Default HVAC Talk

With all the recent heat we have been having here in central Florida, I thought it would be good to have a thread on general HVAC questions and learnings. There are so many misconceptions on HVAC and there are so many "experts" here on TOTV, maybe we can share some knowledge?

To start, I was reading about conventional vs smart thermostats and their potential effects on your HVAC system. We have to assume we are using a basic single or two stage system since newer variable speed systems generally use special thermostats or what they call Wall Units becasue they are small computers that control the different components in a communicating system.

So, which is better a conventional basic thermostat that came with your home or ones like you can get in the hardware store or Nest or Ecobee Smart thermostats? I've had all three and can tell you about my thoughts but can anyone share theirs?

For these types of thermostats:
Which one kept the temperature the most constant?
Which one kept the humidity the most constant?
Which one saved the most money and how do you think it did that?
Which one was the easiest to install and use?

Remember we are talking about basic HVAC systems that go full 100% On and full 100% OFF eventhough some many be two stange.
  #2  
Unread 08-16-2025, 10:48 AM
retiredguy123 retiredguy123 is online now
Sage
Join Date: Feb 2016
Posts: 17,609
Thanks: 3,087
Thanked 16,767 Times in 6,640 Posts
Default

I have the basic, single stage Carrier heat pump, with the original basic thermostat. It has been working fine for almost 10 years, and every room is within one degree of the thermostat setting. Once, about 6 years ago, my capacitor went bad, and Munn's came out and replaced it within a few hours. There was no charge because he system was still under warranty. The only change I ever made was that I use MERV 11 filters instead of the standard MERV 8 and I change it every 6 months. I found that these seem to make the house quieter and less dusty. I pour a gallon of hot tap water down the condensate drain every month, and I inspect the coils for dirt but I have never needed to clean them, although I have hosed down the outside unit. I have never paid any company for maintenance.
  #3  
Unread 08-16-2025, 11:36 AM
jrref jrref is offline
Platinum member
Join Date: May 2021
Posts: 1,524
Thanks: 508
Thanked 919 Times in 496 Posts
Default

Quote:
Originally Posted by retiredguy123 View Post
I have the basic, single stage Carrier heat pump, with the original basic thermostat. It has been working fine for almost 10 years, and every room is within one degree of the thermostat setting. Once, about 6 years ago, my capacitor went bad, and Munn's came out and replaced it within a few hours. There was no charge because he system was still under warranty. The only change I ever made was that I use MERV 11 filters instead of the standard MERV 8 and I change it every 6 months. I found that these seem to make the house quieter and less dusty. I pour a gallon of hot tap water down the condensate drain every month, and I inspect the coils for dirt but I have never needed to clean them, although I have hosed down the outside unit. I have never paid any company for maintenance.
I also feel MERV 11 is the best but I wouldn't go above that. With the 4 inch filters you can do this because of the better air flow than a 1 inch filter provides. Since you don't get your unit serviced, I would suggest once a year or whenever you change your filter, get one of these temperature probes and at your air handler measure the difference in temperature at the return and at the output of the air handler. These temperature probes usually have a sharp metal tip where you can easily pierce the duct board. You should measure about 18-20 degree difference. This is a good way to tell if the system is working properly without putting gauges and measureing the pressures, etc.. If it's alot less than you probably want to investigate what could be wrong. When you are done just take some blue tape and cover the two holes on the duct board for next time.

If you change the filter regularly, flush the condensate line once a month, keep the coils clean, If you can, change the start capacitor and contactor with a good American made one and not a cheap Chinese one that costs $12 on Amazon maybe every 5 years, and if you put a surge protector at the outside power disconnect, If you don't develop a leak, your system has a good chance of lasting 10-15 years if it's a heat pump.

If you have one of these installed which in addition to power surges protects against brown outs and over voltages, then you increase your chances even more. RectorSeal RSH-50 VRMDC KIT - AC Unit Surge Protector

Also installing a soft start kit will help but they also can fail.

