AC question Set at 83, current temp in CYV 89, humidity is 55-56. All OK?

Closed Thread
Thread Tools
  #46  
Old 08-19-2024, 12:00 PM
Karmanng Karmanng is offline
Senior Member
Join Date: Sep 2022
Posts: 246
Thanks: 501
Thanked 80 Times in 49 Posts
Default

Quote:
Originally Posted by JRcorvette View Post
Clogged drain line… check that first. If not that it is probably your capacitor. Buy on Amazon for about $12 easy to install or hire any handyman. An AC company will charge your $180-$225. Rip Off.
mine was free just because I had the warrenty transferred over for 100
  #47  
Old 08-19-2024, 12:21 PM
DrHitch DrHitch is offline
Senior Member
Join Date: Mar 2017
Location: Rio Grande village and Cleveland, OH
Posts: 309
Thanks: 736
Thanked 112 Times in 83 Posts
Default Tripped breaker means NO THERMOSTAT

If the breaker is (somehow) tripped, then your thermostat won't get 24v power and a remote (eg Nest) will be blank (no wireless).

In this case, the OP is seeing a setpoint much lower than the actual house. As others pointed out, likely a blown blower motor or clogged condensate line.


Quote:
Originally Posted by Altavia View Post
Off topic: Would be interesting to know if homes with the SECO or other surge protectors had tripped breakers.

Many Villagers Concerned About Lightning and Surge Protection
  #48  
Old 08-19-2024, 05:27 PM
rjm1cc's Avatar
rjm1cc rjm1cc is offline
Soaring Eagle member
Join Date: Apr 2010
Posts: 2,458
Thanks: 267
Thanked 574 Times in 278 Posts
Default

My thermostat has a red light that comes on when their is a problem. Yours might too.
  #49  
Old 08-21-2024, 07:49 AM
DonnaNi4os DonnaNi4os is offline
Veteran member
Join Date: Aug 2017
Posts: 662
Thanks: 221
Thanked 353 Times in 213 Posts
Default

If your thermostat is set at this high a number your ac should have no problem reaching that temp. Definitely a problem. I had a 4 degree difference two summers ago and ended up with no ac at all. First SunKool changed the coil, then the capacitor, then the compressor before it finally worked. This all took 3 weeks in stifling heat in August 2022. It was brutal. Despite me telling the service man over and over again with every service visit that my thermostat wasn’t reaching the set temp, he would tell me that it was normal in the heat of the summer. It is NOT NORMAL! Your ac should bring the temp to what you set the thermostat. Call your service company and if it’s SunKool get another company!
  #50  
Old 08-21-2024, 08:15 AM
Bill14564 Bill14564 is online now
Sage
Join Date: Nov 2020
Location: Village of Hillsborough
Posts: 6,824
Thanks: 2,092
Thanked 7,263 Times in 2,833 Posts
Default

Quote:
Originally Posted by DonnaNi4os View Post
If your thermostat is set at this high a number your ac should have no problem reaching that temp. Definitely a problem. I had a 4 degree difference two summers ago and ended up with no ac at all. First SunKool changed the coil, then the capacitor, then the compressor before it finally worked. This all took 3 weeks in stifling heat in August 2022. It was brutal. Despite me telling the service man over and over again with every service visit that my thermostat wasn’t reaching the set temp, he would tell me that it was normal in the heat of the summer. It is NOT NORMAL! Your ac should bring the temp to what you set the thermostat. Call your service company and if it’s SunKool get another company!
I know my system will cool my house at least 25 degrees below the outside temperature, but there is a limit. I wouldn't expect to be able to cool my house to 50 degrees on a 100 degree day but cooling to 75 degrees works just fine. Since replacing the compressor made yours work properly, you obviously were not asking for anything excessive.
__________________
Why do people insist on making claims without looking them up first, do they really think no one will check? Proof by emphatic assertion rarely works.
Confirmation bias is real; I can find any number of articles that say so.


Victor, NY
Randallstown, MD
Yakima, WA
Stevensville, MD
Village of Hillsborough
  #51  
Old 08-21-2024, 11:40 AM
DonnaNi4os DonnaNi4os is offline
Veteran member
Join Date: Aug 2017
Posts: 662
Thanks: 221
Thanked 353 Times in 213 Posts
Default

