Electrical issue in microwave box Electrical issue in microwave box - Talk of The Villages Florida

Electrical issue in microwave box

Closed Thread
Thread Tools
  #1  
Old 05-18-2015, 03:56 PM
ajbrown's Avatar
ajbrown ajbrown is offline
Sage
Join Date: Oct 2009
Location: Mallory Square (9 months/year), TBD the rest
Posts: 2,641
Thanks: 12
Thanked 21 Times in 12 Posts
Default Electrical issue in microwave box

I know from years of reading TOTV there are come electricians lurking here. I was hoping for some tips on how they may debug the root issue.

I am not an electrician by trade, but know my way around general wiring issues. I am not looking for numbers for electricians you have used. I have those if the need be

The other day, microwave had no power. First time ever and I have been here since 2007. I went out to garage and found a breaker had kicked. I reset breaker and all seemed fine. A few days later I was using it and saw it power off. I 'think' I heard a pop as it did (this 'pop' may have occurred first time), sure enough breaker had tripped again.

This time I turned breaker OFF and was going to unplug and try microwave in a different outlet to further isolate issue. I had a hard time unplugging. I had to pry it off with a screw driver. The pictures explain why it would not come off.

Looking at the pictures, any explanations come to mind or next steps to further isolate? Thanks for any insight...

The Villages Florida

The Villages Florida

PS. My wife swears she has not been using an liquids in that cabinet lately. My initial thought was dirt, or something that got into plug...
__________________
.
Photobucket has changed their site from free for years to now blocking your photos, shame on them and will have to find new way to post albums I have.
  #2  
Old 05-18-2015, 04:25 PM
villagetinker's Avatar
villagetinker villagetinker is offline
Sage
Join Date: Sep 2013
Location: Village of Pinellas
Posts: 11,116
Thanks: 3
Thanked 8,256 Times in 3,001 Posts
Default

The "other day" when you first noticed the MW not working and the breaker tripped, was there a storm in the area? This looks like this could be the result of a nearby lightning strike. If not, then the other possibility would be a loose connection in the plug/socket connection. This damage could be overheating due to a loose connection. The heat from the loose connection could easily cause the plug or cord to the MW to fail, and cause a short circuit causing the breaker to trip. If this is the case, replacing the receptacle will only fix half of the problem, as the cord set is probably damaged, and is now probably a fire hazard. I would suggest replacing the MW.

I looked at the photos again, and I see burn marks INSIDE the box next to the receptacle, this looks suspicious to me. Was anything else tripped at this time?

Look very closely at the receptacle when you replace it for burn marks, especially outside the receptacle. If you find these or anything that indicates arcing, please have a licensed electrician check the entire wiring system for possible damage.

Please proceed very carefully here, and I will strongly suggest you get expert help from a licensed electrical contractor. You do have a problem that if not fixed correctly may cause a future fire.
Hope this helps.
__________________
Pennsylvania, for 60+ years, most recently, Allentown, now TV.
  #3  
Old 05-18-2015, 04:38 PM
rjm1cc's Avatar
rjm1cc rjm1cc is offline
Soaring Eagle member
Join Date: Apr 2010
Posts: 2,470
Thanks: 268
Thanked 583 Times in 283 Posts
Default

Not an electrician but you could have had a lose wire. Buy a new outlet and connect. Be sure screws are tight.

Did microwave work on a different outlet?

If it did I would plug back into the new outlet.But for a while I would unplug it when not using.

Fire is a big risk.
  #4  
Old 05-18-2015, 04:45 PM
ajbrown's Avatar
ajbrown ajbrown is offline
Sage
Join Date: Oct 2009
Location: Mallory Square (9 months/year), TBD the rest
Posts: 2,641
Thanks: 12
Thanked 21 Times in 12 Posts
Default

villagetinker, Thanks, it does make sense.To be clear, there will be no chances taken...

Nothing else is tripped. The microwave is on an isolated circuit. I suspect the 'plug' and the receptacle are NG now. Further examination is required.

I can certainly explain such a thing by a loose connection or a dirty connection, but...

Is it possible that a microwave can ask for so much power that it overheats the components before a circuit trips? This is a pretty bad design, no? No wiring changes have occurred in this home.

