Humidity is likely low because humidity in Central Florida is low this past week (because enesto sucked humidity out) but that will change today with temps to 96ish all week.

If the water catch pan or the drain is clogged, it would shut off outside cooling unit but inside fan would still be running, usually continuous.

This is 95% likely the problem. I had to flush my drain yesterday after it clogged up.

Call for service.
  #32  
Old 08-19-2024, 09:42 AM
Albany Albany is offline
Member
Join Date: Dec 2013
Posts: 92
Thanks: 129
Thanked 67 Times in 38 Posts
Default Ac/humidistat setting

Quote:
Originally Posted by E Cascade View Post
My AC thermostat is set at 83. Temp in house is saying 89. Humidity in CYV by my clock on wall says 55-56. I am not at the house and I just had a friend check it out for me.
Question is: Is this too big of a variable between set temp and actual temp that is being read on the thermostat? Since I am not at the house at this time, I am wondering if all is OK. Villa is only <5 yo. Never had any problems before and I actually have never noticed what the variable is before the unit comes on, when I am there It's always been fine.
Any thoughts would be appreciated. Thanks.
It is probably fine. The humidistat overrides the AC, which will not come on until the humidistat hits 55 and activates it. It is simple to find out. Turn the humidistat to ON from the 55 setting. Wait a little, if the AC comes on you do not have a problem. The system is operating as it should. Then turn the humidistat back to 55.
  #33  
Old 08-19-2024, 09:51 AM
retiredguy123 retiredguy123 is offline
Sage
Join Date: Feb 2016
Posts: 17,436
Thanks: 3,047
Thanked 16,612 Times in 6,563 Posts
Default

Quote:
Originally Posted by Albany View Post
It is probably fine. The humidistat overrides the AC, which will not come on until the humidistat hits 55 and activates it. It is simple to find out. Turn the humidistat to ON from the 55 setting. Wait a little, if the AC comes on you do not have a problem. The system is operating as it should. Then turn the humidistat back to 55.
Note that, if the system were trying to control humidity, the house temperature would be lower than the thermostat setting, not 6 degrees higher. The only way to reduce humidity is to overcool the house. Unless you have a real humidifier with reheat, which most Village houses do not have, the optional humidity setting will overcool the house by about 3 degrees below the thermostat setting to reduce humidity. To me, a house temperature of 89 degrees indicates that the AC may not be cooling at all.
  #34  
Old 08-19-2024, 10:01 AM
westernrider75 westernrider75 is offline
Senior Member
Join Date: Aug 2020
Posts: 452
Thanks: 153
Thanked 313 Times in 178 Posts
Default

Quote:
Originally Posted by E Cascade View Post
My AC thermostat is set at 83. Temp in house is saying 89. Humidity in CYV by my clock on wall says 55-56. I am not at the house and I just had a friend check it out for me.
Question is: Is this too big of a variable between set temp and actual temp that is being read on the thermostat? Since I am not at the house at this time, I am wondering if all is OK. Villa is only <5 yo. Never had any problems before and I actually have never noticed what the variable is before the unit comes on, when I am there It's always been fine.
Any thoughts would be appreciated. Thanks.
Just a point of reference, my a/c comes when temp is one degree higher than what it is set at.

My snowbird neighbor had this same problem several months ago and there was something wrong with her a/c. Minor fix now all is well.
  #35  
Old 08-19-2024, 10:01 AM
DAVES DAVES is offline
Sage
Join Date: Feb 2014
Posts: 3,539
Thanks: 196
Thanked 1,920 Times in 984 Posts
Default

Quote:
Originally Posted by E Cascade View Post
My AC thermostat is set at 83. Temp in house is saying 89. Humidity in CYV by my clock on wall says 55-56. I am not at the house and I just had a friend check it out for me.
Question is: Is this too big of a variable between set temp and actual temp that is being read on the thermostat? Since I am not at the house at this time, I am wondering if all is OK. Villa is only <5 yo. Never had any problems before and I actually have never noticed what the variable is before the unit comes on, when I am there It's always been fine.
Any thoughts would be appreciated. Thanks.
I think the real question is, you do not want to stick your friend in the middle. "Not in the house at this time," you do not say how long you will be gone. Apparently your friend has a key. A service call will cost about $100. It is not like the service person will not realize you are not home. IF, I was the friend, I would not be willing to mess with it. I would lay out the money for you and get a receipt for you-assuming you have a good history. Simple cheap stuff. Drain line clogged. Filter needs replacing.
  #36  
Old 08-19-2024, 10:02 AM
Bill14564 Bill14564 is offline
Sage
Join Date: Nov 2020
Location: Village of Hillsborough
Posts: 7,244
Thanks: 2,247
Thanked 7,656 Times in 2,989 Posts
Default