Quote:
Originally Posted by Bill14564 View Post
I know my system will cool my house at least 25 degrees below the outside temperature, but there is a limit. I wouldn't expect to be able to cool my house to 50 degrees on a 100 degree day but cooling to 75 degrees works just fine. Since replacing the compressor made yours work properly, you obviously were not asking for anything excessive.
My thermostat was set to 74. In the morning the temp would be 74-75 when I woke up. By noon the actual temp in my home was between 78-80. This was an ongoing situation that the serviceman claimed was normal and that I would never get my temp to any less than 10 degrees lower than what was outside. (BTW the thermostat was no where near a window in case you were wondering). So he was trying to convince me that if it was 95 outside I would never get the inside temp to lower than 85. I call bull-oney since that was ludicrous. So again, when it finally completely went it took 3 weeks in brutal heat with the only cool air coming from the portable unit I bought. I learned a lot about air conditioning that summer and was very grateful that my house was under 5 years old so still under parts and labor warranty. I also learned that by calling Carrier directly I finally got the needed parts installed.
  #52  
Old 08-21-2024, 11:55 AM
retiredguy123 retiredguy123 is online now
Sage
Join Date: Feb 2016
Posts: 16,843
Thanks: 2,922
Thanked 16,046 Times in 6,299 Posts
Default

Quote:
Originally Posted by DonnaNi4os View Post
My thermostat was set to 74. In the morning the temp would be 74-75 when I woke up. By noon the actual temp in my home was between 78-80. This was an ongoing situation that the serviceman claimed was normal and that I would never get my temp to any less than 10 degrees lower than what was outside. (BTW the thermostat was no where near a window in case you were wondering). So he was trying to convince me that if it was 95 outside I would never get the inside temp to lower than 85. I call bull-oney since that was ludicrous. So again, when it finally completely went it took 3 weeks in brutal heat with the only cool air coming from the portable unit I bought. I learned a lot about air conditioning that summer and was very grateful that my house was under 5 years old so still under parts and labor warranty. I also learned that by calling Carrier directly I finally got the needed parts installed.
Baloney is correct. The achievable temperature difference between outside and inside temperatures should be at least 20 to 25 degrees. I would suggest that you write down the model number and serial number for your Carrier system from the sticker on the inside air handling unit. Then, go to the Carrier warranty website where you will see the exact status of your warranty. You can also find the authorized Carrier dealers in the area. The most prominent dealer is Munn's.

Some HVAC repair companies claim that they can do Carrier warranty work, but I suspect that some of them will partner with another contractor. For example, if a non-authorized company diagnoses a defective compressor, I doubt that Carrier will send them a new compressor under a warranty claim because the compressor could have been damaged by a faulty installation.
  #53  
Old 08-22-2024, 06:41 AM
jrref jrref is offline
Gold member
Join Date: May 2021
Posts: 1,060
Thanks: 399
Thanked 660 Times in 346 Posts
Default

Quote:
Originally Posted by retiredguy123 View Post
Baloney is correct. The achievable temperature difference between outside and inside temperatures should be at least 20 to 25 degrees. I would suggest that you write down the model number and serial number for your Carrier system from the sticker on the inside air handling unit. Then, go to the Carrier warranty website where you will see the exact status of your warranty. You can also find the authorized Carrier dealers in the area. The most prominent dealer is Munn's.

Some HVAC repair companies claim that they can do Carrier warranty work, but I suspect that some of them will partner with another contractor. For example, if a non-authorized company diagnoses a defective compressor, I doubt that Carrier will send them a new compressor under a warranty claim because the compressor could have been damaged by a faulty installation.
The best way, and probably the most accurate way to check if you A/C is running correctly temperature wise is to take a temperature probe and stick it through the foam return duct at your air handler and take a reading then do the same at the output at the top of the air handler. The most you should see is a 20 degree temperature differential. 15-20 degree differential is considered "normal" but it should be close to 20 degrees once running for about 15 minutes. This will remove all the other variables trying to measure against the outside temperature. You can then take blue tape and cover the holes for next time. These HVAC temperature probes are available on amazon. Amazon.com
  #54  
Old 08-23-2024, 05:56 AM
Freehiker Freehiker is offline
Senior Member
Join Date: May 2020
Location: The Villages
Posts: 286
Thanks: 245
Thanked 198 Times in 87 Posts
Default

83?! 🥵🔥
__________________
AANR member since 1996

Hike naked, it adds color to your cheeks!
  #55  
Old 08-23-2024, 07:00 AM
mtdjed mtdjed is offline
Platinum member
Join Date: Jan 2009
Posts: 1,525
Thanks: 1
Thanked 1,215 Times in 424 Posts
Default

