Quote:
Originally Posted by roadtoad View Post
actually pretty sure the propane regulator does not convert liquid to gas.
The liquid sublimates to gas as it expands in the bottle.
The regulator regulates the gas flow; not liquid.
you would probably have enjoyed a tour of an lng facility where the gas arrives in liquid form -260 ⁰f
  #17  
Old 08-04-2025, 06:21 AM
Worldseries27 Worldseries27 is online now
Platinum member
Join Date: Oct 2019
Posts: 1,615
Thanks: 357
Thanked 917 Times in 528 Posts
Default Natural gas bbq

Quote:
Originally Posted by tophcfa View Post
it can be done, a friend did that up north. We don’t have gas at our villages home so it’s not an option. To do the conversion, you obviously need to run a gas line to the grill. You also would have to get a different type of regulator since you would be using gas instead of a regulator that is designed to convert liquid propane into a gas.
attached is a photo of my natural gas bbq installation done at the build. The line travels from the gas dryer connection in the attic to the wall of the bedroom closest to the lanai and exits the home to a shut off valve. At that point it then enters the ground and cuts under the lanai and up.
Attached Thumbnails
The Villages Florida: Click image for larger version

Name:	IMG_20250804_071939.jpg
Views:	74
Size:	21.3 KB
ID:	109413  
  #18  
Old 08-04-2025, 06:26 AM
CoachKandSportsguy CoachKandSportsguy is offline
Sage
Join Date: Jan 2019
Location: Marsh Bend
Posts: 3,761
Thanks: 653
Thanked 2,760 Times in 1,340 Posts
Default

Quote:
Originally Posted by FredMitchell View Post
Yes. Call a plumber.
for a plumber to come out and do what specifically
when LNG gas is not available at the location?
  #19  
Old 08-04-2025, 06:57 AM
Worldseries27 Worldseries27 is online now
Platinum member
Join Date: Oct 2019
Posts: 1,615
Thanks: 357
Thanked 917 Times in 528 Posts
Default Baby it's cold outside

We used to cook on our propane bbq up north in 5⁰ f or 95 without any regulator issues. My sister lived in the villages since 98 and this never happened to her either. Anyway lets blame it on the " safety devices" inside the tank. I use ng but if i used propane i would try wrapping the tank to insulate it before i dealt with the issues of connecting and reconnecting hoses.
Don't get me started about regulating high pressure regulators for dual fuel boilers using manometers.
  #20  
Old 08-04-2025, 07:09 AM
Worldseries27 Worldseries27 is online now
Platinum member
Join Date: Oct 2019
Posts: 1,615
Thanks: 357
Thanked 917 Times in 528 Posts
Default

Quote:
Originally Posted by roadtoad View Post
actually pretty sure the propane regulator does not convert liquid to gas.
The liquid sublimates to gas as it expands in the bottle.
The regulator regulates the gas flow; not liquid.
point of interest. I was riding in a car with an lng operator who spotted a gas facility off warm springs ave nb by the ftpk. He believed it was a small heat exchanger plant that warms up the super cold pipeline gas to more manageable pressures. We couldn't pull off to check.
  #21  
Old 08-04-2025, 07:27 AM
Bruceg0028 Bruceg0028 is offline
Member
Join Date: Aug 2021
Posts: 37
Thanks: 13
Thanked 14 Times in 10 Posts
Default

We have had Webber’s for years and never had a problem with the regulator but I have had problems with some tanks. There is a small rubber oring where the tank valve hooks up to the regulator hose. I’ve seen them damaged or missing.

