Default Breaker/wiring problem

Got this unusual problem with one of my circuits. The breaker trips eradicate. I’ve replaced one socket looked kind burnt but not real bad. This problem keeps coming up.

When I test circuit with tester the red light lights faintly. I check voltage with multi meter. I guess going have inspect all outlets on circuit. See it I see anything before I replace breaker?

The tester lights up red faintly at one shown in picture, all rest of circuit outlets test good with only yellow light lite. I have replace that outlet but it connectored with another line I don’t know where those wires go so far?
Attached Thumbnails
The Villages Florida: Click image for larger version

Name:	IMG_0019.jpg
Views:	2051
Size:	36.4 KB
ID:	109024   The Villages Florida: Click image for larger version

Name:	IMG_0020.jpg
Views:	1925
Size:	36.2 KB
ID:	109025   The Villages Florida: Click image for larger version

Name:	IMG_0021.jpg
Views:	1929
Size:	36.5 KB
ID:	109026  

Last edited by Topspinmo; 07-02-2025 at 10:01 AM.
  #2  
Old 07-02-2025, 11:23 AM
Maker Maker is offline
Veteran member
Join Date: Jul 2022
Posts: 629
Thanks: 13
Thanked 557 Times in 247 Posts
Default

Ground and neutral should be tied together somewhere upstream. Seeing 5.3vac says the neutral wire is disconnected somewhere before being reaching this outlet. Likely that voltage is more like a static reading because the meter has a very high input impedance. If you put a 3-way outlet adapter in, with the tester and then your meter, I bet the voltages goes close to zero. Or to 117vac, depending on how that tester is set up. (or use a load without a ground lead)
Next step is to look at other outlets located between this one and the breaker. Check the white wires for a bad wirenut, open junction, loose white wire, etc.
Do not tie the white to the ground.
Looks like that outlet is in concrete block. Garage maybe? There could be an outlet on that circuit in the attic too.
Is the breaker tripping a GFCI ?? Power flowing from outlet hot to a device and returning via ground will trip a GFCI.

Last edited by Maker; 07-02-2025 at 11:36 AM.
  #3  
Old 07-02-2025, 11:28 AM
jimhoward jimhoward is offline
Senior Member
Join Date: Oct 2024
Posts: 292
Thanks: 20
Thanked 273 Times in 140 Posts
Default

There is a typo in your post somewhere which is obscuring meaning. Maybe the word "eradicate" is in error? Maybe should be erratically? Not sure.

It does not seem likely that the breaker is the problem. Seems more like an intermittent short, particularly if the outlet is burnt. The short is probably right in that outlet box. Are the wires overly crowded in there? If so, maybe replace the box with a bigger one and rewire the outlet. Or maybe just rewire in the existing box but being careful to make sure nothing is jammed together or potentially exposed wire touching.
  #4  
Old 07-02-2025, 12:10 PM
village dreamer village dreamer is offline
Veteran member
Join Date: Jul 2014
Posts: 972
Thanks: 0
Thanked 507 Times in 183 Posts
Default

my guess is a gfi , outside.it rains it pops the gfi.
  #5  
Old 07-02-2025, 02:21 PM
Topspinmo's Avatar
Topspinmo Topspinmo is offline
Sage
Join Date: Dec 2012
Location: Somewhere over the rainbow
Posts: 15,032
Thanks: 7,557
Thanked 6,224 Times in 3,203 Posts
Default

Thanks for suggestions. I did some digging around in outlet shown. There a grounding screw in box that was loose? The ground came into box from the main breaker fastened to grounding screw then out to grounding screw on outlet?

I didn’t think loose screw on box would make difference beings it was connected to outlet grounding plate? But, after I tighten up the screw and of course moved wires around getting outlet back in box. The tester lite up all yellow. So, I guess it fixed for now? We see if breaker trips later?

Last edited by Topspinmo; 07-02-2025 at 07:57 PM.
  #6  
Old 07-02-2025, 02:23 PM
Topspinmo's Avatar
Topspinmo Topspinmo is offline
Sage
Join Date: Dec 2012
Location: Somewhere over the rainbow
Posts: 15,032
Thanks: 7,557
Thanked 6,224 Times in 3,203 Posts
Default

Quote:
Originally Posted by jimhoward View Post
There is a typo in your post somewhere which is obscuring meaning. Maybe the word "eradicate" is in error? Maybe should be erratically? Not sure.

