Old Topic, but I still can't solve this: CYV light & fan out in master bathroom

Closed Thread
Thread Tools
  #1  
Old 11-11-2024, 09:58 PM
E Cascade E Cascade is offline
Member
Join Date: Aug 2019
Posts: 99
Thanks: 0
Thanked 52 Times in 31 Posts
Default Old Topic, but I still can't solve this: CYV light & fan out in master bathroom

CYV about 5 yo with light and its fan out in ceiling of Roman walk-in shower in master bathroom. 2 GFCI outlets by paired sinks also out. Other lights and fan by toilet are fine. The circuit breaker in garage has flipped and when I move it totally to the off position and then attempt to reset it, it won't reset. I cannot find any GFCI outlets in villa with a test and reset buttons. I only have two outlets in garage and both work and do not have test buttons either.
3 questions: If the light bulb is now blown (it would usually light slowly and slowly get brighter as a norm), would that trip the circuit and also affect the fan, and the daisy chained outlets by the sinks?
Or, is the problem with the circuit breaker and how can I tell that?
Where do I get one of those bulbs that lights slowly, to full bright?

Also wondering where that outlet would be with the 2 reset/test buttons.

What a bummer to solve! Thanks for ideas.
  #2  
Old 11-11-2024, 10:16 PM
CarlR33 CarlR33 is offline
Veteran member
Join Date: Dec 2023
Location: Newell the place to be in the South
Posts: 830
Thanks: 605
Thanked 594 Times in 308 Posts
Default

If you posted before and no luck then it’s time to bite the bullet and call an electrician. The breaker is tripping for a reason and electric is nothing to mess with it could be your home or life if not diagnosed properly or let go, IMO. Your post should read can you recommend an electrician?
__________________
I will say the things that others are probably thinking but afraid to say.
  #3  
Old 11-12-2024, 04:29 AM
Mrprez's Avatar
Mrprez Mrprez is offline
Veteran member
Join Date: Jul 2020
Location: DeSoto
Posts: 874
Thanks: 1,330
Thanked 1,062 Times in 376 Posts
Default

What brand is the breaker? If they are Eaton, they have a defect but are warranted for 10 years. You have to go through Eaton directly. My master bath was doing the same thing. I replaced the breaker and the problems stopped.
Attached Thumbnails
The Villages Florida: Click image for larger version

Name:	IMG_1659.jpg
Views:	1715
Size:	50.3 KB
ID:	106407  
__________________
  #4  
Old 11-12-2024, 09:06 AM
villagetinker's Avatar
villagetinker villagetinker is offline
Sage
Join Date: Sep 2013
Location: Village of Pinellas
Posts: 10,974
Thanks: 3
Thanked 8,039 Times in 2,925 Posts
Default

Remove the bulb and see if the problem clears. I have never seen a bulb that slowly turns on, I suspect you have a bad connection somewhere that caused this effect and it has now failed completely. Also, I have seen a GFCI hidden in a closet next to the shower.

Now if none of this helps, as noted above, call an electrician.
__________________
Pennsylvania, for 60+ years, most recently, Allentown, now TV.
  #5  
Old 11-12-2024, 10:04 AM
blueash's Avatar
blueash blueash is offline
Sage
Join Date: Jan 2008
Posts: 3,386
Thanks: 253
Thanked 3,483 Times in 937 Posts
Default

Quote:
Originally Posted by villagetinker View Post
Remove the bulb and see if the problem clears. I have never seen a bulb that slowly turns on, I suspect you have a bad connection somewhere that caused this effect and it has now failed completely. Also, I have seen a GFCI hidden in a closet next to the shower.

Now if none of this helps, as noted above, call an electrician.
I have some CFL bulbs that produce fewer lumens when first switched on and reach full brightness after maybe a minute. I suspect that is what the OP is seeing.
__________________
Men plug the dikes of their most needed beliefs with whatever mud they can find. - Clifford Geertz
  #6  
Old 11-12-2024, 01:25 PM
villagetinker's Avatar
villagetinker villagetinker is offline
Sage
Join Date: Sep 2013
Location: Village of Pinellas
Posts: 10,974
Thanks: 3
Thanked 8,039 Times in 2,925 Posts
Default

Quote:
Originally Posted by blueash View Post
I have some CFL bulbs that produce fewer lumens when first switched on and reach full brightness after maybe a minute. I suspect that is what the OP is seeing.
OMG, I forgot about those, good point, I was thinking incandescent as LED types would not do this.
__________________
Pennsylvania, for 60+ years, most recently, Allentown, now TV.
  #7  
Old 11-13-2024, 04:26 AM
RoadToad RoadToad is offline
Senior Member
Join Date: Aug 2017
Posts: 221
Thanks: 56
Thanked 128 Times in 71 Posts
Default

Probably GFCI or AFCI ckt breaker. If Fault protection is in the breaker, none of the protected outlets would have buttons.
ArcFault breakers are quite sensitive and prone to failure.
  #8  
Old 11-13-2024, 04:33 AM
rsmurano rsmurano is offline
Veteran member
Join Date: Jul 2021
Posts: 999
Thanks: 6
Thanked 922 Times in 466 Posts
Default