I also always turn off the tank when not in use. Just takes a minute to do and takes the pressure off the regulator.
  #22  
Old 08-04-2025, 07:28 AM
Miboater Miboater is online now
Senior Member
Join Date: Oct 2021
Location: Village of Hawkins
Posts: 225
Thanks: 13
Thanked 132 Times in 85 Posts
Default

I had the same problem with my Weber and it was the tank and not the regulator. I have a spare tank and I would get both of them refilled at Ace. One of the tanks would work just fine while the other would shut off every 20 minutes or so. I finally did a tank exchange and never had another problem.
  #23  
Old 08-04-2025, 08:05 AM
Dgodin Dgodin is offline
Senior Member
Join Date: Feb 2018
Location: Orange Blossom
Posts: 249
Thanks: 83
Thanked 118 Times in 82 Posts
Default

I've had my Weber grill outside, directly exposed to the sun for seven years without issue but I use a cover, which also keeps rainwater out of the grease trap.
  #24  
Old 08-04-2025, 08:12 AM
ton80 ton80 is offline
Senior Member
Join Date: Oct 2012
Posts: 166
Thanks: 15
Thanked 160 Times in 74 Posts
Default So Many Incorrect Statements in These Posts

Quote:
Originally Posted by Worldseries27 View Post
you would probably have enjoyed a tour of an lng facility where the gas arrives in liquid form -260 ⁰f
I have worked on LNG plants design and operations and in US NG pipelines. I also have dealt with the LPG Tank regulator safety shutoff issues. So here goes:

1. The original basic problem was identified correctly in above posts as opening the LPG tank valve when the burner valves were not closed. The safety treated the very low pressure as a leak and reduced the LPG flow to minimum. Just close the LPG tank valve; close all burner valves; finally open the LPG tank valves slowly wait a minute then open the burner valves and light off.

2. Insulating the LPG tank will not do anything good to eliminate the low flow propane vapor issue..

3. LPG vapors are not the result of sublimation which is vapors going from solid to vapor without going through the liquid phase.

4. Pipeline NG is not at low temperatures. Pipeline gas is typically at soil temperatures say 50 to 90F in Florida. There is no heater on Florida NG distribution systems. Sometimes there are recompression stations which may have some controlled releases for equipment isolation etc.

5. In a LPG tank, the liquid Propane is at equilibrium conditions with the Propane Vapor. If the tank heats up the vapor pressure increases until the safety valve relieves the pressure. This high pressure release is not caused by ambient temperatures unless there is a fire.

That is enough for now.
  #25  
Old 08-04-2025, 08:28 AM
Bill14564 Bill14564 is online now
Sage
Join Date: Nov 2020
Location: Village of Hillsborough
Posts: 7,357
Thanks: 2,282
Thanked 7,719 Times in 3,028 Posts
Default

Quote:
Originally Posted by Bruceg0028 View Post
We have had Webber’s for years and never had a problem with the regulator but I have had problems with some tanks. There is a small rubber oring where the tank valve hooks up to the regulator hose. I’ve seen them damaged or missing.

I also always turn off the tank when not in use. Just takes a minute to do and takes the pressure off the regulator.
Good advice, and it is what I normally do, but I bet this is what caused my problems.

I always turn off both the grill and the tank. It's easy enough to turn the tank back on and up north I've seen where squirrels have eaten through the rubber line leading to a leak. Turning the tank off protects against that and it is simple enough to start the grill, just spin the tank valve open and then work with the burner control.

BUT, I wonder if this sometimes leads to the safety issue. What if there was a slow leak, like a bad o-ring or a loose connection, that allowed the pressure in the line to dissipate? The leak could be small enough to never notice it, just enough that it allowed the pressure in the line to drop between uses. If that happened then when I quickly opened the tank and the fuel quickly refilled the line, it might have appeared to be a leak and triggered the safety.

I've gotten lazy and haven't worried about the squirrels so the tank has been left on with pressure in the line. I haven't had the safety issue since.

Seeing ton80's response, maybe I didn't need to disconnect/reconnect the lines, maybe doing that just caused me to wait a minute before turning the tank back on. If it ever happens again I'll try being more patient.
__________________
Why do people insist on making claims without looking them up first, do they really think no one will check? Proof by emphatic assertion rarely works.
Confirmation bias is real; I can find any number of articles that say so.