It does not seem likely that the breaker is the problem. Seems more like an intermittent short, particularly if the outlet is burnt. The short is probably right in that outlet box. Are the wires overly crowded in there? If so, maybe replace the box with a bigger one and rewire the outlet. Or maybe just rewire in the existing box but being careful to make sure nothing is jammed together or potentially exposed wire touching.
Yes you are correct typo (ai added probably due to my misspelling and I didn’t catch it) erratically was word I was after.
  #7  
Old 07-02-2025, 02:26 PM
Topspinmo's Avatar
Topspinmo Topspinmo is offline
Sage
Join Date: Dec 2012
Location: Somewhere over the rainbow
Posts: 15,032
Thanks: 7,557
Thanked 6,224 Times in 3,203 Posts
Default

Quote:
Originally Posted by Maker View Post
Ground and neutral should be tied together somewhere upstream. Seeing 5.3vac says the neutral wire is disconnected somewhere before being reaching this outlet. Likely that voltage is more like a static reading because the meter has a very high input impedance. If you put a 3-way outlet adapter in, with the tester and then your meter, I bet the voltages goes close to zero. Or to 117vac, depending on how that tester is set up. (or use a load without a ground lead)
Next step is to look at other outlets located between this one and the breaker. Check the white wires for a bad wirenut, open junction, loose white wire, etc.
Do not tie the white to the ground.
Looks like that outlet is in concrete block. Garage maybe? There could be an outlet on that circuit in the attic too.
Is the breaker tripping a GFCI ?? Power flowing from outlet hot to a device and returning via ground will trip a GFCI.

I had go somewhere and haven’t check see it 5Vs still there. The dim red light out now. I’ll Check see if I still have ghost voltage in outlet?
  #8  
Old 07-02-2025, 04:46 PM
Topspinmo's Avatar
Topspinmo Topspinmo is offline
Sage
Join Date: Dec 2012
Location: Somewhere over the rainbow
Posts: 15,032
Thanks: 7,557
Thanked 6,224 Times in 3,203 Posts
Default

Ok, got back on outlet. No stray voltage now. Evidently that ground came from main breaker panel? I wouldn’t thought trighten the screw attached to box would fixed the problem.
Attached Thumbnails
The Villages Florida: Click image for larger version

Name:	IMG_0023.jpg
Views:	867
Size:	61.2 KB
ID:	109028   The Villages Florida: Click image for larger version

Name:	IMG_0022.jpg
Views:	861
Size:	60.4 KB
ID:	109029  
  #9  
Old 07-02-2025, 08:20 PM
Topspinmo's Avatar
Topspinmo Topspinmo is offline
Sage
Join Date: Dec 2012
Location: Somewhere over the rainbow
Posts: 15,032
Thanks: 7,557
Thanked 6,224 Times in 3,203 Posts
Default

Ok I think I figured it out. When pushing the outlet back in Box the grounding wire was probably touching the common side of the outlet. When I would plug something in drawing current from outlet I guessing with ground touching outlet at common connection it would trip breaker. I tighten up grounding screw in box and when putting outlet back in it wasn’t touching. I know this cause when I took it apart again for photo the problem was back with red dimly lite. I bent ground wire back so it wasn’t close and problem fixed again.

The photo show grounding wire by red arrow. The left arrow show where the ground wire was making contact with common side when I pushed back in box, the center top arrow show where ground wire comes in from breaker box. The red arrow on right shows box grounding screw I found that was very loose.
Attached Thumbnails
The Villages Florida: Click image for larger version

Name:	IMG_0025.jpg
Views:	781
Size:	55.2 KB
ID:	109030  
  #10  
Old 07-03-2025, 07:38 AM
HJBeck's Avatar
HJBeck HJBeck is offline
Senior Member
Join Date: Jan 2020
Location: The Villages
Posts: 230
Thanks: 13
Thanked 88 Times in 60 Posts
Default