Quote:
Originally Posted by Albany View Post
It is probably fine. The humidistat overrides the AC, which will not come on until the humidistat hits 55 and activates it. It is simple to find out. Turn the humidistat to ON from the 55 setting. Wait a little, if the AC comes on you do not have a problem. The system is operating as it should. Then turn the humidistat back to 55.
Are you saying that the thermostat cannot control both the humidity and the temperature? If I ask it to control humidity then the temperature can rise well above the set point as long as the humidity is low? That isn't what I would have expected.

I would expect my thermostat to keep my home near the temperature setting. If I have the dehumidify function enabled then I would expect the AC to EXTRA, if necessary, to keep the humidity level down.

If I have the AC set to a high temp, maybe 85, then I would expect that the humidity might rise and the AC to run to dehumidify the home. This additional running might keep the temp below 85 at times. But I would never expect the thermostat to ignore the temperature setting and allow the home to get very warm just because the humidity level has not risen.

I didn't see this "dehumidify-only" setting in the manual for my old, dumb thermostat. Is it a feature of the newer, "smart" thermostats?
__________________
Why do people insist on making claims without looking them up first, do they really think no one will check? Proof by emphatic assertion rarely works.
Confirmation bias is real; I can find any number of articles that say so.


Victor, NY - Randallstown, MD - Yakima, WA - Stevensville, MD - Village of Hillsborough
  #37  
Old 08-19-2024, 10:19 AM
biker1 biker1 is offline
Sage
Join Date: May 2014
Posts: 3,641
Thanks: 2
Thanked 1,231 Times in 709 Posts
Default

The system has some issue(s). There is a high probability that it is a clogged condensate tube that is tripping the float valve or a failed start capacitor. This has already been suggested as a possible cause. There are numerous other possibilities such as low refrigerant from a leak. Without the capability of checking the two highly probable reasons, the home owner should engage an HVAC professsional. It appears that the system may still be under a 10 year parts and 5 year labor warranty (unless the default warranty has changed since I bought my home new). Relative humidity is a strong function of temperature. You can drop the relative humidity by increasing the temperature with the same absolute amount of moisture in the air. The actual moisture content of the air is higher than it should be if the temperature set point was being met with 55% relative humidity. This means the system has not been running and removing moisture. I have never seen a properly functioning system sustain a 6 degree temperature difference between the actual temperature and the set point.

I have had both a clogged condensate drain and failed start capacitor cause my system to stop. I regularly pour vinegar and hot water down the condensate drain and preemptively replace the start capacitor every two years. It is a $15 part and takes 10 minutes to swap out. Yes, that is overkill but we are gone a fair amount.

Quote:
Originally Posted by Albany View Post
It is probably fine. The humidistat overrides the AC, which will not come on until the humidistat hits 55 and activates it. It is simple to find out. Turn the humidistat to ON from the 55 setting. Wait a little, if the AC comes on you do not have a problem. The system is operating as it should. Then turn the humidistat back to 55.

Last edited by biker1; 08-19-2024 at 10:44 AM.
  #38  
Old 08-19-2024, 10:21 AM
retiredguy123 retiredguy123 is offline
Sage
Join Date: Feb 2016
Posts: 17,436
Thanks: 3,047
Thanked 16,612 Times in 6,563 Posts
Default

The typical thermostat in The Villages has an option humidity setting that will reduce the humidity by allowing the AC to run longer than it needs to, so the house temperature will occasionally drop below the temperature setting. It is a "compromise" because the only way to control both the temperature and the humidity is with a real humidity control system that has a reheat feature. With a reheat feature, both the temperature and humidity can be controlled simultaneously by cooling and reheating the air to obtain the desired temperature and humidity. Personally, I never use the optional humidity setting because it makes the house too cold, and a real humidity control system is expensive and not worth it.
  #39  
Old 08-19-2024, 10:26 AM
rjm1cc's Avatar
rjm1cc rjm1cc is offline
Soaring Eagle member
Join Date: Apr 2010
Posts: 2,470
Thanks: 268
Thanked 583 Times in 283 Posts
Default

Quote:
Originally Posted by SaucyJim View Post
95% the drain condensate line needs to be vacuumed out and then flushed with hot water — not vinegar. Just hot water from the tap. That will clear the shutoff switch and the AC - not just the blower - will fire back up. I own two homes here and proactively flush mine monthly so vacuuming the line is not necessary.

