Quote:
Originally Posted by StamperTV25 View Post
I am not concerned about the one inch....it is about the other connection points going up to the roof. We have built many homes and always did a pre-drywall inspection to verify things were done correctly and to code. These homes are released when they are completed.....so if found to be incorrectly installed.....it will need to be reinstalled.
Per FL code:

M1502.4.2 Duct installation.
Exhaust ducts shall be supported at intervals not to exceed 12 feet (3658 mm) and shall be secured in place.

The insert end of the duct shall extend into the adjoining duct or fitting in the direction of airflow.

Exhaust duct joints shall be sealed in accordance with Section M1601.4.1. Ducts shall not be joined with screws or similar fasteners. Where dryer exhaust ducts are enclosed in wall or ceiling cavities, such cavities shall allow the installation of the duct without deformation.

[url]https://codes.iccsafe.org/content/FLRC2020P1/chapter-15-exhaust-systems[/url


Let us know how it turns out.
  #17  
Old 06-07-2025, 11:28 AM
retiredguy123 retiredguy123 is online now
Sage
Join Date: Feb 2016
Posts: 17,222
Thanks: 3,005
Thanked 16,420 Times in 6,467 Posts
Default

Quote:
Originally Posted by Altavia View Post
Per FL code:

M1502.4.2 Duct installation.
Exhaust ducts shall be supported at intervals not to exceed 12 feet (3658 mm) and shall be secured in place.

The insert end of the duct shall extend into the adjoining duct or fitting in the direction of airflow.

Exhaust duct joints shall be sealed in accordance with Section M1601.4.1. Ducts shall not be joined with screws or similar fasteners. Where dryer exhaust ducts are enclosed in wall or ceiling cavities, such cavities shall allow the installation of the duct without deformation.

[url]https://codes.iccsafe.org/content/FLRC2020P1/chapter-15-exhaust-systems[/url


Let us know how it turns out.
I am not sure I understand the bolded part of your quote. Most dryers I have seen come with a flexible duct that wraps around the metal duct and is attached using a metal collar that is tightened with a screwdriver. In that case, the insert end of the metal duct would be pointed against the direction of airflow. Is this a code violation?
  #18  
Old 06-07-2025, 11:52 AM
Altavia Altavia is offline
Sage
Join Date: Jun 2019
Posts: 4,507
Thanks: 1,924
Thanked 3,470 Times in 1,654 Posts
Default

Quote:
Originally Posted by retiredguy123 View Post
I am not sure I understand the bolded part of your quote. Most dryers I have seen come with a flexible duct that wraps around the metal duct and is attached using a metal collar that is tightened with a screwdriver. In that case, the insert end of the metal duct would be pointed against the direction of airflow. Is this a code violation?
Good question?

Apparently that does not apply to transition ducts. The dryerbox manufacturer has directions installing in that manner and the ducts should be joined with clamps or foil tape.

I used this:

DryerFlex(R) Transition Duct

Magvents have been a great solution for some previous very tight/offset installs.

Magvent Dryer Vent - Magnetic Dryer Vent | Dryer Vent Hose Replacement
  #19  
Old 06-08-2025, 04:40 AM
SeanInFlorida SeanInFlorida is offline
Junior Member
Join Date: Apr 2025
Posts: 7
Thanks: 0
Thanked 8 Times in 4 Posts
Default

All the new construction is like that in TV. The pipe exposed has a double crimped end, so in the wall the crimps go in the direction of the airflow. They just have a crimped end exposed for ease of connection.
  #20  
Old 06-08-2025, 05:32 AM
StamperTV25 StamperTV25 is offline
Junior Member
Join Date: Mar 2025
Posts: 13
Thanks: 33
Thanked 6 Times in 5 Posts
Default

Thanks Sean.......I was assuming that was the reason since it can be difficult for some to attach the Vent coming from the dryer. I just thought someone currently living there would have the answer. Thanks again.
  #21  
Old 06-08-2025, 06:57 AM
Malsua Malsua is offline
Veteran member
Join Date: Jun 2019
Posts: 701
Thanks: 50
Thanked 939 Times in 342 Posts
Default

