smoke an CO alarms have a lifespan. it depends on the unit, the ones with the sealed 10 year battery are dead when the battery dies. Most of the "regular" AA, 9v and hardwired units are 8 years and they are done, assuming they don't fail before that.

The sensitivity of the detectors starts downward after they expire. They all have mfg dates listed on the back, if it's 7+ years, toss 'em.
  #5  
Old 11-18-2021, 07:20 PM
Papa_lecki Papa_lecki is offline
Soaring Eagle member
Join Date: Nov 2020
Posts: 2,024
Thanks: 81
Thanked 2,606 Times in 943 Posts
Default

Went to Lowes and bought the 10 year battery ones - simple.
  #6  
Old 11-18-2021, 07:28 PM
retiredguy123 retiredguy123 is offline
Sage
Join Date: Feb 2016
Posts: 14,253
Thanks: 2,345
Thanked 13,717 Times in 5,245 Posts
Default

Quote:
Originally Posted by Papa_lecki View Post
Went to Lowes and bought the 10 year battery ones - simple.
So, are you bypassing the hardwired system in your house? I would have replaced the smoke alarms with the hardwired type that have a battery for backup only. Typically, the 10 year sealed battery type are for locations where there is no hardwired system in place.
  #7  
Old 11-18-2021, 08:02 PM
DAVES DAVES is offline
Sage
Join Date: Feb 2014
Posts: 3,338
Thanks: 179
Thanked 1,875 Times in 949 Posts
Default

Learn from my mistake. Take the battery out when you toss it. The beep warning stops and then goes again in an hour or whatever it is. Also the carbon monoxide ones do not last as long as the smoke only ones.
  #8  
Old 11-18-2021, 09:09 PM
Papa_lecki Papa_lecki is offline
Soaring Eagle member
Join Date: Nov 2020
Posts: 2,024
Thanks: 81
Thanked 2,606 Times in 943 Posts
Default

Quote:
Originally Posted by retiredguy123 View Post
So, are you bypassing the hardwired system in your house? I would have replaced the smoke alarms with the hardwired type that have a battery for backup only. Typically, the 10 year sealed battery type are for locations where there is no hardwired system in place.
No, hardwired in, they have the same plug. 10 year battery backup. Don’t need to change battery every year.
  #9  
Old 11-18-2021, 10:26 PM
Topspinmo's Avatar
Topspinmo Topspinmo is offline
Sage
Join Date: Dec 2012
Location: Somewhere over the rainbow
Posts: 12,408
Thanks: 6,353
Thanked 4,933 Times in 2,456 Posts
Default

Quote:
Originally Posted by twoplanekid View Post
Having never lived in a community where houses on both sides of the street were built within months of each other, my friends and neighbors are all needing to replace their First Alert smoke detectors. It seems that after seven years, they all do fail and need replacement.

At first, I thought a simple battery replacement would do the trick. I should have listened to the beep code (five chirps) that was telling me a full replacement was needed. I then discussed my issue with several neighbors who told me that almost everyone on the street had recently replaced all of their units.

I seems that two models of First Alert smoke detectors (SC9120B – 9120B) are used with the SC9120B having a carbon monoxide alarm added. Both smoke alarms are AC powered interconnected with battery backup. I needed two SC9120B and two 9120B while my brother up the street needed two SC9120B and four 9120B. As I replaced my old First Alert units with new identical model units, all I had to do was twist the new units onto the original mounting brackets and plug in the existing quick connect clip to the new detector.

Some of my neighbors replaced all of their units with the carbon monoxide alarm added unit as the mounting brackets between the alarms are identical. The cost of the 9120B unit is around $18 and the other online is around $33.

While I did all of the work replacing the alarms this time, seven years in the future if I am still around I believe I will let the fire dept. do the installation work for me. You purchase the alarm and the Villages Fire Dept. will install for free. Hope this information helps others with chirping (five chirps) smoke detectors.

I replaced mine two years ago, they were 17 years old and turning yellow. Agree pretty easy but next time I’ll probably be too old to be climbing around on ladder.
  #10  
Old 11-19-2021, 01:52 AM
retiredguy123 retiredguy123 is offline
Sage
Join Date: Feb 2016
Posts: 14,253
Thanks: 2,345
Thanked 13,717 Times in 5,245 Posts
Default

Quote:
Originally Posted by Papa_lecki View Post
No, hardwired in, they have the same plug. 10 year battery backup. Don’t need to change battery every year.
I agree with that. But, you can accomplish the same thing by replacing the alkaline battery with a lithium battery in a regular, non-sealed smoke detector. If you buy the sealed type smoke detectors, you cannot replaced the battery.
  #11  
Old 11-19-2021, 05:45 AM
DaleDivine DaleDivine is offline
Platinum member
Join Date: Apr 2014
Posts: 1,679
Thanks: 516
Thanked 876 Times in 532 Posts
Wink

Ours and five neighbors went out last week. Seven years old. Ordered new ones on Amazon, arrived next day and replaced all as did my neighbors.

  #12  
Old 11-19-2021, 06:09 AM
Catalina36 Catalina36 is offline
Senior Member
Join Date: Nov 2020
Posts: 293
Thanks: 13
Thanked 345 Times in 113 Posts
Default

Good info thanks, all of my smoke detectors are located high close to the ceiling. I thought carbon monoxide detectors need to be about 3 ft from the ground or located near a furnace or gas hot water heater? Placing a Carbon monoxide detector near a ceiling seems useless??? Your thoughts??
  #13  
Old 11-19-2021, 06:21 AM
rjn5656's Avatar
rjn5656 rjn5656 is offline
Gold member
Join Date: Apr 2008
Posts: 1,478
Thanks: 431
Thanked 600 Times in 199 Posts
Send a message via AIM to rjn5656
Default smoke detectors

Have 5 in my old house. Only replaced 2 in the 10 years I lived there.
__________________
Bob anc Cheri
Upstate NY/Bonita
  #14  
Old 11-19-2021, 06:33 AM
noslices1 noslices1 is offline
Veteran member
Join Date: Jul 2012
Posts: 568
Thanks: 55
Thanked 520 Times in 240 Posts
Default

I have one detector that’s high up on top of my vaulted ceiling. I had changed batteries a couple of times in the last 11 years, but then I saw a detector at Lowe’s with a 10 year battery, so that’s what I changed it to. At least no more battery changes in that one for 10 years.
  #15  
Old 11-19-2021, 06:52 AM
JoeinFL JoeinFL is offline
Member
Join Date: Sep 2018
Posts: 83
Thanks: 443
Thanked 70 Times in 39 Posts
Default Placement

Quote:
Originally Posted by Catalina36 View Post
Good info thanks, all of my smoke detectors are located high close to the ceiling. I thought carbon monoxide detectors need to be about 3 ft from the ground or located near a furnace or gas hot water heater? Placing a Carbon monoxide detector near a ceiling seems useless??? Your thoughts??
Carbon Monoxide is a bit lighter than the air we breathe. So, it will not settle down low as many people believe. It can rise up high throughout the home. The suggested height is about 6 feet. ( It may be 4-5’) but, it can go higher so ceiling or high on walls is fine.
If you only have one it should be placed near your sleeping area so you hear it easily if there’s an issue.
I hope this helps.