Your voltmeter was showing 5 v ac reading on the neutral to ground terminals which suggests you have a loose neutral wire or bad outlet somewhere between your outlet and the breaker box. This in itself could be a fire hazard. I would trace back all the outlets from the outlet you measured from and check that all the wiring is tightly connected to the daisy chained outlets all the way back to the breaker box, including the neutral connection for that circuit in the breaker box. (You need to shut off thar breaker to do this). If all the wires are tightly connected to the outlets and you still have the 5v ac reading on the neutral to ground in your outlet shown, then I believe you have a bad outlet somewhere in the daisey chain of outlets back to the breaker box. I would replace ALL of the outlets in the daisey chain. BETTER SAFE THEN SORRY!
  #11  
Old 07-03-2025, 08:36 AM
Camranhvet Camranhvet is offline
Junior Member
Join Date: Mar 2019
Posts: 15
Thanks: 0
Thanked 13 Times in 9 Posts
Default

Quote:
Originally Posted by HJBeck View Post
Your voltmeter was showing 5 v ac reading on the neutral to ground terminals which suggests you have a loose neutral wire or bad outlet somewhere between your outlet and the breaker box. This in itself could be a fire hazard. I would trace back all the outlets from the outlet you measured from and check that all the wiring is tightly connected to the daisy chained outlets all the way back to the breaker box, including the neutral connection for that circuit in the breaker box. (You need to shut off thar breaker to do this). If all the wires are tightly connected to the outlets and you still have the 5v ac reading on the neutral to ground in your outlet shown, then I believe you have a bad outlet somewhere in the daisey chain of outlets back to the breaker box. I would replace ALL of the outlets in the daisey chain. BETTER SAFE THEN SORRY!
Did you not read his last few posts? He found the problem and it is fixed.
  #12  
Old 07-03-2025, 08:55 AM
Fitnusbuf Fitnusbuf is offline
Junior Member
Join Date: Sep 2015
Posts: 13
Thanks: 25
Thanked 7 Times in 5 Posts
Default

Quote:
Originally Posted by Topspinmo View Post
Ok, got back on outlet. No stray voltage now. Evidently that ground came from main breaker panel? I wouldn’t thought trighten the screw attached to box would fixed the problem.
Having a screw loose can get you every time!
  #13  
Old 07-03-2025, 12:21 PM
Topspinmo's Avatar
Topspinmo Topspinmo is offline
Sage
Join Date: Dec 2012
Location: Somewhere over the rainbow
Posts: 15,032
Thanks: 7,557
Thanked 6,224 Times in 3,203 Posts
Default

Quote:
Originally Posted by Fitnusbuf View Post
Having a screw loose can get you every time!
Since my last post I had to also replace the outlet, the problem came back tripping breaker. So far good. I when through every breaker amps (15 and 20 amps circuits) found six 15 amp outlets on 20 amp breaker. I’m assume if got 20 amp circuit you have to have 20amp rated outlets? These are original outlets installed when house was built in 2002. Most of wrong amp outlets are on outsside GFI outlets and two in kitchen. Hopefully I hit bottom of this rats nest?

Last edited by Topspinmo; 07-03-2025 at 02:59 PM.
  #14  
Old 07-03-2025, 12:54 PM
FredMitchell FredMitchell is offline
Senior Member
Join Date: Aug 2023
Posts: 180
Thanks: 46
Thanked 105 Times in 56 Posts
Default

If your breaker is an Eaton 20A AFCI/GFC1, (BRP120DF, for example) you can determine the cause of the trip from the number of LED flashes on the breaker. They have a video for doing that. Or see, this There is also a lawsuit against them for two series of those breakers. I have replaced 3 this year that started tripping intermittently, including one that had nothing plugged into any of the sockets. Eaton will replace the breaker free of charge (BRP120A1CS BR PON, the older one is discontinued. 3-5 days shipping). The replacement breaker is about $68.00 at Lowes.

As to labeling the circuit number on the plate, you can label it on the inside of the plate. Looks less cheezy and you only have to take out one screw to see it.

HTH.
  #15  
Old 07-03-2025, 01:24 PM
Win1894 Win1894 is offline
Senior Member
Join Date: Dec 2015
Posts: 106
Thanks: 95
Thanked 69 Times in 36 Posts
Default

This is good to know Fred. I've had trouble with the Eaton GFCI breakers too. Thanks.