Quote:
Originally Posted by StamperTV25 View Post
We will be coming up to TV to purchase a new home this coming week. The question I have is for those that have noticed the dryer vent pipe looks to be installed with the crimped end on the vent pipe sections facing down instead of upwards toward the roof. I have always had homes with the vent piping installed the crimped ends facing towards the roof vent.....that way allows air to flow freely through the pipe without any obstructions. If the crimped end is facing down....or against the air flow.....the lint would naturally collect on the crimped ends of the pipe sections. I don't know if anyone else has addressed this?......but would love any feedback. I tried to attach a photo.....hopefully it shows up.
This is a common installation in the newer sections of The Villages. I am a Licensed, certified, bonded and insured home inspector and I have inspected north of 500 homes in The Villages.

Here is an example from a home on Katie Keith Loop, i.e. "Street of Dreams". I inspected this one in March. This is near Middleton, south of 470.

The older homes have just a smooth opening and people couldn't figure out how to install the pipe so ended up getting a male to male coupler anyway instead of an extender. With periodic maintenance, it won't be an issue.
Attached Thumbnails
The Villages Florida: Click image for larger version

Name:	2025-03-26-11_24_34_585.jpg
Views:	124
Size:	16.9 KB
ID:	108732  
  #22  
Old 06-08-2025, 07:19 AM
DrHitch DrHitch is offline
Senior Member
Join Date: Mar 2017
Location: Rio Grande village and Cleveland, OH
Posts: 319
Thanks: 785
Thanked 112 Times in 83 Posts
Default Finally . A quality response!

Quote:
Originally Posted by Malsua View Post
....ended up getting a male to male coupler anyway instead of an extender. With periodic maintenance, it won't be an issue.
Yea! Good reply....I was going to say that installing sheet metal duct with crimps reversed downwards was "to keep the rainwater flowing down the pipe into the dryer"....haha
  #23  
Old 06-08-2025, 07:49 AM
jimmy o jimmy o is offline
Senior Member
Join Date: Mar 2021
Location: Village of Sunset Point
Posts: 203
Thanks: 25
Thanked 105 Times in 63 Posts
Default

Quote:
Originally Posted by StamperTV25 View Post
We will be coming up to TV to purchase a new home this coming week. The question I have is for those that have noticed the dryer vent pipe looks to be installed with the crimped end on the vent pipe sections facing down instead of upwards toward the roof. I have always had homes with the vent piping installed the crimped ends facing towards the roof vent.....that way allows air to flow freely through the pipe without any obstructions. If the crimped end is facing down....or against the air flow.....the lint would naturally collect on the crimped ends of the pipe sections. I don't know if anyone else has addressed this?......but would love any feedback. I tried to attach a photo.....hopefully it shows up.
It seems some responders do not understand the problem. Yes your photo shows the crimped end going wrong direction. In your setup each connection going all the way up and out through the roof would become a trapping point for the lint which is flowing up and out. For those that don’t get it, picture a rake; the teeth of the rake grab the grass when pulling towards you. If you turn the rake over and use the back of it the rake will just slide across the grass and catch nothing. That is the same as having crimped connection going the wrong way, the lint will get caught.
  #24  
Old 06-08-2025, 07:55 AM
Malsua Malsua is offline
Veteran member
Join Date: Jun 2019
Posts: 701
Thanks: 50
Thanked 939 Times in 342 Posts
Default

Quote:
Originally Posted by jimmy o View Post
In your setup each connection going all the way up and out through the roof would become a trapping point for the lint which is flowing up and out.
Except it's not like that. That piece that is crimped that way is only there. The rest, up through the termination vent, are male into female and taped. They added a male-to-male at the termination point because most people couldn't seem to figure it out.
  #25  
Old 06-08-2025, 08:11 AM
Andyb Andyb is offline
Senior Member
Join Date: Dec 2017
Posts: 325
Thanks: 83
Thanked 459 Times in 177 Posts
Default Vent pipe