Trust me. It’s not your thermostat. It’s not your electric panel. And it’s not the underpants gnomes. 😎
Good suggestion, clogged drain line is common. I run about a gallon of water through each month and then a cup of vinegar.
  #40  
Old 08-19-2024, 10:35 AM
Altavia Altavia is offline
Sage
Join Date: Jun 2019
Posts: 4,567
Thanks: 1,930
Thanked 3,507 Times in 1,678 Posts
Default

Quote:
Originally Posted by BobGraves View Post
I'm assuming you have the Ecobee smart thermometer. Log in on Ecobee WEBSITE and click HOME IQ, then SYSTEM MONITOR. This will show you system run times.
I had this problem. Compressor was running $$$ but fan was not. Had new fan installed under warranty (Tank God). System showed constantly running but would not cool because no air movement.
Good tip - thanks!

Here's a link:

https://www.ecobee.com/consumerporta...s/411935960765
  #41  
Old 08-19-2024, 10:47 AM
Altavia Altavia is offline
Sage
Join Date: Jun 2019
Posts: 4,567
Thanks: 1,930
Thanked 3,507 Times in 1,678 Posts
Default

Quote:
Originally Posted by Nana2Teddy View Post
I don’t know where your villa is located, but last week down south of 44 many homes in some villages were affected by a lightning strike on a transmission line in Coleman, that caused a “blink”, which tripped random breakers in our panels. We had 8-10 breakers tripped, as did many villagers here in DeLuna, plus there were some in Richmond and likely other villages down here. We had to call SECO the next day to ask what happened because there was zero communication from them about it. Not likely your issue, but thought I’d mention in just in case.
Off topic: Would be interesting to know if homes with the SECO or other surge protectors had tripped breakers.

So I hope you don't mind I copied your post to one of the surge suppression threads so people can reply to that question there.

Many Villagers Concerned About Lightning and Surge Protection
  #42  
Old 08-19-2024, 10:49 AM
JRcorvette JRcorvette is offline
Veteran member
Join Date: Oct 2022
Posts: 583
Thanks: 609
Thanked 456 Times in 228 Posts
Default

Quote:
Originally Posted by E Cascade View Post
My AC thermostat is set at 83. Temp in house is saying 89. Humidity in CYV by my clock on wall says 55-56. I am not at the house and I just had a friend check it out for me.
Question is: Is this too big of a variable between set temp and actual temp that is being read on the thermostat? Since I am not at the house at this time, I am wondering if all is OK. Villa is only <5 yo. Never had any problems before and I actually have never noticed what the variable is before the unit comes on, when I am there It's always been fine.
Any thoughts would be appreciated. Thanks.
The variation should only be 2 degrees but your Thermostat may not be reading accurately
  #43  
Old 08-19-2024, 10:52 AM
JRcorvette JRcorvette is offline
Veteran member
Join Date: Oct 2022
Posts: 583
Thanks: 609
Thanked 456 Times in 228 Posts
Default

Clogged drain line… check that first. If not that it is probably your capacitor. Buy on Amazon for about $12 easy to install or hire any handyman. An AC company will charge your $180-$225. Rip Off.
  #44  
Old 08-19-2024, 11:06 AM
Altavia Altavia is offline
Sage
Join Date: Jun 2019
Posts: 4,567
Thanks: 1,930
Thanked 3,507 Times in 1,678 Posts
Default

Quote:
Originally Posted by biker1 View Post
The system has some issue(s). There is a high probability that it is a clogged condensate tube that is tripping the float valve .
Adding, The float valve may be wired to also cut power to the thermostat.

If so, the thermostat goes blank when the floor valve activates.
  #45  
Old 08-19-2024, 11:59 AM
Karmanng Karmanng is offline
Senior Member
Join Date: Sep 2022
Posts: 246
Thanks: 501
Thanked 80 Times in 49 Posts
Default

things may need cleanings including the fan blower and the bottom part of the air unit plus the outside..........may need new capacitor mine needed all that after 5 years and over $1000.00 later and I had people here that took care of it for a bit and regular maitnence