I ponder if there is any harm in testing the microwave off of a similar sized circuit, but using a GFI outlet for more protection. How does one prove a microwave is ok?
__________________
.
Photobucket has changed their site from free for years to now blocking your photos, shame on them and will have to find new way to post albums I have.
  #5  
Old 05-18-2015, 04:48 PM
ajbrown's Avatar
ajbrown ajbrown is offline
Sage
Join Date: Oct 2009
Location: Mallory Square (9 months/year), TBD the rest
Posts: 2,641
Thanks: 12
Thanked 21 Times in 12 Posts
Default

Quote:
Originally Posted by rjm1cc View Post
Not an electrician but you could have had a lose wire. Buy a new outlet and connect. Be sure screws are tight.

Did microwave work on a different outlet?

If it did I would plug back into the new outlet.But for a while I would unplug it when not using.

Fire is a big risk.
Thank you. My next step is to pull the receptacle out of the box and inspect the connections a bit later.
__________________
.
Photobucket has changed their site from free for years to now blocking your photos, shame on them and will have to find new way to post albums I have.
  #6  
Old 05-18-2015, 05:15 PM
ajbrown's Avatar
ajbrown ajbrown is offline
Sage
Join Date: Oct 2009
Location: Mallory Square (9 months/year), TBD the rest
Posts: 2,641
Thanks: 12
Thanked 21 Times in 12 Posts
Exclamation Holy COW

Much worse that I could have expected. Going to call warranty (or someone in TV) to see what resources they can provide to understand root issue. This is more than a switch that does not work. I cannot ever remember seeing something like this before, but maybe I have been lucky in my previous homes...

The black wire (burned) may have come disconnected when I pulled receptacle out of box. It does seem all of the wires have a good tight connection.

I am taking no further action at this time. A piece of duct tape is over the breaker to prevent accidental turn on.

The Villages Florida
__________________
.
Photobucket has changed their site from free for years to now blocking your photos, shame on them and will have to find new way to post albums I have.
  #7  
Old 05-18-2015, 05:28 PM
Uberschaf Uberschaf is offline
Senior Member
Join Date: Jul 2014
Posts: 384
Thanks: 0
Thanked 5 Times in 2 Posts
Default

Black wire (load) was loose on receptacle causing heat issue.New plug,new receptacle and your good to go.I believe your microwave is 1800 watts which is 15 amperes and the receptacle is a 20 amp. Loose wire.
  #8  
Old 05-18-2015, 07:13 PM
villagetinker's Avatar
villagetinker villagetinker is offline
Sage
Join Date: Sep 2013
Location: Village of Pinellas
Posts: 11,116
Thanks: 3
Thanked 8,256 Times in 3,001 Posts
Default

To all,
Many of the original receptacles and switches use PUSH IN WIRE CONNECTIONS. Personally I do not like these. My step son moved into a mobile home recently, and in the process of adding a GFCI to bring it up to code, some of the wires in other receptacles on the same circuit pulled out of the receptacles as I was taking these out of the box, YIKES!!. I immediately replaced every switch and receptacle, and use the screw terminals.

A follow up discussion with UL indicated the specific brand (about 20 years old) was recalled and delisted due to problems with the push in connections, and the newer versions were redesigned to avoid these problems. IMHO, I still like the properly torqued screw connections.

I would hope some of the electrical inspectors jump in here.....

ALL, please do not attempt electrical repair, unless you really know what you are doing, plastic boxes are not going to contain a fire, and while the push in connectors are typically use, it is interesting that there appear to be more then one instance of problems. I will be inspecting ours tomorrow.

AJBrown, I would bet the black wire was nicked and stressed to the point of almost breaking, then repeated used (aka heating and cooling) caused the failure, this is just a guess.

Also, you could take the microwave to the garage, there is a dedicated 20 amp GFCI circuit, or use one of the counter outlets (15 amp GFCI) in the kitchen. MAKE SURE YOU HAVE A CUP OF WATER OR EQUAL IN THE MICROWAVE. But I would have the cord set carefully inspected for damage, and replaced if possible.
__________________
Pennsylvania, for 60+ years, most recently, Allentown, now TV.
  #9  
Old 05-18-2015, 07:21 PM
DonH57's Avatar
DonH57 DonH57 is offline
Sage
Join Date: Mar 2011
Location: Village Santo Domingo.
Posts: 3,959
Thanks: 1
Thanked 623 Times in 321 Posts
Send a message via AIM to DonH57
Default