Does your breaker have the 2nd slide switch on top of it? Some are colored while while others are black no color. Most of the time you only need to reset this smaller switch. If you reset the larger breaker switch it still won’t reset the smaller switch. When I built a new house 10 years ago, most of my single pole breakers had these 2nd switches and the electrical code was to put them in any new house at the time. I had the electrician come back and he replaced most of them with standard breakers and never had a problem again. When I sold the house I put the original breakers back in
  #9  
Old 11-13-2024, 07:01 AM
MikeN MikeN is offline
Senior Member
Join Date: Jul 2023
Posts: 172
Thanks: 468
Thanked 133 Times in 71 Posts
Default

Never heard of a light bulb that comes on dim and gradually gets brighter. That is a very good place to start looking. Something about that fixture is wrong and a good place for an electrician to start looking
  #10  
Old 11-13-2024, 07:20 AM
Dream2retire Dream2retire is offline
Junior Member
Join Date: Dec 2023
Posts: 10
Thanks: 15
Thanked 1 Time in 1 Post
Default

Breakers sometime fail when they trip. If they are ground fault they tend to fail in more frequently and in a safe state ( which means it won’t close again). When changing the breaker, If you have a multi meter I would test resistance to ground on the wire you remove from the breaker. There should not be a path to ground if all fan/light switches are off. If you turn them on there still shouldn’t be a very low resistance to ground. If there is, you can at least narrow it down to where the issue is. I suspect it’s just the breaker failing after an actual problem.
  #11  
Old 11-13-2024, 07:48 AM
lpkruege1 lpkruege1 is offline
Senior Member
Join Date: Feb 2020
Posts: 170
Thanks: 386
Thanked 186 Times in 83 Posts
Default Check and Recheck

Quote:
Originally Posted by E Cascade View Post
CYV about 5 yo with light and its fan out in ceiling of Roman walk-in shower in master bathroom. 2 GFCI outlets by paired sinks also out. Other lights and fan by toilet are fine. The circuit breaker in garage has flipped and when I move it totally to the off position and then attempt to reset it, it won't reset. I cannot find any GFCI outlets in villa with a test and reset buttons. I only have two outlets in garage and both work and do not have test buttons either.
3 questions: If the light bulb is now blown (it would usually light slowly and slowly get brighter as a norm), would that trip the circuit and also affect the fan, and the daisy chained outlets by the sinks?
Or, is the problem with the circuit breaker and how can I tell that?
Where do I get one of those bulbs that lights slowly, to full bright?

Also wondering where that outlet would be with the 2 reset/test buttons.

What a bummer to solve! Thanks for ideas.
Do the GFI outlets work when you plug something into them? Is there a GFI outlet in the master bathroom? Does it test properly when you press the test & Reset buttons? Have you looked at your outside outlets to see if any of the GFI outlets are tripped? Have you tried to replace the bulb with a new and tested bulb? Try a standard bulb. Is there a dimmer switch controlling the bulb that comes on slowly? Could be the dimmer switch. If the simple things do not make a difference, time to call an electrician.
  #12  
Old 11-13-2024, 08:37 AM
Biskopski Biskopski is offline
Junior Member
Join Date: Oct 2023
Posts: 20
Thanks: 16
Thanked 8 Times in 6 Posts
Default

Call the electrican whose sticker is in the box of the panel. That's who wired the home. They will tell you how to reset the breaker. Seems they are a little different than the older traditional box breakers. You must move the breaker switch to the off position and hold it there for about 10 seconds count then move it to the on position. Breaker should then hold. Hope that does the trick for you. We encountered the exact problem when we moved here 1 yr ago and the same light and plug outlets affected.
  #13  
Old 11-13-2024, 09:07 AM
Maker Maker is offline
Veteran member
Join Date: Jul 2022
Posts: 616
Thanks: 13
Thanked 532 Times in 237 Posts
Default

Questions...

>2 GFCI outlets by paired sinks also out. Other lights and fan by toilet are fine.
Do you mean the 2 dead outlets are both the type with GFCI test and reset buttons? Or are they on a common circuit with a GFCI circuit breaker?

I do not recall if you mentioned if there is a GFCI breaker that is tripping? Or is it a regular breaker? Post a picture.

>The circuit breaker in garage has flipped and when I move it totally to the off position and then attempt to reset it, it won't reset.
Try moving it to the full off position, and leave it there for a few minutes. Then try reset.

>If the light bulb is now blown ... would that trip the circuit
If bulb is shorted, then it should trip breaker. Not generally a GFCI issue, but a simple overload. Put in a new bulb. Easier than trying to guess.
If that is tripping a GFCI, that means there is a current leak path from the hot lines to ground. That should not happen in a light bulb fixture. That would be a wiring problem (frayed, pierced...)
  #14  
Old 11-17-2024, 05:44 AM
Maker Maker is offline
Veteran member
Join Date: Jul 2022
Posts: 616
Thanks: 13
Thanked 532 Times in 237 Posts
Default

There have been several people who have offered suggestions and help.
OP is silent. Would be nice to hear back and see if things were solved, and what the problem was if fixed.
  #15  
Old 11-17-2024, 10:15 AM
villagetinker's Avatar
villagetinker villagetinker is offline
Sage
Join Date: Sep 2013
Location: Village of Pinellas
Posts: 10,974
Thanks: 3
Thanked 8,039 Times in 2,925 Posts
Default

Quote:
Originally Posted by Maker View Post
There have been several people who have offered suggestions and help.
OP is silent. Would be nice to hear back and see if things were solved, and what the problem was if fixed.
I agree and even sent a PM to help with no reply.