Although most have the single stage systems, every time they go On they can draw a huge amount of current. Given these Smart Thermostats cycle many times an hour to keep the temperature and humidity more constant, thats a lot of wear and tear. It's kind of like driving your car full throttle all the time then stopping. I don't understand why manufacturers don't install some sort of Soft Start system as part of the unit.

Last edited by jrref; 08-16-2025 at 11:53 AM.
  #4  
Unread 08-19-2025, 10:20 PM
Bilyclub's Avatar
Bilyclub Bilyclub is offline
Platinum member
Join Date: Aug 2019
Posts: 1,974
Thanks: 578
Thanked 1,368 Times in 646 Posts
Default

I’m curious to see what most people here try to keep their humidity level at in the house.
  #5  
Unread Yesterday, 07:53 AM
jrref jrref is offline
Platinum member
Join Date: May 2021
Posts: 1,524
Thanks: 508
Thanked 919 Times in 496 Posts
Default

Quote:
Originally Posted by Bilyclub View Post
I’m curious to see what most people here try to keep their humidity level at in the house.
I set mine to 56%
  #6  
Unread Yesterday, 08:22 AM
retiredguy123 retiredguy123 is online now
Sage
Join Date: Feb 2016
Posts: 17,609
Thanks: 3,087
Thanked 16,767 Times in 6,640 Posts
Default

Quote:
Originally Posted by Bilyclub View Post
I’m curious to see what most people here try to keep their humidity level at in the house.
I don't use the optional humidity feature on the standard thermostat. This feature will overcool the house by about 3 degrees to reduce humidity when it exceeds the humidity setting. I always have the feature turned off and I have never had an issue with high humidity. Currently, the relative humidity in the house is 40 percent, and the range from the past 36 hours has been from 37 to 44 percent. My thermostat is set at 78 degrees. You can buy a humidity measuring device from Amazon for about 10 dollars, and it will track the humidity over the past 36 hour time period.
  #7  
Unread Yesterday, 08:47 AM
Michael G. Michael G. is offline
Soaring Eagle member
Join Date: Nov 2019
Posts: 2,406
Thanks: 0
Thanked 2,443 Times in 947 Posts
Default

My 3 yr. old two stage Carrier installed by Munn's came with a Ecobee Premium Smart thermostat stalled.
I live alone, and home most of the time and have it set "on hold" at 77 degrees 24/7, no auto resets.
Set it and forget it.

Every household has to determine what temp is comfortable for them.
I sleep perfectly at those temps with a ceiling fan running on low in the bedroom.

If I would leave the house, for say a week, I would probably set it @ 80 degrees on hold.

When I lived up north, and my wife and I both worked, the reset thermostats really worked great,
set lower on heating during the day when nobody was home.
  #8  
Unread Yesterday, 11:23 AM
Altavia Altavia is offline
Sage
Join Date: Jun 2019
Posts: 4,613
Thanks: 1,944
Thanked 3,540 Times in 1,699 Posts
Default

60% on an Ecobee.

The humidity calibration was 8% high, adjusted via the settings.

I've been experimenting with adjusting the minimum on time from 5 min to 10 min to reduce start/up wear and tear on the system.

For the data junkies, there's information available via the reports tab.
Attached Thumbnails
The Villages Florida: Click image for larger version

Name:	IMG_1334.jpg
Views:	80
Size:	32.7 KB
ID:	109626  
  #9  
Unread Today, 08:47 AM
Topspinmo's Avatar
Topspinmo Topspinmo is offline
Sage
Join Date: Dec 2012
Location: Somewhere over the rainbow
Posts: 15,349
Thanks: 7,708
Thanked 6,329 Times in 3,279 Posts
Default

not a cheap Chinese One? So, new units come with Chinese ones. My recently installed carrier less than two years old. Will never be able to eliminate Chinese products.
Attached Thumbnails
The Villages Florida: Click image for larger version

Name:	IMG_0782.jpg
Views:	18
Size:	54.4 KB
ID:	109640   The Villages Florida: Click image for larger version

Name:	IMG_0781.jpg
Views:	18
Size:	65.1 KB
ID:	109642  
  #10  
Unread Today, 12:59 PM
jrref jrref is offline
Platinum member
Join Date: May 2021
Posts: 1,524
Thanks: 508
Thanked 919 Times in 496 Posts
Default

Quote:
Originally Posted by Altavia View Post
60% on an Ecobee.