Vent pipe should always fit over the dryer discharge pipe.
  #26  
Old 06-08-2025, 08:38 AM
RRGuyNJ RRGuyNJ is offline
Senior Member
Join Date: Sep 2023
Posts: 146
Thanks: 131
Thanked 85 Times in 47 Posts
Default You are correct

You are 100% correct. Unfortunately the walls are already closed in so we have no idea what's behind them. The way I understand it is if you buy a "Spec-Home" you don't have much say over what goes on and can't be on site watching the build as you can in the outside world. I certainly hope if it's a custom built home the owner can be on site to see how things are progressing.
Your photo shows what should be an onsite crimp done during installation for the flex vent to attach too and the connections are opposite within the wall and going with the air flow as you described. That crimp appears to be a factory crimp and could be a male to male adapter as mentioned earlier. In the end, who knows? Maintain it by cleaning it every few years with a rotary brush and a shop vac and you should be fine
Good luck with your move.

Last edited by RRGuyNJ; 06-08-2025 at 09:02 AM.
  #27  
Old 06-08-2025, 09:28 AM
NoMoSno NoMoSno is offline
Gold member
Join Date: Mar 2013
Posts: 1,330
Thanks: 188
Thanked 361 Times in 227 Posts
Default

Quote:
Originally Posted by RRGuyNJ View Post
In the end, who knows?
The county building inspector knows, as this is part of the inspection before the walls are closed in.
  #28  
Old 06-08-2025, 09:56 AM
retiredguy123 retiredguy123 is online now
Sage
Join Date: Feb 2016
Posts: 17,222
Thanks: 3,005
Thanked 16,420 Times in 6,467 Posts
Default

Quote:
Originally Posted by Andyb View Post
Vent pipe should always fit over the dryer discharge pipe.
That is not the way most dryers are installed. The dryer comes with a flexible duct and a metal band clamp to secure it to the outside of the permanent metal exhaust duct. If you try to put the flexible duct inside of the exhaust duct it is too large to fit, and even if you get it inside, how do you secure it?
  #29  
Old 06-08-2025, 11:12 AM
Accidental1 Accidental1 is offline
Senior Member
Join Date: Nov 2020
Posts: 132
Thanks: 50
Thanked 91 Times in 48 Posts
Default Just took mine apart

Quote:
Originally Posted by StamperTV25 View Post
We will be coming up to TV to purchase a new home this coming week. The question I have is for those that have noticed the dryer vent pipe looks to be installed with the crimped end on the vent pipe sections facing down instead of upwards toward the roof. I have always had homes with the vent piping installed the crimped ends facing towards the roof vent.....that way allows air to flow freely through the pipe without any obstructions. If the crimped end is facing down....or against the air flow.....the lint would naturally collect on the crimped ends of the pipe sections. I don't know if anyone else has addressed this?......but would love any feedback. I tried to attach a photo.....hopefully it shows up.
We're getting rid of the original washer/dryer tomorrow so I disconnected everything yesterday. I have what appears to be the exact same vent box setup (i.e. crimped end against airflow) as shown in your photo, and the one from the home inspector. We bought new in 2021. When I disconnected the flexible ducting from the vent box there was some, but not a substantial amount of lint build up.
  #30  
Old 06-08-2025, 11:17 AM
Lgellar Lgellar is offline
Junior Member
Join Date: Sep 2019
Posts: 2
Thanks: 0
Thanked 0 Times in 0 Posts
Default Ventless all in one washer dryer

Quote:
Originally Posted by retiredguy123 View Post
The code says that the inside of the duct must be "smooth", but it is somewhat unclear as to whether the end can be crimped. It appears that some installations use a smooth end and others use a crimped end. If you want to make the inside of the vent pipe to be more smooth you can use a plastic transition piece between the flexible dryer duct and the crimped metal pipe. This transition piece will fit inside of the metal duct. But, I tend to agree with Poster No. 7 that it is probably insignificant.
You may want to look into an all in one washer dryer that is ventless. I would recommend the GE one.