Victor, NY - Randallstown, MD - Yakima, WA - Stevensville, MD - Village of Hillsborough
  #26  
Old 08-04-2025, 09:59 AM
ton80 ton80 is offline
Senior Member
Join Date: Oct 2012
Posts: 166
Thanks: 15
Thanked 160 Times in 74 Posts
Default Go To Weber Site to see their advise on Regulator in Bypass Mode

Quote:
Originally Posted by ton80 View Post
I have worked on LNG plants design and operations and in US NG pipelines. I also have dealt with the LPG Tank regulator safety shutoff issues. So here goes:

1. The original basic problem was identified correctly in above posts as opening the LPG tank valve when the burner valves were not closed. The safety treated the very low pressure as a leak and reduced the LPG flow to minimum. Just close the LPG tank valve; close all burner valves; finally open the LPG tank valves slowly wait a minute then open the burner valves and light off.

2. Insulating the LPG tank will not do anything good to eliminate the low flow propane vapor issue..

3. LPG vapors are not the result of sublimation which is vapors going from solid to vapor without going through the liquid phase.

4. Pipeline NG is not at low temperatures. Pipeline gas is typically at soil temperatures say 50 to 90F in Florida. There is no heater on Florida NG distribution systems. Sometimes there are recompression stations which may have some controlled releases for equipment isolation etc.

5. In a LPG tank, the liquid Propane is at equilibrium conditions with the Propane Vapor. If the tank heats up the vapor pressure increases until the safety valve relieves the pressure. This high pressure release is not caused by ambient temperatures unless there is a fire.

That is enough for now.
Some additional advice can be found on Weber site : why wont your gas-grill get hot its probably in bypass mode

Why Won'''t Your Gas Grill Get Hot? It'''s Probably in Bypass Mode. | Burning Questions | Weber Grills

They list:
1. Bypass mode required since 1995 as a safety measure
2, How to avoid creating the bypass mode flow restriction.
3. How to get out of the bypass mode if you have the issue
  #27  
Old 08-04-2025, 02:19 PM
Worldseries27 Worldseries27 is online now
Platinum member
Join Date: Oct 2019
Posts: 1,615
Thanks: 357
Thanked 917 Times in 528 Posts
Default

Quote:
Originally Posted by thirdoffive View Post
i can't address the issue of the leaking regulator other than ours (3 years old) is working fine. I'm not surprised though as it is obvious that things built recently are built more cheaply than things built some time back. My brother has the refrigerator our parents bought when they got married (1947) and it works as well today as it ever did.
the film " a tree grows in brooklyn" 1945 depicts many old appliances in it. I especially liked the gas lighting and the little t valves and i know it was impossible for those not to have been leaking with the constant on and off usages. Some of the refrigerators of that era also were powered by ng.
  #28  
Old Yesterday, 07:48 AM
ThirdOfFive ThirdOfFive is offline
Sage
Join Date: Jun 2021
Posts: 3,513
Thanks: 759
Thanked 5,545 Times in 1,884 Posts
Default

Quote:
Originally Posted by Worldseries27 View Post
the film " a tree grows in brooklyn" 1945 depicts many old appliances in it. I especially liked the gas lighting and the little t valves and i know it was impossible for those not to have been leaking with the constant on and off usages. Some of the refrigerators of that era also were powered by ng.
Interesting. Back in the day my parents bought a piece of riverfront land and (with the help of one of my younger brothers) built a log cabin on it. Lighting was all gaslight (pretty efficient: Dad had rigged up a complete piping system to something like six gas lights overall), and they did have an LP refrigerator. I have no idea where they got it from.
  #29  
Old Today, 05:17 AM
Ignatz Ignatz is offline
Senior Member
Join Date: Nov 2023
Posts: 224
Thanks: 160
Thanked 215 Times in 91 Posts
Default

Great thread. Looking back, I did have an experience where I thought I replaced a tank that I thought still had lp in it but the grill wouldn’t burn. Didnt know about the low flow.