Quote:
Originally Posted by Uberschaf View Post
Black wire (load) was loose on receptacle causing heat issue.New plug,new receptacle and your good to go.I believe your microwave is 1800 watts which is 15 amperes and the receptacle is a 20 amp. Loose wire.
I'm thinking that too as any loose connection of a wire and a device or a two wire connection will cause excessive heat melting components causing damage.
  #10  
Old 05-19-2015, 05:03 AM
l2ridehd's Avatar
l2ridehd l2ridehd is offline
Sage
Join Date: Dec 2007
Location: Bridgeport At Miona Shores
Posts: 3,603
Thanks: 1
Thanked 353 Times in 122 Posts
Send a message via AIM to l2ridehd
Default

The Villages electricians use the type receptacle where you strip and push the wire in a hole. Over time and a heavy load (microwave) these connections will arc. Very minor at first, but over time will cause the exact problem you have. I would strip the 12-2 Romex back a few inches if possible, replace the outlet with a new one, use the screws on the side vs the push in holes, replace the plug on the microwave cord, and you should be good to go. Might also check the screw on the breaker to be sure that is tight as well. Somewhere in the circuit there was a loose connection. Most likely the connection at the outlet, but would also check the CB in the panel.

If you need any assistance just PM me and I will come over and give you a hand.
__________________
Life is to short to drink cheap wine.
  #11  
Old 05-19-2015, 05:08 AM
l2ridehd's Avatar
l2ridehd l2ridehd is offline
Sage
Join Date: Dec 2007
Location: Bridgeport At Miona Shores
Posts: 3,603
Thanks: 1
Thanked 353 Times in 122 Posts
Send a message via AIM to l2ridehd
Default

Looking at the photo more closely, looks like the did use the screw on the side of the outlet. Could have been loose, could have been scored by wire strippers when installed, could have been cut covering and arced to the ground wire, but this was most likely an issue when installed. Replace all the components, make sure all connections are tight and you should be fine.
__________________
Life is to short to drink cheap wine.
  #12  
Old 05-19-2015, 06:15 AM
ajbrown's Avatar
ajbrown ajbrown is offline
Sage
Join Date: Oct 2009
Location: Mallory Square (9 months/year), TBD the rest
Posts: 2,641
Thanks: 12
Thanked 21 Times in 12 Posts
Default

Thanks all. Everything you have posted makes good sense and was the feed back I was hoping for. I also appreciate the multiple offers for assistance. In this case I will be all set, but thank you, it is very nice

I am feeling better that the microwave is not the culprit and will test it on a GFI circuit. Facts as we know them lean towards this issue existing since the installation of the wiring when the house was built.

It does make me ponder how many other 'sleeping time bombs' exist .
__________________
.
Photobucket has changed their site from free for years to now blocking your photos, shame on them and will have to find new way to post albums I have.
  #13  
Old 05-19-2015, 07:41 AM
ajbrown's Avatar
ajbrown ajbrown is offline
Sage
Join Date: Oct 2009
Location: Mallory Square (9 months/year), TBD the rest
Posts: 2,641
Thanks: 12
Thanked 21 Times in 12 Posts
Default For you fire marshals in training

A couple of interesting pictures... I mean, I think they are interesting


If you look close you can see what looks like a hole through the body of the receptacle. The wire no longer comes out the normal path.

It is unclear if the hole goes through. I do not wish to change "the evidence" to find out if it does. I may give the fire dept. a call to see if they can take a look. Why not.. I am a curious guy...

The Villages Florida

Here is the other side of "what appears to be" a hole.

The Villages Florida
__________________
.
Photobucket has changed their site from free for years to now blocking your photos, shame on them and will have to find new way to post albums I have.
  #14  
Old 06-18-2015, 11:31 AM
TimH25 TimH25 is offline
Junior Member
Join Date: Jun 2015
Posts: 2
Thanks: 0
Thanked 0 Times in 0 Posts
Default

Could you say how you are getting on please.
  #15  
Old 06-18-2015, 12:22 PM
villagetinker's Avatar
villagetinker villagetinker is offline
Sage
Join Date: Sep 2013
Location: Village of Pinellas
Posts: 11,116
Thanks: 3
Thanked 8,256 Times in 3,001 Posts
Default

Yes, I was wondering also if AJBrown found the root cause of the problem.
__________________
Pennsylvania, for 60+ years, most recently, Allentown, now TV.
Closed Thread


You are viewing a new design of the TOTV site. Click here to revert to the old version.

All times are GMT -5. The time now is 06:10 AM.