The humidity calibration was 8% high, adjusted via the settings.

I've been experimenting with adjusting the minimum on time from 5 min to 10 min to reduce start/up wear and tear on the system.

For the data junkies, there's information available via the reports tab.
I think it would be better adjusting the temperature "Swing". I believe it's set to 4 degrees on the Ecobee meaning 2 degrees above and below your setting. But you are correct, the better the thermostat keeps the temperature at the set point, the more it's running accelerating wear on the compressor.

A thermostat's swing setting, also known as temperature differential or maintenance band, determines how much the temperature fluctuates above or below the setpoint before the heating or cooling system engages. This setting affects how often your HVAC system cycles on and off. A smaller swing setting results in more frequent but shorter cycles, while a larger swing setting leads to fewer but longer cycles.

Last edited by jrref; Today at 01:31 PM.
  #11  
Unread Today, 01:30 PM
jrref jrref is offline
Platinum member
Join Date: May 2021
Posts: 1,524
Thanks: 508
Thanked 919 Times in 496 Posts
Default

Quote:
Originally Posted by Topspinmo View Post
not a cheap Chinese One? So, new units come with Chinese ones. My recently installed carrier less than two years old. Will never be able to eliminate Chinese products.
Are you sure that capacitor was not changed? Because they never write on the capacitor from the factory. That's usually done by a repair tech, so the next tech knows the values if the description is worn off over time.
  #12  
Unread Today, 01:35 PM
jrref jrref is offline
Platinum member
Join Date: May 2021
Posts: 1,524
Thanks: 508
Thanked 919 Times in 496 Posts
Default

You can better find the temperature "sweet spot" that you like by adjusting the set temperature and humidity. In some cases you can set the temperature higher with a lower humidity setting giving your more comfort and efficiency.

On a single stage system it's going to be harder to set the humidity since the system only runs at 100% or Off. With a variable speed system or even a two stage system, you will have better control of the humidity because the system runs longer and slower. My variable speed system sometimes goes into Dehumidifing mode which is running at a very low speed specifically to lower the humidity.
  #13  
Unread Today, 02:02 PM
retiredguy123 retiredguy123 is online now
Sage
Join Date: Feb 2016
Posts: 17,609
Thanks: 3,087
Thanked 16,767 Times in 6,640 Posts
Default

Quote:
Originally Posted by jrref View Post
You can better find the temperature "sweet spot" that you like by adjusting the set temperature and humidity. In some cases you can set the temperature higher with a lower humidity setting giving your more comfort and efficiency.

On a single stage system it's going to be harder to set the humidity since the system only runs at 100% or Off. With a variable speed system or even a two stage system, you will have better control of the humidity because the system runs longer and slower. My variable speed system sometimes goes into Dehumidifing mode which is running at a very low speed specifically to lower the humidity.
To clarify, most HVAC systems in The Villages do not have the capability to "increase" the humidity in your house. This requires a humidifier that actually sprays water into your duct. What you do have is an optional humidity setting on your thermostat that can "reduce" the relative humidity by increasing the cooling time or by overcooling your house to a few degrees below the temperature setting. Even today, when it is raining, my thermostat is set on 79 degrees, the optional humidity feature is turned off, and the relative humidity in my house is a comfortable 43 percent. It seems to me that if you need to set your humidity setting to 55 or 60 percent, you must be leaving a door or window open, or you are adding outside air into your house. The relative humidity in my house never gets that high.
Reply