Quote:
Originally Posted by E Cascade View Post
My AC thermostat is set at 83. Temp in house is saying 89. Humidity in CYV by my clock on wall says 55-56. I am not at the house and I just had a friend check it out for me.
Question is: Is this too big of a variable between set temp and actual temp that is being read on the thermostat? Since I am not at the house at this time, I am wondering if all is OK. Villa is only <5 yo. Never had any problems before and I actually have never noticed what the variable is before the unit comes on, when I am there It's always been fine.
Any thoughts would be appreciated. Thanks.
Would be interesting to have an OP update to this post as to what the real problem was. People care enough to offer their time to respond, and others read and appreciate advice that may help them in the future. Which if any of the responses came close and what has been done to solve the dilemma?
  #56  
Old 08-23-2024, 07:29 AM
opinionist opinionist is offline
Senior Member
Join Date: Feb 2024
Posts: 268
Thanks: 59
Thanked 215 Times in 103 Posts
Default

I had the HVAC system freeze up due to a failed temperature control valve. Some cooling came from the system but not enough to maintain temperature control.
  #57  
Old 08-23-2024, 09:03 AM
Teed_Off Teed_Off is offline
Member
Join Date: May 2022
Posts: 71
Thanks: 1
Thanked 83 Times in 30 Posts
Default

Had a similar problem years ago. Indoor coil froze preventing cooled air to get to the house. Turned off the A/C, coil thawed, water dripped past the drain pan and into the return duct below the unit. The weight of the water collapsed the duct separating it from the unit. Took two days to dry out the fiberglass duct. Had to cut a hole in the side of the plenum to repair the ductwork.
Hopefully you won’t have the same issues.
  #58  
Old 08-23-2024, 03:10 PM
retiredguy123 retiredguy123 is online now
Sage
Join Date: Feb 2016
Posts: 16,843
Thanks: 2,922
Thanked 16,046 Times in 6,299 Posts
Default

Quote:
Originally Posted by jrref View Post
The best way, and probably the most accurate way to check if you A/C is running correctly temperature wise is to take a temperature probe and stick it through the foam return duct at your air handler and take a reading then do the same at the output at the top of the air handler. The most you should see is a 20 degree temperature differential. 15-20 degree differential is considered "normal" but it should be close to 20 degrees once running for about 15 minutes. This will remove all the other variables trying to measure against the outside temperature. You can then take blue tape and cover the holes for next time. These HVAC temperature probes are available on amazon. Amazon.com
I don't disagree with your technical method. But, my thermostat is always set on 78 degrees and, on some days, the outside temperature has exceeded 100 degrees, with no increase in the inside temperature. So, my system is able to maintain at least a 22 degree difference between the outside and inside temperatures. I have several outside and inside thermometers, so I know this is correct. I have not tested it to see if I can lower the thermostat setting and achieve a lower inside temperature. I don't know what other variables I would need to consider.
  #59  
Old 08-24-2024, 05:39 PM
jrref jrref is offline
Gold member
Join Date: May 2021
Posts: 1,060
Thanks: 399
Thanked 660 Times in 346 Posts
Default

Quote:
Originally Posted by retiredguy123 View Post
I don't disagree with your technical method. But, my thermostat is always set on 78 degrees and, on some days, the outside temperature has exceeded 100 degrees, with no increase in the inside temperature. So, my system is able to maintain at least a 22 degree difference between the outside and inside temperatures. I have several outside and inside thermometers, so I know this is correct. I have not tested it to see if I can lower the thermostat setting and achieve a lower inside temperature. I don't know what other variables I would need to consider.
That's fine. As I mentioned, the A/C can only reduce the temperature of the RETURN AIR, not the outside air, 20 degrees. And you measure this by taking a temperature reading at the return duct at the air handler and another reading at the output of the air handler at the duct right above it. You should see a maximun of about 20 degrees. Regardless of the outside air temperature, whatever the air temperature inside your home shoud be the reading you get at the return duct at the air handler. This is why you should never turn off or significantly lower your A/C on very hot days. If you do this it will take a very long time for your A/C to bring down the temperature in the house.
  #60  
Old 08-24-2024, 05:45 PM
Pairadocs Pairadocs is offline
Soaring Eagle member
Join Date: Oct 2020
Location: Here, there, a lot of time in the Caribbean and keys, not much time spent in cold climates
Posts: 2,318
Thanks: 1,777
Thanked 2,075 Times in 892 Posts
Default

Quote:
Originally Posted by E Cascade View Post
My AC thermostat is set at 83. Temp in house is saying 89. Humidity in CYV by my clock on wall says 55-56. I am not at the house and I just had a friend check it out for me.
Question is: Is this too big of a variable between set temp and actual temp that is being read on the thermostat? Since I am not at the house at this time, I am wondering if all is OK. Villa is only <5 yo. Never had any problems before and I actually have never noticed what the variable is before the unit comes on, when I am there It's always been fine.
Any thoughts would be appreciated. Thanks.
NOT OKAY AT ALL ! Only time we had anything like that was when we (foolishly!) did not keep track of putting the monthly white vinegar down the drain line and.... well, you KNOW what an expensive mistake that can be !